Anonymous Poster #1

Bus Bar Current Collect Wearing Out Quickly

07/25/2017 1:51 AM

Dear All,

I am no means a electrical guy but our current collectors on 380 v bus bar and wearing out too soon. We had replacement them 2 weeks back and now again they are completely worn out. What can be the reason. Please help us solve this issue.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 2:07 AM

Are you talking about current transformers with an open secondary?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Off Topic
Anonymous Poster #1
#2
In reply to #1

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 2:15 AM

No . I am talking about the powerrail for the cranes.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #2

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 4:51 AM

Oh. Too bad that was not described well in the first post.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Off Topic
2
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#14
In reply to #2

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 11:00 AM

Sounds like the current collectors were not set up in accordance with OEM guidelines.

You need to have a one-on-one, face-to-face meeting with whomever it is that services and certifies your cranes, explaining to them about what you are experiencing and why they are going to fix the problem.

If the thing was set up for a "clean" shop, and this is a smelter, or very dusty gritty environment, you probably do not have sufficient dust booting on the bus bars to prevent contamination damage.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 3:15 AM

What did the crane manufacturer say in response to the telephone call(s) that have been made to it on this topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 3:40 AM

There could be several reasons.....corrosive environment, overloaded, improper wiring, crane motor failing, damage to structure in some way, bad connection.....We would need good close-up pictures, ratings and current measurements, to even start....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 3:52 AM

...and so would the crane's manufacturer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 3:53 AM

Were OEM parts installed, with warranty, or did the replacement parts "fall off the back of a lorry"?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 4:38 AM

It is troubling that <...no means a electrical guy...> is replacing <...current collectors on 380 v bus bar...> with all the safety implications that surround it.

One of the possible reasons that the things are wearing out quickly is installation otherwise than in accordance with the OEM's instructions. Those instructions cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#9

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 4:56 AM

What current are the bus bars rated at?

What current are the collectors rated at?

What current do the collectors carry: steady state and inrush?

Do the bus bars show any signs of damage/wearing out?

How long did the original collectors last?

Who manufactured the original collectors? Part numbers?

Who manufactured the replacements? Part numbers?

I am also no means an electrical guy.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Reply
Commentator

Join Date: Aug 2010
Posts: 56
#10
In reply to #9

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 5:24 AM

What current are the bus bars rated at?

Not sure

What current are the collectors rated at?

200 amps

What current do the collectors carry: steady state and inrush?

Inrush

Do the bus bars show any signs of damage/wearing out?

One of the lines showing a bit of damage

How long did the original collectors last?

This is a fairly new plant May be around 6 months

Who manufactured the original collectors? Part numbers?

Wampfler

Who manufactured the replacements? Part numbers?

I am also no means an electrical guy.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 5:28 AM

Here they are. Pick up the phone!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2010
Posts: 56
#12
In reply to #11

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 6:07 AM

Already called them before . They might visit our site next week

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #12

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 6:12 AM

Then phone them again and convert <...might...> into "will", FFS!

  • What is the matter with people these days (rhetorical question - NNTR)?

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#15
In reply to #13

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 12:00 PM

"

  • What is the matter with people these days (rhetorical question - NNTR)? "

Good chance that because so many use either text speak or technical abbreviations that are not universally know people have no clue what they are talking about and they ignore the advice given due to it's cryptic conveyance of anything useful.

(FFS, OMG, NNTR, STFU, LOL, WTF, FBI, SCr, HFe, CIA, NBS, PBS, MAGA, NIBY!)

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#16
In reply to #15

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 12:12 PM

You left out CNN, and NBC.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #16

Re: Bus Bar Current Collect Wearing out quicky

07/26/2017 6:39 AM

WTF...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
3
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#17

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 12:39 PM

I agree with PWSlack : the manufacturer, it will be the best address. However, I think, usually the problem it is in brushes: the low pressure on the busbar- high contact resistance- or inadequate brushes.

__________________
Julius
Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#18
In reply to #17

Re: Bus Bar Current Collect Wearing out quicky

07/25/2017 2:30 PM

Yes it could be a buildup of corrosion and carbon on the bars, possibly pitting....probably need to be cleaned....might try some conducting grease...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #18

Re: Bus Bar Current Collect Wearing out quicky

07/26/2017 6:41 AM

Possibly, though the forum cannot see the problem as well as the original poster, who seems to have vanished. Perhaps there are too many texts, emails and WhatsApps to send to maintain an interest here; who knows (rhetorical question - NNTR)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#26
In reply to #20

Re: Bus Bar Current Collect Wearing out quicky

07/27/2017 11:07 AM

Look carefully PWSlack - unusually for anonymouse posters, "plckid" has emerged.

Reply
Commentator

Join Date: Aug 2010
Posts: 56
#21
In reply to #18

Re: Bus Bar Current Collect Wearing out quicky

07/26/2017 8:15 AM

We have checked for corrosion but we had found of the lines colour seems to be a bit of black as compare to others. I dont know why .Also the power rails are galvanized . Just one question ,how do they align these power rails. Is there any instrument for this since the manufacture thinks the rails are not aligned and the current collectors are wearing out soon.

Reply
Commentator

Join Date: Aug 2010
Posts: 56
#22

Re: Bus Bar Current Collect Wearing out quicky

07/26/2017 8:31 AM

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#23
In reply to #22

Re: Bus Bar Current Collect Wearing out quicky

07/26/2017 9:33 AM

Nah, it is probably something in your local environment that is causing black oxide.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#24
In reply to #22

Re: Bus Bar Current Collect Wearing out quicky

07/26/2017 5:47 PM

Check your spring tension, they have probably relaxed, and with poor contact, may run hotter and relax sooner.

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#25
In reply to #24

Re: Bus Bar Current Collect Wearing out quicky

07/27/2017 8:53 AM

Yeah, when my contacts are weak, I run hotter, and want to relax sooner also.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#27
In reply to #22

Re: Bus Bar Current Collect Wearing out quicky

07/27/2017 11:26 AM

Some thoughts.....

  1. "Rough handed" operator engages collector with too much force.
  2. Collector brought into contact with rail at start current when it should be off-load.
  3. The busbar damage should have been repaired when collector was replaced.
  4. The manufacturer will know what busbar alignment tools and methods are adequate.
  5. The manufacturer might now sell you busbar dust covers which should have been specified for your environment?
Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#28

Re: Bus Bar Current Collect Wearing Out Quickly

08/04/2017 7:18 PM

Check the quality of the material. That is always the problem.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Reply to Forum Thread 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); 7anoter4 (1); Anonymous Poster (1); James Stewart (4); plckid (4); PWSlack (8); Randall (1); rwilliams (1); Simon Wan (1); SolarEagle (2); tcmtech (1); Tornado (2)