Trench Heating

11/23/2018 11:12 AM

Hi guys,

just wondering whether someone could lend a hand on working out how much extra heat I can extract from a 15mm copper heating pipe if I added aluminium grilling to the system.

My understanding that a 1m length of 15mm copper will give off 40w of heat if the temperature difference between room and flow is 55 degrees Celsius.

I need to design my own trench heating as ready made units will not fit. My thinking was copper pipe with aluminium fins to increase the surface area. I will be using a 6 pipe loop. The size of the alluminium grill will be 150mm x 150mm x 0.5. How much more heat could I extract if over the meter I use 100 of these fins?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Trench heating

11/23/2018 11:45 AM

Depends on cfm of air flow, and gpm of water flow, and incoming water temperature supply...but you seem to be approaching this in a bassackwards way....First you would determine the btu load requirement for heating the space, then you design the delivery system.....in any case here is a calculator for convection heating...

...pure convection heating calculator....

https://www.engineersedge.com/calculators/heat_sink_convection_with_fins_calculator_10048.htm

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2018
Posts: 4
#2
In reply to #1

Re: Trench heating

11/23/2018 12:19 PM

Hi solaredge,

The client is a friend of mine and he doesn’t want radiators. I’ve been told the space I can use for these underfloor radiators, so there is only so much pipework I can fit in.

The room requires a heat load of 1.5 kw or 5118 btu’s. I only have space in two areas for 12m of 15mm copper pipe so around 480w of heat, not enough, so from an educated guess of modern radiators and trench heating with grills I said I’ll need to add fins. From an engineers point of view would adding fins along the length of the pipe increase heat transfer from the water to the room?

I get your point on the flow of water through the convector, I will be able to adjust the flow rate once installed.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Trench heating

11/23/2018 1:48 PM

There are many products and strategies for hydronic radiant floor heating that include finned pipes....

Steam/Hydronic Heater Element, Length 3 ft., Tube Size 1-1/4 In., Tubing Material Steel, Fin Material Steel, Inlet/Outlet NPT 1-1/4 In., Max. Fluid Temp. 650 Degrees F, Max. Pressure 660 psi, Output @ 2 PSI Steam 1600/2250 BtuH, Max. Heat/Linear Ft. @ 150 F Water Temp. 720/1010 BtuH, Max. Heat/Linear Ft. @ 160 F Water Temp. 850/1190 BtuH, Max. Heat/Linear Ft. @ 170 F Water Temp. 975/1370 BtuH, Max. Heat/Linear Ft. @ 180 F Water Temp. 1080/1640 BtuH

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #2

Re: Trench heating

11/26/2018 7:16 AM

<...would adding fins along the length of the pipe increase heat transfer from the water to the room?...> Naturally, though how much depends upon a range of factors, not least of which is the air flow past those fins.

There are also off-the-shelf electric underfloor heating systems available for a range of applications.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#16
In reply to #15

Re: Trench heating

11/26/2018 7:25 AM

Worth mentioning, the fins that I am familiar with had 2 opposing edges folded so that the butted up to the next fin. This formed a channel to encourage convection air flow through the fins rather than relying on radiation.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: Trench heating

11/26/2018 10:24 AM

Good point. Corrugated ones may also be found.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Trench heating

11/23/2018 2:15 PM

"Trench" heating? Will this system be buried. or just under the floor?

Some issues I see with this.

1. Energy loss. How will the water be heated? What is the cost per BTU per unit volume to heat the water? How will you pump (move) the water through the system?

2. System heat loss. As heat is transferred out of the water and into the room the useful radiation will diminish. Flow (velocity) will be critical, as in high.

3. System cost. Would it be less expensive over time to simply install electric convection heat, without the cost of a massive water heater, copper pipe, aluminum fins and pump?

Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#5

Re: Trench heating

11/24/2018 2:28 AM

Hydraulic systems are the normal method of heating homes in the UK. Pumps generally use under 100W, and have a flow rate of 5-20 litres a minute depending on plumbing complexity.

Two ways to increase heat transfer are increasing the surface area or increasing the flow of air.

You could use 10mm pipe with a manifold each end to get larger surface area.

You could add PC fans to assist airflow: these can be almost silent if running slowly, but be able to boost the heat transfer for warming up. Many newer emitters have some form of fan fitted so they work with heat pumps. A well insulated house can have a flow temperature of 40C and keep the space at 20C.

