Changing from 3 Pole to 4 Pole Circuit Breaker

06/07/2017 4:55 PM

Good day

We have two 22KV/400 V Transformers (3 phases and neutral) supplying our Electrical equipments in the Plant. The Substation MCC arrangement is that, two Main Circuit Breakers (3 poles) are supplied from each transformer, plus 3 pole Bus Coupler in between (for changeover). The neutrals of the two transformers are linked.

From the very same substation or MCC, we are supplying another 2 substations, meaning those 2 transformers are feeding three substation (Main substation, Substation 1 and Substation 2). And all those Substations MCC arrangement are the same (2 Main Circuit breakers and a Bus Coupler).

And then from those MCC's, they are supplying different loads (Single phase loads, 3 phase loads, 3 phase + N Loads, etc).

NOTE: All loads Main Circuit breakers are 1, 2 or 3 poles, depending on the load.

At the Main Substation, Sub.1&2 are supplied from 3 pole circuit breakers, 4 core cable. The neutral core is just going through the Core balance or CT which is connected with the main C/B tripping coil and then goes to the substations (Sub.1&2).

The challenge is, when we have to do switch changeover (Closing the Bus Coupler) at Sub 1&2, we have to manually linked the neutral bus bar, and un-linked it to switch back to normal.

Now we considering to change from 3 poles to 4 pole Circuit breakers, so that we can have automatic neutral breaking.

The obvious fact is that, the MCC bus bar arrangement and the space will have to be considered due to the fact that the C/B sizes are different.

My questions: what technical factors including protections do i have to consider or the challenges during this exercise?

__________________
Dan Segami
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Changing from 3 pole to 4 pole circuit breaker

06/07/2017 10:42 PM

Since source of supply is same , and there is no parallel operation, there is no need to change the 3 pole ACB to 4 pole ACB.

This is my opinion.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Associate

Join Date: Oct 2009
Location: kuruman NC. SOUTH AFRICA
Posts: 51
Good Answers: 1
#2
In reply to #1

Re: Changing from 3 pole to 4 pole circuit breaker

06/08/2017 12:49 AM

Hey Ramvinod

Thanks for your opinion

Let me just be more specific. REMEMBER WE HAVE TWO 22KV/400 V Transformers WHICH SUPPLY THE MAIN SUBSTATION. So at Sub 1&2, we have 2 incomers, from Transformer 1 and from Transformer 2 , with the bus coupler. And also we have 2 neutral bus bars which are supplied from Transformer 1&2, and the 2 neutral bus-bars are coupled together with a piece of a bus-bar link, which is removable.

If you supply the Loads at Sub 1&2 with both Transformers/Incomers at the same time, with the Bars Coupler open, the neutral link must be removed, otherwise the Core balance/CT will trip the Main CB at the Main Substation because of the circulation of the neutral currents.

The only time when you have to connect the neutral link is when you supply the Loads from one incomer and close the Bars Coupler.

So we don't want that manual removing and connection of the Neutral Link that is why we considering the change.

__________________
Dan Segami
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#3
In reply to #2

Re: Changing from 3 pole to 4 pole circuit breaker

06/08/2017 1:07 AM

You are correct.

Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#4

Re: Changing from 3 pole to 4 pole circuit breaker

06/08/2017 1:11 AM

You need to change only the Buscoupler to 4 pole. So it will break or make the neutral provided that you must have interlock between two incomers and buscoupler to make sure any 2 breakers will ON at a time.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5

Re: Changing from 3 pole to 4 pole circuit breaker

06/08/2017 1:38 AM

Yes , the neutral at the bus coupler to be opened to avoid nuisance tripping due to core balance CT and earth leakage relay.

You have two options:

1) Replace the existing 3 pole breaker of bus coupler with 4 pole

OR

2) Provide one Contactor in the neutral bus removing the link between two neutral buses.

This contactor will be open when buscoupler is open and this contactor will be in closed when bus coupler is in closed.

Rating of the contactor can be 1/6 of the rating of bus coupler breaker.

The contactor poles are to be connected in parallel.

suppose bus coupler breaker is rated 2400Amps, provide 400 Amps , 4 pole contactor AC 3 duty.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Changing from 3 pole to 4 pole circuit breaker

06/08/2017 4:45 AM

How about a telephone conversation with the original switchgear manufacturer?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Changing from 3 Pole to 4 Pole Circuit Breaker

06/08/2017 6:03 AM

I wouldn’t alter the main board neutral. As you’re using E/L to feed the sub boards the sub board bus coupler should be 4 pole.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Changing from 3 Pole to 4 Pole Circuit Breaker

06/09/2017 9:33 AM

Please clarify the system, maybe I misunderstand. Diagram below shows system with two transfo with neutrals earthed by rods at each transfo. Each input to board has core balance CT with a relay which trips the input breaker. The resistances of neutral cable from transfo to switch board are r1, r2 respectively, probably r1 = r2 =r. If your transfos are 1 MVA, full load is about 1400 amps.

Assuming resistance r drops 1% phase (230V)volts at rated current, the voltage across r will be about 2 volts. A resistance of 2 ohms between earths would circulate 1 amp, which could be negligible.

According to your first paragraph, "the neutrals of the the two transformers are linked". In that case there is a definite neutral loop, my resistance Re ~= 0, and the circulating current could be 750 amp and a trip results.

My questions is...

If you supply all loads from one transfo with the switchgear neutral link IN, then there will be a circulating neutral current and a trip - unless there is something you did not tell us, like taking a neutral link out at de-energised transfo??

I feel that with neutrals joined only at transfos, the bus coupler could be closed to parallel the transfos briefly, as part of a "no-break" load transfer sequence to one transfo. With a neutral tie breaker and four pole main breakers (or neutral breaker on each transfo incomer) there could be an auto transfer, provided transfo core balance CT relays have time delay (surely must have delay else earth fault way down system takes out main breaker).

67model

Register to Reply
Associate

Join Date: Oct 2009
Location: kuruman NC. SOUTH AFRICA
Posts: 51
Good Answers: 1
#9
In reply to #8

Re: Changing from 3 Pole to 4 Pole Circuit Breaker

06/09/2017 12:18 PM

Looking at your drawing: The neutrals are linked before the CT or Core-balance not after the Core balance

__________________
Dan Segami
Register to Reply
Member

Join Date: Jun 2017
Posts: 7
#10

Re: Changing from 3 Pole to 4 Pole Circuit Breaker

06/10/2017 2:50 PM

If two or more LV(400V) sources feed the same bus and TN system of earthing is adopted in network, then the neutral of such incomers should be switched meaning 4P incomers to avoid incorrect operation of earth fault / leakage relay or other residual current device due to existence of parallel paths of neutral to earth currents. Neutral pole should be rated for the switchboard neutral bus rating.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

3ps (1); 67model (1); Alanvaderi (2); DannyD (2); PWSlack (1); ramvinod (2); TonyS (1)

Previous in Forum: Generator Size   Next in Forum: 138KV HLR ABB Breaker Fault Clearing Time

Advertisement