Heat Run Test of Power Transformers

05/09/2018 3:02 AM

In heat run test the voltage is applied to primary and secondary is shorted.

What will be the effect if we short the primary and voltage is applied to secondary.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: heat run test of power transformers

05/09/2018 4:11 AM

One way to find out would just be to try it.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: heat run test of power transformers

05/09/2018 8:18 AM

None. On method draws more current than the other, the other uses higher voltage than the other.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Heat Run Test of Power Transformers

05/09/2018 10:42 AM

If the circuit protection equipment is set-up and working, the transformer will survive the experience undamaged.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #3

Re: Heat Run Test of Power Transformers

05/09/2018 9:53 PM

Not necessarily. When used as a type/design test, a heat run may uncover uneven cooling and/or unanticipated hot-spots that can lead to insulation charring, outgassing, and premature dielectric failure.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Heat Run Test of Power Transformers

05/10/2018 2:34 AM

Ah! "Testing to destruction." Understood.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#4

Re: Heat Run Test of Power Transformers

05/09/2018 5:32 PM

Primary and secondary of a transformer are application related.

Usually the branch powered during all transformer tests is the one you have test equipment for, as a transformer can be used in different configurations.

As an example, if you have a transformer from 48Vac to 400Vac, tests are very likely to consist on powering the secondary 400Vac side, mostly because 400Vac power equipment is more common than 48Vac equipment.

__________________
Building the future!
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #4

Re: Heat Run Test of Power Transformers

05/09/2018 10:37 PM

The voltages involved in a factory heat run are not directly related to the primary or secondary voltage, they are based on forcing the rated full load current through one winding while short-circuiting the other. The input voltage is slowly increased until the current on the shorted side reaches the desired current, the actual voltage is recorded as a check variable.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2016
Posts: 16
Good Answers: 1
#8

Re: Heat Run Test of Power Transformers

05/10/2018 8:35 AM

I supervised multiple heat run tests of generators, in the past. Of course we tested the transformers, as well, because we shorted the transformer output (after disconnecting the transmission lines, of course.) We could control the generator current with the manual voltage regulators.

Control of current and measurement of temperature would be VERY HARD, from the secondary side.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#9

Re: Heat Run Test of Power Transformers

05/10/2018 8:44 AM

A suitable voltage is applied on the high voltage side to ensure a full load current in shorted secondary.it is much easier to ensure a higher current on lower voltage side.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10

Re: Heat Run Test of Power Transformers

05/11/2018 6:45 AM

There is no difference in the heating if you set rated current in the appropriate winding.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers: