138KV HLR ABB Breaker Fault Clearing Time

06/09/2017 5:10 PM

When we had a maintenance test on 138KV HLR ABB breaker the breaker opens within a design specified time of 32 milliseconds. But when clearing the fault this breaker takes 130 milliseconds. One of the suggestion is that this might to do with the CTs in service, the remanence flux(residual magnetism) remained in the core. The solution would be the CTs need demagnetized removing the remanence.

Is there someone who knows some details in this theory and resolve this kind of situations, or do you have any suggestions.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: 138KV HLR ABB breaker fault clearing time

06/09/2017 7:54 PM

It depends upon how you did the testing. Did you perform the first test by applying a trip signal directly to the operating coil, then perform the second test by injecting a suitable trip current directly via the secondaries of the CTs? If so then the latency and pickup time of the relaying circuitry accounted for the extra time.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 3)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: 138KV HLR ABB breaker fault clearing time

06/10/2017 7:18 AM

Commonly, overcurrent relays have an inverse time characteristic. Relay takes longer to operate if fault current is smaller according to a designed curve.

Was the fault an actual fault? In that case you may not know the fault current. Maybe fault location allows an estimate.

Also breakers may take several cycles after contact separation to stop all current on a heavy fault.

Or was it a simulated fault. In that case the current must be drawn on the relay curve to find expected operate time.

If your breaker is at power source, relay will necessarily have longer delay, to allow a succession of downstream relays & breakers to operate first - so relay operate time is longer than breaker operation time.

Remanent flux depends on previous breaks - if last break was on positive current, you have no influence, for example, on the next break being positive or negative half cycle or on remanent flux reappearing.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: 138KV HLR ABB Breaker Fault Clearing Time

06/10/2017 11:57 PM

As pointed out by others , tripping of breaker under fault conditions depends on relay characteristics and master trip relay time and breaker trip time.

While maintenance check , probably you would have direct trip command with out any relay in the circuit.

Hence the difference.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: 138KV HLR ABB Breaker Fault Clearing Time

06/11/2017 11:41 AM

Remove the guano from it?

What did ABB have to say in response to the telephone calls that have already been made for help?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#5

Re: 138KV HLR ABB Breaker Fault Clearing Time

06/12/2017 5:38 PM

Clearing a fault includes the time to interrupt the flow of current across the breaker contacts. This is a function of the breaker, an air breaker will take longer than a vacuum breaker, for instance, because you have to cool and extinguish the arc.

You need to know this to coordinate upstream and downstream devices. You have the response of your protective relay, the time it takes to release the trip mechanism of your breaker, the time it takes for the contacts to physically separate to the design interrupting distance, and the time it takes to extinguish the arc, stopping the current flow.

Total clearing time would be at the design rating of the circuit breaker, a smaller fault should clear sooner, but you need to design your coordination for worst case.

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); PWSlack (1); RAMConsult (1); ramvinod (1); rwilliams (1)

Previous in Forum: Changing from 3 Pole to 4 Pole Circuit Breaker   Next in Forum: Wonderware: Pumps on Drive Control Off

Advertisement