__________________
Madness is all in the mind
Register to Reply
Participant

Join Date: Nov 2018
Posts: 4
#6
In reply to #5

Re: Trench heating

11/24/2018 3:24 AM

Thank you for all the input. I’ll be using a 43 Kw vaillant boiler https://www.vaillant.co.uk/homeowners/products/ecotec-exclusive-with-green-iq-combi-24448.html

After giving it thought and exposing the joists, it’s a house built in 18th century, I do not have enough room to get adequate heat into the area, which is a shame. Going for standard panel and old style school radiators as a feature piece.

thanks for the input guys.

Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#7

Re: Trench heating

11/24/2018 3:41 AM

I would be concerned about the electro-chemical reaction of mounting copper in close proximity to aluminum. The two metals are not compatible and the aluminum will suffer from serious corrosion with just atmospheric moisture acting as the electrolyte between the two metals. The resulting aluminum oxide formed adjacent to the copper is not a good heat conductor and will form an insulating barrier so the performance will quickly degrade to the equivalent of just having the copper pipe.

Register to Reply
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#10
In reply to #7

Re: Trench heating

11/24/2018 10:04 AM

I worked in this field some time ago for about 7 years designing perimeter & trench heating for mainly commercial buildings. The core of both products was aluminium fins on copper pipe, the fins being loosely assembled onto the pipe which was then expanded by ball-sizing to lock the fins in place. I don't recall hearing of any problems due to electrolytic corrosion in that time. Our local hospital has one of the systems I designed in their entrance lobby which is still in use after about 30 years. I guess the risk is there but minimised by the fairly benign environment it operates in.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#11
In reply to #10

Re: Trench heating

11/24/2018 6:53 PM

If after 30 years you can still observe the color of copper rather than the green of verdigris then there is a good chance that the copper had some protective coating sprayed onto it that formed a barrier to prevent the aluminum corroding. Bare copper in contact with aluminum over that period would certainly show signs of corrosion on the aluminum with a puffy white oxide covering the areas in direct contact.

Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#12
In reply to #11

Re: Trench heating

11/25/2018 3:38 AM

Alu fin on copper tube is the normal construction of any outdoor unit of an air conditioner or heat pump. The alu is coated to reduce corrosion, water adhesion and to aid sliding onto the copper tubes.

__________________
Madness is all in the mind
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#14
In reply to #12

Re: Trench heating

11/25/2018 11:51 AM

Similar to my reply to jhhassociates the units I saw being made had no coating unless the raw ali sheet was pre-coated. The fins came off of the press & straight into assembly.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Register to Reply
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#13
In reply to #11

Re: Trench heating

11/25/2018 11:47 AM

Certainly, the units I saw being made in the factory had no coating. The copper pipe was cut, fins punched into shape, then assembled.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: Trench heating

11/24/2018 5:41 AM

If my memory serves correctly, the two will form a battery and drastically increase corrosion. But even copper on its own buried needs a plastic sheath to stop contact with possible moisture!

See here:- https://www.finishing.com/78/97.shtml

Alu on its own MIGHT be OK.....guessing only.

Most people use special flexible plastic hoses as far as I am aware laid under a special concrete (as a name to use!) floor.

Many experience leaks years later, very damaging and expensive leaks, taking months to find and dry out!! BIG PROBLEMS....

It took my daughter and her husband 6 months, with no proper bathroom for all that time! And 2 small children!! Luckily it was mostly summer....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Nov 2018
Posts: 4
#9

Re: Trench heating

11/24/2018 5:58 AM

Yes good point on the Electrolisis, like copper to galvanised steel is a big no no with water, didn’t realise copper and Alu had the same effect. Yes for underfloor heating you run plastic pipes around the floor area on top of insulation buried in a screed. I was thinking trench heating but no longer doing this.

https://www.trenchstyle.co.uk/jaga-canal-compact-36-cm-width.html

good for when building from new to place in front backdoors to eliminate the cold spot, unless triple glazing is used!

Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Emery1990 (3); GM1964 (2); jhhassociates (2); lyn (1); Nigh (4); PWSlack (2); SolarEagle (2)

Previous in Forum: Gear Wear Rig Calculations   Next in Forum: Unstayed Flat Heads

Advertisement