UL508A 3 Phase Color Code?

04/27/2017 10:36 AM

Hello

I have a copy of UL508A

Trying to locate the appropriate wire color for 3 phase wiring

I was always under the impression of the following

L1 = Brown

L2 = Orange

L3 = Yellow

Does someone happen to know the section of 508A that describes this for reference?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#1

Re: UL508A 3 phase color code?

04/27/2017 11:00 AM

120V / 240V A/C Electrical Wiring Color Codes & Conventions: U.S.

Wire Insulation Color

Alternative Wire Colors

Label

Function

Comments

Black
LLine voltage, single phaseAbbreviation: BK
Black
Brown
L1Line voltage, 3-phaseAbbreviation: BK, BN, RD
Red
LLine voltage, single phase, second "hot" wire
Often used to indicate switched power
Red
Orange
L2Line voltage, 3-phaseAbbreviation: RD
White
Gray
NNeutral In wiring a switch the electrician may use the white wire as a second hot conductor and will mark each end of the wire with black electrical tape - shown below.

Abbreviation: WT, GY

Blue
Yellow
L3Line voltage, 3-phaseAbbreviation: BL, YL
Green
PG Protective ground wire

Abbreviation: GN

Green + YellowPG Protective ground wire

Abbreviation: GN+YL

Bare
PG
Protective ground wire, no insulation
Orange
Yellow
L "Excepted voltage", these wires may be hot when main disconnect is switched off"

Abbreviation: OR, YL

Notes & wiring color code standard sources:

1. National Electrical Code 2011 (NEC) - see http://www.nfpa.org/ (adopted in all 50 U.S. states)
2. UL508A, Section 66.5.3 & 66.9
3. NFPA 79, Chapter 13 - see http://www.nfpa.org/

Some sources include red with white tracer line = switched neutral

Source.

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Commentator

Join Date: Jan 2017
Posts: 57
Good Answers: 1
#2
In reply to #1

Re: UL508A 3 phase color code?

04/27/2017 11:15 AM

Thanks for the effort.

of course i have seent that doc many times

I am specifically after something from UL with a ref number that specs 3 phase color codes

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#3
In reply to #2

Re: UL508A 3 phase color code?

04/27/2017 11:18 AM

It says it on the bottom of the document, I put it in bold for you. Section 66.5.3 and 66.9. Is that not what you were looking for?

I don't have a copy of UL508A, so I can't verify.

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Commentator

Join Date: Jan 2017
Posts: 57
Good Answers: 1
#4
In reply to #3

Re: UL508A 3 phase color code?

04/27/2017 11:24 AM

Ill try to be more specific sorry

I dont see anywhere atleast in m 2013 version of UL508A

That says Brown Orange Yellow for 3 phase

Is there an updated version?

Typically from what i have seen they are all black with either a color tape or ferrel at the end indicating the Brown orange yellow.

But i have not seen anything in 66.9 or 66.5.3 that says that

Maybe my 508 is out of date?

Says 12/25/13 on it

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#5
In reply to #4

Re: UL508A 3 phase color code?

04/27/2017 11:44 AM

From what I read, 2013 is the latest version. But I can't find any reference to 3 phase color coding when it comes to UL508A. Are you sure they have it in UL508A?

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Commentator

Join Date: Jan 2017
Posts: 57
Good Answers: 1
#6
In reply to #5

Re: UL508A 3 phase color code?

04/27/2017 11:54 AM

no im not sure its in there

Thats what im trying to find.

Im trying to find a specific UL standard that states 3 phase color codes

I need to be able to refer back to it to prove we are in compliance

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#7
In reply to #6

Re: UL508A 3 phase color code?

04/27/2017 12:06 PM

Sorry, I can't help you, I can't find any reference to UL508A for 3 phase color codes. I believe it's in NFPA 79, chapter 13, but that probably isn't going to help you.

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Commentator

Join Date: Jan 2017
Posts: 57
Good Answers: 1
#8
In reply to #7

Re: UL508A 3 phase color code?

04/27/2017 12:20 PM

Thanks for trying

Think its possible that UL does not designate this at all?

Or perhaps in a different UL standard

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#9
In reply to #8

Re: UL508A 3 phase color code?

04/27/2017 12:27 PM

I am starting to think UL does not designate it at all, other than the wires need to be black.

I found this from Siemens, look at chapter 7, nothing listed for conductor colors in a UL cabinet other than black for ungrounded conductors.

http://www.siemens.fi/pool/products/industry/iadt_is/tuotteet/pienjannitekojeet/kytkenta_suojaus_ja_ohjaus/ul-opas-2010-englanti.pdf

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Commentator

Join Date: Jan 2017
Posts: 57
Good Answers: 1
#10
In reply to #9

Re: UL508A 3 phase color code?

04/27/2017 12:53 PM

funny you link to that doc

I also found that and read it intently

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#11
In reply to #10

Re: UL508A 3 phase color code?

04/27/2017 1:31 PM

Good Luck.

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Power-User

Join Date: Sep 2013
Posts: 152
Good Answers: 2
#20
In reply to #4

Re: UL508A 3 phase color code?

04/28/2017 3:49 AM

From the Siemens document you're talking about.

All ungrounded conductors should be BLACK

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#21
In reply to #20

Re: UL508A 3 phase color code?

04/28/2017 4:08 AM

I think the thread is about power conductors rather than control circuit conductors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Sep 2013
Posts: 152
Good Answers: 2
#22
In reply to #21

Re: UL508A 3 phase color code?

04/28/2017 4:37 AM

Section 7.2 Colour Coding for Conductors in Power Circuit

Section 7.3 was only added FYI.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#23
In reply to #22

Re: UL508A 3 phase color code?

04/28/2017 4:49 AM

Well, that's definitely not universal.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Sep 2013
Posts: 152
Good Answers: 2
#24
In reply to #23

Re: UL508A 3 phase color code?

04/28/2017 5:07 AM

What do you mean by universal?

This standard if for the North American market.

The 'U' in UL means 'Underwriters Laboratories'.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#25
In reply to #24

Re: UL508A 3 phase color code?

04/28/2017 5:21 AM

I used to run a UL508 shop, so I know what UL means.

In the NEC, the "high leg" (phase B) of a 240/3 system with center tap between A and C is mandated to be orange, as JRaef has already mentioned in this thread. Hence black is not universal.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#12

Re: UL508A 3 Phase Color Code?

04/27/2017 2:35 PM

Why n heck would it matter when supplying 3-phase power to a motor (as one example) There are other ways to pre-determine rotation.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Commentator

Join Date: Jan 2017
Posts: 57
Good Answers: 1
#13
In reply to #12

Re: UL508A 3 Phase Color Code?

04/27/2017 2:47 PM

It doesnt matter

Its for reporting purposes.

I need something that shows we are in compliance

My rotation is controlled in all my VFD,s anyway

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #13

Re: UL508A 3 Phase Color Code?

04/27/2017 2:59 PM

Surely the Electrician who installed the circuit produced a test record document?

Surely the periodic electrical inspection records for the installation show compliance?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jan 2017
Posts: 57
Good Answers: 1
#15
In reply to #14

Re: UL508A 3 Phase Color Code?

04/27/2017 4:26 PM

no an installation record does now show compliance with UL standard

..... Not a single clue in my mind why you would think that

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#16

Re: UL508A 3 Phase Color Code?

04/27/2017 5:15 PM

Surprisingly, in the US there is no standard color code for power conductors, just that they be identified at each termination. The only conductors that must be identified in reserved colors tend to be grounding/protective earthing/neutral related, or identified for special or reserved use such as ungrounded DC or unswitched AC.

That said, the IEC does specify single and three phase wiring color codes, as do many other countries' standards. However, the AHJ (Authority Having Jurisdiction) where the equipment is being installed is the ultimate judge of what is applicable. For example, NYC requires #12 copper as the minimum wire type (along with many other modifications to the NEC).

You will have to do your own due diligence to make sure your equipment will be accepted at its final destination.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#17

Re: UL508A 3 Phase Color Code?

04/27/2017 5:21 PM

RAMConsult is somebody I would listen too. There is your answer.

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18

Re: UL508A 3 Phase Color Code?

04/27/2017 6:58 PM

UL 508A does not designate color codes for power wires. The NEC does in some cases, i.e. Green for ground and Orange for B phase on 3 phase 4 wire Delta systems, but that would relate to the incoming and outgoing cables, not inside of the panel. Local utilities often have their own color code requirements, but again, that would not apply inside of a cabinet.

NFPA79, the compliance standard for "industrial machinery" has some conductor color rules in section 14.2.4, might be worth checking those out, but in there, phase conductors are all black unless there is something different about them.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#19

Re: UL508A 3 Phase Color Code?

04/27/2017 8:22 PM

Apart from code requirements, there is at least a common de facto practice of brown-orange-yellow for 480/3 systems and black-red-blue for 208/3. (Plus green for ground and white for neutral, if present.)

To be on the safe side, one assumes that all electricians are color-blind, anyway. Measure everything, even after lockout/tagout.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#26

Re: UL508A 3 Phase Color Code?

04/28/2017 8:44 AM

That is for 480V three phase, you know.

For 208V you typically use black / red / blue.

UL 508A is concerned about inside the panel only. I've seen them ignore a non-UL approved fitting if it is connected to a UL approved one that is the one that actually penetrates the enclosure. So when building a 508A panel we don't continue the color coding past the main disconnecting device, and that is actually the end users responsibility. In the panel the conductors are black with labels L1 / L2 / L3...or whatever, unless a customer specifically requests the color coding to continue throughout the panel in their specifications.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

DodgySolenoid (3); James Stewart (1); JPool (7); JRaef (1); Phys (1); PWSlack (1); RAMConsult (1); Rscott9399 (7); Tornado (4)

Previous in Forum: 2250kW 3.3kV Air-Cooled and Water-Cooled Drive   Next in Forum: Terminology

Advertisement