How to Optimise Solar Energy During Load Shedding Period

06/11/2017 2:45 PM

I would like to know how to optimize solar energy production and consumption during a load shedding period by connecting the optimum load to the solar system. i.e. if I have a 10kW solar hybrid system with a small battery back up, and when grid is available, I can harvest maximum solar energy by exporting to grid the balance energy. However, in the event of grid failure, the solar system will function as off grid mode and solar will be used for internal consumption. But, in this case if solar output comes down, then I need to provide a load shedding scheme to make the internal consumption equal to the solar generation. My question is.. whether any such load shedding scheme using a PLC or controller is available in the market? I will appreciate experts' feedback.

Register to Reply
Pathfinder Tags: solar energy optimization
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: How to optimise solar energy during load shedding period

06/11/2017 3:57 PM

<...in the event of grid failure...if solar output comes down...make the internal consumption equal to the solar generation...>

Er, ah, um, this is illogical. When the equipment is off-grid then, regardless of actual sunshine levels, the load consumption in the absence of storage will always be equal to the solar generation less, of course, any conversion losses inherent in operating the equipment! The only way it could be more involves using up storage, such as that contained in the <...battery...>.

These fora usually encourage users to do their own market research using search engines such as Google (usual disclaimer).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: How to optimise solar energy during load shedding period

06/11/2017 5:15 PM
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: How to optimise solar energy during load shedding period

06/12/2017 3:46 AM

No wonder 16.6kW is needed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jun 2017
Posts: 3
#11
In reply to #2

Re: How to optimise solar energy during load shedding period

06/12/2017 2:34 PM

Thanks for recommending the site and it is really informative.

However, I will appreciate if you could recommend a cheaper model for load shedding controller for a 10kW solar hybrid power system.

Thanks.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#12
In reply to #11

Re: How to optimise solar energy during load shedding period

06/12/2017 8:38 PM

So why exactly can't the sources be turned off or put into a non power producing standby mode?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: How to optimise solar energy during load shedding period

06/13/2017 5:47 AM

The cheapest would be a simple voltmeter and a bank of on/off switches...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#14
In reply to #13

Re: How to optimise solar energy during load shedding period

06/13/2017 8:56 PM

I'm getting the strong impression that actually turning off the power sources to keep them from overloading the drain side of the system is not something he wants to discus.

'Ignore it and it and people will stop asking about it.' sort of thing.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #14

Re: How to optimise solar energy during load shedding period

06/14/2017 9:15 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3

Re: How to optimise solar energy during load shedding period

06/11/2017 7:29 PM

So why can't you just turn the solar power supply off or just use what part of its output you need?

Pretty sure they don't blow up of they are not running at peak power output every second the sun is shining.

Just because you have the capacity to do something doesn't mean you have to use all that capacity all the time. Especially with solar power.

Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#4

Re: How to Optimise Solar Energy During Load Shedding Period

06/11/2017 9:46 PM

This is simpler, if you add more batteries or storage modules as buffer system.

Register to Reply
Commentator

Join Date: May 2011
Posts: 73
Good Answers: 3
#5

Re: How to Optimise Solar Energy During Load Shedding Period

06/12/2017 2:57 AM

This is an interesting problem with some complications. We have solar, diesel generators as well as grid based electricity. Due to local municipal regulations we block any energy going back into the grid. (Worst case, we will get charged for feeding into the grid.) We therefore generate as much as we can, throttle if we go over demand and supplement with the grid.

If the grid goes down for any reason - load shedding (reason for the diesel generators) or grid maintennance, we have to stop using solar energy as this creates a safety risk for anyone who might be working on the supposed to be "dead" circuit. This goes against my intuition, but our electrical specialists and local municipal regulations are adament.

Check with your local municipal authorities how they address this issue and stay safe.

Andries

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9
In reply to #5

Re: How to Optimise Solar Energy During Load Shedding Period

06/12/2017 10:12 AM

Clearly, your inter-connect may not be appropriate. It is supposed to isolate the solar/diesel gen-sets from the grid source during outage of the grid, so no "back-feed" takes places. That is the hazard.

You could install some extra light bulbs around if you just have to "waste" some power.

More batteries in the battery bank makes good sense, also.

So during normal use, are you mostly using your local sources, then pulling in just that power from the grid that is needed for full production?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#7

Re: How to optimise solar energy during load shedding period

06/12/2017 4:28 AM

Depending on the climate where you live, you could consider using excess solar power to either add or remove heat from a large thermal sink, perhaps a phase change material. Heating up water in a well insulated extra (electric) water heater would be an easy fairly cheap and useful load in which to shed. Making ice, or chilling brine might also be useful, but would be more complicated in reaping benefits.

If you have a swimming pool, you could shed a huge amount in there heating or cooling the water.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: How to Optimise Solar Energy During Load Shedding Period

06/12/2017 7:26 AM

If you look at the performance curve of a solar panel, in 1000W/m2 sunlight, it has an DC open circuit voltage of about 37 and optimum max power voltage of about 30.

So long as the inverter producing AC adjusts to its AC load with normal voltage e.g. 230, there is no reason it should not feed load below its capacity.

The problem is that systems intended to be applied by the million to homes MUST disconnect automatically from Grid and shut down if the Grid section becomes isolated. If the load on the isolated section were less than solar capacity, it could continue running - but there is no means to reconnect it without "out of sync" closure, possible damage to all the solar power and making further problems for restoring normal power - one of which is the danger to personnel due to supposedly "dead" sections still being live. Remember that these systems have a contactor to isolate the inverter, but there is no contactor to isolate the house load.

To get this behaviour, the usual method is to design the inverter so it will inherently shift off frequency without dominant Grid power and shut down quickly on "out of frequency limits" fault.

This does not preclude systems which isolate the in-house load from the Grid, so long as they disconnect from Grid just as effectively - but the inverters have to be different.

Usually, the capacity of the Grid infeed is ten times that of any solar capacity so there is little demand for load isolation - it would not work unless excess loads could be switched off instantly for which equipment and wiring is expensive & not viable unless there is a vital load.

You only mention a PLC - but the biggest cost is probably the necessary breakers, new distribution board and re-wiring and detection gear.

Register to Reply Good Answer (Score 2)
Participant

Join Date: Jun 2017
Posts: 3
#10
In reply to #8

Re: How to Optimise Solar Energy During Load Shedding Period

06/12/2017 10:55 AM

Thank a lot for your detailed reply.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15
In reply to #10

Re: How to Optimise Solar Energy During Load Shedding Period

06/14/2017 5:06 AM

Having thought some about your problem, the following may be your best option..

  1. Feed a suitable inverter direct from your battery to power the vital loads, which may require new circuits/distribution board for these loads. Provision for bypass to mains may be automatic/short break/uninterruptible [UPS]/manual [move plug to another socket!!] according to risk & cost.
  2. Hand switching of other necessary circuits to a supplementary,hand-energised, inverter, according to battery capacity and practicality - remembering that your actual experience may modify what is "practical" - start "simple/small", which is less cost & time.
  3. Remember that some kinds of loads, particularly refrigerators may be difficult to start from an inverter, even if other equipment does not mind voltage dips. Also friges start when they need to - not to suit your sensitive power supply. It may be possible to use for vital stuff, a domestic "no-motor" frige (resistive), which does not have a starting surge - caravan units may even work from DC direct.
Register to Reply
Register to Reply 16 comments