Good day
We have two 22KV/400 V Transformers (3 phases and neutral) supplying our Electrical equipments in the Plant. The Substation MCC arrangement is that, two Main Circuit Breakers (3 poles) are supplied from each transformer, plus 3 pole Bus Coupler in between (for changeover). The neutrals of the two transformers are linked.
From the very same substation or MCC, we are supplying another 2 substations, meaning those 2 transformers are feeding three substation (Main substation, Substation 1 and Substation 2). And all those Substations MCC arrangement are the same (2 Main Circuit breakers and a Bus Coupler).
And then from those MCC's, they are supplying different loads (Single phase loads, 3 phase loads, 3 phase + N Loads, etc).
NOTE: All loads Main Circuit breakers are 1, 2 or 3 poles, depending on the load.
At the Main Substation, Sub.1&2 are supplied from 3 pole circuit breakers, 4 core cable. The neutral core is just going through the Core balance or CT which is connected with the main C/B tripping coil and then goes to the substations (Sub.1&2).
The challenge is, when we have to do switch changeover (Closing the Bus Coupler) at Sub 1&2, we have to manually linked the neutral bus bar, and un-linked it to switch back to normal.
Now we considering to change from 3 poles to 4 pole Circuit breakers, so that we can have automatic neutral breaking.
The obvious fact is that, the MCC bus bar arrangement and the space will have to be considered due to the fact that the C/B sizes are different.
My questions: what technical factors including protections do i have to consider or the challenges during this exercise?
"Almost" Good Answers: