Generator Size

06/05/2017 6:20 PM

Hi, I would just like to ask what is the correct generator size if I have 3 loads, 70 kVA each. For 220 Volts, and 440 Volts supply. It is three phase connected, and direct on line.

Register to Reply
Pathfinder Tags: Generator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: Generator Size

06/05/2017 7:31 PM

It all depends on the 70kVA loads. Load starting requirements? If the 70 kVA loads were all carbon comp resistors, then a 210 kVA genset would be fine. Not so if you were driving piston style refrigeration compressors. You'll need some transformers too.

Register to Reply Score 1 for Good Answer
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Generator Size

06/06/2017 4:02 AM

That would depend upon whether all three loads want starting simultaneously or whether a sequence-start activity is desired, which detail has been withheld from the forum.

However, the forum really doesn't need to get in the way of telephone discussions between the original poster and generator suppliers, which is by far the quickest and easiest way of obtaining equipment to solve this problem.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Generator Size

06/06/2017 1:16 PM

What is this "telephone" device you speak of? How does one interface with it?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#4
In reply to #3

Re: Generator Size

06/06/2017 1:55 PM

Absolutely hilarious!

He needs a generator that is larger than 210 kVA to be sure, since nearly any load hooked up to this will surge a bit on start.

How much larger clearly depends on the specifics of the three load devices.

If they happened to be single phase motors, that is one thing. Three phase motors or even DC motors, quite another, but I would probably start with 100% overage (420 kVA) for starters and see if that works.

You can't put silly putty back in a bottle very easily without making thin strings of it.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #3

Re: Generator Size

06/08/2017 8:24 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jun 2017
Posts: 2
#5

Re: Generator Size

06/06/2017 5:58 PM

Thanks for your replies.

Just another, if the three loads are connected in single phase, direct on line because no transformers will be used. What size of genset should be considered? How to compute that one?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Generator Size

06/07/2017 3:22 AM

It is exactly the same, as specifics of the sequence of starting and the nature of the loads are STILL withheld from the forum.

It might be a different piece of equipment, now being single phase, and the rating is just the same.

How did those telephone calls with the equipment suppliers go, by the way? The forum always has opportunities for learning from subscribers that post the outcome of their deliberations.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Participant

Join Date: May 2017
Posts: 2
#10
In reply to #7

Re: Generator Size

06/07/2017 11:57 AM

telephone calls with equipment manufacturer - genset manufacturer will refer you to their distributor / contractors. These guys will quote you a price for installation. They are not engineers and have no idea of application theory.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #10

Re: Generator Size

06/08/2017 8:15 AM

That's nonsense.

<...you...> It's not needed here so there won't be any outgoing calls from this location!

They might quote the original poster, were that individual to ask, and that quotation will provide the answer to that individual's original question. However, the original poster STILL needs to discuss with the recipient(s) of the call(s) what the details of the loads are and any sequential-starting, which is STILL unforthcoming to the forum. Perhaps that individual will have a better chance with the suppliers directly.

Just because a quotation has been received doesn't place one under any obligation to purchase, and it can be a useful learning exercise that does not warrant denial.

Under those circumstances:

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8
In reply to #5

Re: Generator Size

06/07/2017 9:32 AM

The result will be the result of the telephone conversation with your vendor, you still need to allow for start up surges of each load, especially when the impedance is complex, not simply resistive.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#6

Re: Generator Size

06/07/2017 12:20 AM

Your question is not clear. What is meant by 3 loads, 70kVA each for 220 volts , and 440Volts?

I assume it is 3 loads of 70kVA , 3 phase 440 Volt.

Hence 3 x 70 = 210 kVA

If we consider the Generator works at 80% efficiency, then you need 262.5kVA Generator. ( 210kvA/0.8)

Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1375
Good Answers: 105
#11
In reply to #6

Re: Generator Size

06/07/2017 5:31 PM

Plus the nature of the load is important, your generator has to provide power (HP or kW) to accelerate the load. A smaller generator will start variable torque loads, may not start constant torque loads. You must have enough accelerating torque to beat out the overcurrent protection for your motor, to get past starting current.

You have kVA specified, but you really need to know kW and/or power factor, then you can assume an 80% Power Factor and size the kVA of the generator as (210kW/80%). The kW is the rating of your engine (prime mover), the kVA is the rating of the generator.

Direct On Line starting with a low end (cheap) voltage regulator has failed when the generator was 3 times the size of the motor being started, though don't know if centrifugal or positive displacement pumps. OP I think gave up.

See this thread for tale of woe

Compensating For An Undersized Generator http://cr4.globalspec.com/thread/111965

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #6

Re: Generator Size

06/08/2017 8:21 AM

That would only be true if the loads were to exclude the prospect of three 70kVA motors starting simultaneously. The original poster STILL has not excluded that prospect from this forum's deliberations.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: Generator Size

06/07/2017 10:10 AM

Your "information" is insufficient and inconsistent. Please describe correctly what you have/want.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #9

Re: Generator Size

07/07/2017 4:50 AM

...directly to equipment vendors, by telephone in the first instance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alanvaderi (1); BayouFun (1); bluemanjunkie (1); Brave Sir Robin (1); James Stewart (2); JRaef (1); PWSlack (6); rwilliams (1); Tornado (1)

Previous in Forum: Phase Indication Lamp Flickering in HT Panel   Next in Forum: Changing from 3 Pole to 4 Pole Circuit Breaker

Advertisement