Participant

Join Date: Apr 2017
Posts: 3

2250kW 3.3kV Air-Cooled and Water-Cooled Drive

04/27/2017 10:12 AM

We are planning to install a 2250kW 3.3kV crushing unit motor with a VFD. But VFD Manufacturers are recommending to use water cooled drive since it is in a continuous 24/7 operation. And the price difference between air cooled and water co0led drive is about 50%, is it necessary to use watercooled drive, will it improve the life of drive and will it have less maintenance cost.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: 2250kW 3.3kV air cooled and water cooled drive

04/27/2017 10:24 AM

Usually the manufacturers know their products best, but you can certainly ignore their advice at your own risk and peril. Just remember that when the unit fails you will receive no warranty coverage. The choice is yours.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Apr 2017
Posts: 3
#2
In reply to #1

Re: 2250kW 3.3kV air cooled and water cooled drive

04/27/2017 11:36 AM

Thank you, But we have done a similar 2250kW 690V VFD same application with a air cooled drives and it is working good, is it because we are using high voltage VFD for the same power we need to use water cooled drives?

Going for a 3.3kV motor and Drive will it bring down by running cost of the equipment? since the current drawn for the same 2250 kW is less. if so, why Drive manufacturers are not recommending 6.6kV motor and VFD?

Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#3
In reply to #2

Re: 2250kW 3.3kV air cooled and water cooled drive

04/27/2017 1:02 PM

"... why Drive manufacturers are not recommending 6.6kV motor and VFD?"

Call them and ask. What could be easier?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: 2250kW 3.3kV air cooled and water cooled drive

04/27/2017 3:01 PM

It's time. Do let the forum know the outcome of the calls to the drive manufacturer, as there is always something to share and be learned from it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #2

Re: 2250kW 3.3kV air cooled and water cooled drive

04/27/2017 4:04 PM

So what if the current is less? The voltage is more. You are billed by wattage, not by amperage.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: 2250kW 3.3kV air cooled and water cooled drive

04/27/2017 4:48 PM

OK. Warranty seems to be going out the window.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4497
Good Answers: 137
#8
In reply to #2

Re: 2250kW 3.3kV air cooled and water cooled drive

04/28/2017 4:16 AM

Perhaps 690V without water cooling is more expensive than 3.3kV with? In any case, you would normally tell the vendor what supply voltage is available, not vice-versa.

__________________
Give masochists a fair crack of the whip
Register to Reply
2
Participant

Join Date: Feb 2013
Location: New Zealand
Posts: 4
Good Answers: 1
#7

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

04/28/2017 12:03 AM

I have worked with many HV drives for large electrical motors, from 1000kw @ 690v up to 6.5 Mw @ 2950kv, stepped down from the generation of 11KV and they have all been water cooled. I have also seen a fire inside a drive from lack of cooling which caused a great deal of damage. There is a reason that the drives are cooled and I think that you should have a good talk to the manufacturer and an electrical engineer that has experience in HV motors and drives.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #7

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

04/28/2017 5:54 AM

Absolutely. It's not going to be solved by email or by technical blogging. GA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

04/28/2017 1:09 PM

Dear Member,

The cooling effect achieved with in the permissible level is the criterion. Both air cooling design and water cooling design is unique and have its own merits and de-merits. The cost difference is mainly due to the the size of the cooling device.

Air cooling device - has low over-all heat transfer co-efficient, and water cooling device has higher over-all heat transfer co-efficient.and it may be in the order of 1;2.2 ratio.

Therefore the air cooling device will be larger in size and hence costly.

Better follow the manufacturer's instructions, to get the best out of the equipment.

DHAYANANDHAN.S

Edited Removed Bold - CR4 Admins

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #10

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

04/28/2017 3:55 PM

Quit shouting.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#12
In reply to #10

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

04/29/2017 1:28 PM

"Better follow the manufacturer's instructions, to get the best out of the equipment."

How's that 90 kW motor coming along?

Register to Reply Score 2 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

05/01/2017 2:32 AM

I am in the midst of a project with 4 x 4,000HP (roughly 3,000kW) 4160V VFD driven motors, the end user is demanding air cooled VFDs. To facilitate this, they need 15,000CFM (cubic feet per minute) of air flow for each drive, which equates to roughly 425 CMM, with the air temperature being a maximum of 30 degrees C. I can imagine that for yours, that would be only slightly less air flow. On my project, the drives and motors are in a relatively clean area; a water treatment plant. In a mine environment, that much air is going to bring with it a LOT of contaminants (pollution). So either that VFD will have to suffer the rigors of being dirty all the time, or there will need to be some extreme filtering and if someone forgets to change the filter, you could lose the VFD in short order. Liquid cooling means using heat exchangers mounted somewhere else, so moves that high volume of air movement to a different location where the contaminants are less critical.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Apr 2017
Posts: 3
#14

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

05/02/2017 5:57 AM

We understand from the manufacturer that water cooled drives are compact and the number of fuses and wires running into the panels will be less. Since this is Drive panels are compact it does not provide any advantage on reducing running cost or capital purchase cost. In fact the initial investment is high. Water cooled is preferred in industries where the chillers are available for their factory use. Air cooled system are relatively larger and prices are better than water cooled.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #14

Re: 2250kW 3.3kV Air Cooled And Water Cooled Drive

06/20/2023 8:32 AM

This forum doesn't usually get involved with money.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#16

Re: 2250kW 3.3kV Air-Cooled and Water-Cooled Drive

12/26/2023 6:13 AM

Not necessary.You can have aircooled motors too .water cooled motors have their own problems and additional requirements of piping relays to monitor water flow etc but aircooled apart from normal protection nothing else is required .air cooled motor may be in one higher frame compared to water cooled but over all cost including piping , accessories will more or less even out .

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andrew Westman (2); Codemaster (1); dhayanandhan (1); Ganny.134460 (2); gib (1); JRaef (1); nesubra (1); PWSlack (4); RAMConsult (1); Tornado (2)