Anonymous Poster #1

AHU/ACCU UNIT

03/05/2018 1:18 PM

This is a duty and a standby separate AHU & ACCU unit.
a) Why can't load both the units to 50% instead of operating it one as a duty and the other as a standby unit?
b) Which method produces better efficiency?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: AHU / ACCU UNIT

03/05/2018 2:02 PM

Aa) Because that's the way it is designed. 2*100% gives redundancy in case one of the units fails for whatever reason.

Ab) 2*100%, obviously.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: AHU / ACCU UNIT

03/05/2018 4:29 PM

The more fully any individual unit is loaded, the better the moisture removal.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: AHU / ACCU UNIT

03/05/2018 8:55 PM

It's set up this way so there is no down time when a unit needs repair....the standby unit should be tested at regular intervals....it's not about efficiency, it's about critical application...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#4

Re: AHU / ACCU UNIT

03/06/2018 10:50 AM

The units typically run more efficiently when near rated levels. The idle unit can fail due to lack of use. I would suggest that you alternate use of the units on a regular basis as in 1 week A, then one week B and so on. It should actually extend the life of the backup unit. The only issue I would see is there is likely to be autostart controls for the backup unit and if you alternate unit operation you would also need to be able to switch the autostart controls between units as well.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: AHU / ACCU UNIT

03/06/2018 11:28 AM

It is sometimes of advantage to advance the "run hours" [RH] of the principal unit in advance of the backup one, so that the backup one has rather less "run hours" than the principal. That way, the unit with the longer RH can be taken down for periodic planned maintenance [PPM] as a priority over the other, with the backup accumulating more RH than usual while the other is under PPM. That way, if there is a delay with the unit under PPM for whatever reason, the other can be used in the knowledge that there are spare RH to use up before the second overtakes the one under PPM; PPM on the units can be staggered to optimise the resources available with which it is to be carried out.

Which has nothing to do with unit efficiency and everything to do with resource efficiency.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Jpfalt (1); PWSlack (2); SolarEagle (1); Tornado (1)

Previous in Forum: Oil Seal Mfg   Next in Forum: This is an Interesting Concept

Advertisement