Two 110VAC Supply in One Multicore Cable

12/11/2017 7:59 PM

Hi,

I need to run two power cables to a panel and the panel has only one hole for cable gland. The panel is certified and new holes cannot be made only with re-certification. Is it possible to run two 110 VAC power source in one multicore cable? Will this violate some rules? Thanks.

Milan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Two 110VAC Supply in one Multicore Cable

12/11/2017 8:59 PM

Yes. No. You're welcome.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 4)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Two 110VAC Supply in one Multicore Cable

12/11/2017 10:09 PM

Certified? is this a hazardous area distribution panel?

Why two sources? Is this for current sharing because the conductors are too small or a source-transfer application between two different independent supplies?

Multicore cables are generally for control logic, not power. What standards are you working too, is this an American installation or somewhere else?

Please provide more information.

__________________
jack of all trades
Register to Reply
Participant

Join Date: Dec 2017
Posts: 4
#3
In reply to #2

Re: Two 110VAC Supply in one Multicore Cable

12/11/2017 10:19 PM

Hi Jack,

The panel is hazardous area certified for explosion proof. We need two source supplied by two UPS incase one fails there is no down time. It is not in America but we are following American standards, the panel is supplied by US company.

I have never done this before as well and am not sure if it can be done. However, if it cannot be done, could you please explain why it cannot be done? I need to convince the people who are trying to go this path to not do it. Thank you.

Milan

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #3

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 3:51 AM

<...two UPS incase one fails...> Are these cables to be supplied from two fuses, in case one blows, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #3

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 7:35 AM

<...explosion proof...no down time....> Then the panel has to be functioning correctly before it is installed and energised, for no testing or modification will be possible once energised. That is the drawback with <...explosion proof...> equipment over other methods of achieving safety of electrical equipment in hazardous atmospheres. Incidentally, it will prove possible to install it only using non-sparking hand tools, in that case.

<...have never done this before...> If no training has been completed, then either carry out training beforehand or delegate the task to someone who has been trained. This is a specialised field and not one for the uninitiated.

Other things of note:

  • It is not possible to have humans inside ATEX hazardous area zone 1, as the facility would face enforcement and/or prosecution for non-compliance on health & safety grounds. So the panel goes either into ATEX hazardous area zone 2 or the safe area; if going into the safe area then a hazardous-area-certified unit is not required, and best dispensed with.
  • If the ATEX hazardous area zones are large, then the facility has a major materials containment problem that requires addressing immediately on health & safety, environmental and economic grounds.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
6
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Two 110VAC Supply in one Multicore Cable

12/11/2017 11:45 PM

From a "best practices" standpoint, do you really want to carry your backup source in the same cable as the main supply? Typically they are brought in in separate cables/conduits/trays so that a fault or damage to one source will not impact the integrity of the other.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 6)
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#5

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 1:14 AM

I cannot see any issue with using a multicore cable as long as it is appropriate for the power transmission, which means voltage rated, current rated, and following any other necesary standards for this application.

The only problem you may have could be that multicore cables have worse heat dissipation, so compared with single core cables, you may need higher cross section, incurring in more expensive cables and maybe some dificulties to get the multicore cable trough the core.

If it does not fit, you can use military rated cables, aa long as you can afford it!

__________________
Building the future!
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 1:51 AM

I don't know if any regulations applying to the US that would forbid you punching another hole in the box. Listing of a control panel has no bearing on the number of holes in it, other than the fact that all holes must have something in them, either a cable gland, conduit or a plug. But neither is there anything prohibiting you from having multiple circuits in the same cable. I have used cables with up to 42 separate circuits in the same cable.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Participant

Join Date: Dec 2017
Posts: 4
#7

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 2:54 AM

Thanks guys. My management has agreed not to use multicore cable for the UPS supply and proceed with drilling holes and recertification as required by our supplier.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 2:59 AM

Who gets stuck paying for that?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Dec 2017
Posts: 4
#9
In reply to #8

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 3:07 AM

Above my pay grade. LOL

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#13
In reply to #7

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 1:22 PM

Good. This is the best solution in this case given the information presented.

__________________
jack of all trades
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#10

Re: Two 110VAC Supply in one Multicore Cable

12/12/2017 3:47 AM

US codes not my space, but if that was for underground coal mining in Aus, would need re-cert for any modification to the level of seal. Any new hole = re-cert.

Re-cert testing of a modified unit usually cost more than obtaining an alternative certified unit that would suit.

Congrats for taking the conservative approach and getting the testing done.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#14

Re: Two 110VAC Supply in One Multicore Cable

12/12/2017 2:40 PM

Interesting. Congrats on the decision to run two supplies separately, and re-certify the enclosure.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#15

Re: Two 110VAC Supply in One Multicore Cable

12/13/2017 8:22 AM

Not sure what you mean by "certification", but if this is a UL 508A inspected panel, the new holes, if filled by a gland with correct rating for the area, are allowed. Our in plant shop built UL 508A panels are often inspected before the holes are even made. It is also common to get UL 508A inspected panels for our process skids, built by another shop of the end customer's choosing, not our own in plant shop, with no holes. We add them as needed to run the skid wiring. UL 508A still applies to the panel.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Active Contributor

Join Date: Feb 2015
Location: Greater Memphis, Tn. Metro
Posts: 20
#16

Re: Two 110VAC Supply in One Multicore Cable

12/13/2017 8:47 AM

http://www.cooperindustries.com/content/dam/public/crousehinds/resources/pdfs/other-pdfs/crouse-hinds-codedigest2014.pdf

__________________
Dave Oliver
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

daveoliver (1); Ivanov327950 (1); jack of all trades (2); James Stewart (1); JRaef (1); Just an Engineer (1); Phys (1); PWSlack (2); RaiMilan (3); RAMConsult (1); Tornado (2)