A 100 kVA 11/0.4 kV transformer will have 5.2 Amps as HT full load current. So, 5.2 amps or next higher standard rating will be drop out fuse rating. So this shall be the drop-out fuse rating or fuse link current rating?
A fuse is there to protect the CABLE. So, as the wiring installation detail has been withheld from the forum it would be unreasonable to expect a valid answer from it!
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
And it does protect cable by providing for interruption when the transformer attached downstream (these should usually be found on the service pole, correct?) will have a current such the range {Irf, I3} values (the in-rush and fault currents) will include the rated value of the fuse. If the fuse is outside these limits (usually I3 is about 3-6 times the in-rush) then it will be inappropriate for use, as the established arc upon failure may be able to sustain itself for an undue (indefinite) period of time.
__________________
If it ain't broke, don't fix it. Just build a better one.
It is a mystery to this reader why anyone would intentionally install a fuse assembly that is capable, on rupture, of producing a self-sustaining arc, and therefore a potential learning exercise therefrom.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856