Boiler Feed Water Pump Heating

11/30/2018 7:04 AM

Is this necessary to check the free rotation of a boiler feed water pump after heating for start-up?

__________________
ahb
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Boiler feed water pump heating.

11/30/2018 7:04 AM

It would be wise.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Boiler feed water pump heating.

11/30/2018 8:55 AM

However, if the motor and circuit protection co-ordination is correct, and the pump is siezed, then the arrangement will trip-out on overload.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#3

Re: Boiler Feed Water Pump Heating

11/30/2018 1:12 PM

If it's not rotating you need don't have a boiler feed water pump. You have one of those ubiquitous boat anchors.

__________________
High Tolerance is Beautiful
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Boiler Feed Water Pump Heating

11/30/2018 2:55 PM

It should be checked to make sure it's working....different boilers have different check lists for startup....and different operators sometimes customize the checklist to correspond with current conditions....You should have a startup checklist that is followed and checked off with readings noted for maintenance procedures...This keeps a history of the boilers' operating characteristics for reference....

http://www.ryancompanyinc.com/customer-boiler-startup.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#5

Re: Boiler Feed Water Pump Heating

11/30/2018 4:30 PM

Hopefully, this is a homework/ test question? For you to ask this type of remedial question shows you are not familiar with boilers and should not be working on or around them. There's too much at stake for a simple screw-up that would boil down to a catastrophic explosion.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Boiler Feed Water Pump Heating

11/30/2018 6:43 PM

Is this related to the thread Increasing of Impeler Diameter in any way?

Register to Reply
Commentator

Join Date: Jul 2009
Location: 3325 pakistan
Posts: 56
#7
In reply to #6

Re: Boiler Feed Water Pump Heating

11/30/2018 9:30 PM

No it is related to multi stage centrifugal pump only. Is there a chance of pump seizing or shaft bending or broken if the pump was hard to operate before start up and not checked free rotation before startup.

__________________
ahb
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #7

Re: Boiler Feed Water Pump Heating

11/30/2018 10:04 PM

A pump can seize up at any time, usually from bearing failure...shaft bending usually only occurs in really big pumps from sitting dormant, or when exposed to extreme heat...I don't think I've even seen a pump shaft actually break, or may have and forgot, in any case probably extremely rare...I have seen them form cracks...I've never seen anybody try to hand spin a pump before startup...But you always check them after starting for proper operation....Now this is just my personal experience, your situation may be different, you might have equipment I'm unfamiliar with....I would check with the pump manufacturer for any operational recommendations that might deviate from the norm....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#9

Re: Boiler Feed Water Pump Heating

11/30/2018 10:50 PM

I tend to agree with SolarEagle in reply #8. But, considering the discussion about "Watch Your Units", I wouldn't be surprised to find mis-matched parts within an assembly. Usually the free-rotation of a motor shaft changes slowly over time and gives signs/symptoms before a sudden failure. Even tho you might not have to check it every time, it would be a good idea to check the characteristics when brand new for base-line data, then once-in-a-while thereafter to check for changes/trends to anticipate failure before it actually happens.

__________________
Science is the "cookbook" for making things.
Register to Reply
Associate

Join Date: May 2010
Posts: 26
Good Answers: 1
#10

Re: Boiler Feed Water Pump Heating

12/01/2018 4:12 AM

It is wise to check the free rotation after heating for start-up. If the pump is kept in hot stand by condition, there is a rare possibility of pump jamming. If the pump is in cold stand-by, then you should check the free rotation of pump before start-up. Some manufacturer like KSB not provides worm-up system in there some model of pumps like CHTC 4/12, which we have in our 120 MW units, but we have experienced pump jamming during start-up when the pump kept in stand-by for a long duration.

__________________
Suranjan Chattopadhyay
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11

Re: Boiler Feed Water Pump Heating

12/01/2018 10:05 AM

This statement, "the pump was hard to operate before start up," should have been an indication that something was not right.

It should have been checked immediately.

Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#12

Re: Boiler Feed Water Pump Heating

12/01/2018 10:30 AM

Just by touch you should be able to tell if it's running, If it's the type with a big screw in the middle unscrew it & you can see if it is spinning, If not put a screwdriver in the slot & give it a turn if it starts it should be ok but I would look to put a new pump in as soon as possible,

Bazzer.

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#13

Re: Boiler Feed Water Pump Heating

12/03/2018 7:52 AM

Yes if it has been warmed up from cold. Yes if it has been on hot standby for a lengthy period.

The shafts of multistage boiler feedwater pumps are "slender" and as such have a tendency to sag over time or to go walkabout during heating. Often the the wear rings are made of galling materials, so the slightest rub caused by slight thermal bending can result in catastrophic failure due to galling of wear rings and neck bushes.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#14

Re: Boiler Feed Water Pump Heating

12/04/2018 7:36 AM

Is someone telling you it's NOT necessary, then , Mildred?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#15

Re: Boiler Feed Water Pump Heating

12/04/2018 8:03 AM

U'r not actually telling us what type of system it's on, is it domestic or commercial? totally different types of pumps.

Bazzer

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Commentator

Join Date: Jul 2009
Location: 3325 pakistan
Posts: 56
#16
In reply to #15

Re: Boiler Feed Water Pump Heating

12/04/2018 7:27 PM

Multistage (11)high pressure1600PSIG 200GPM flow.

__________________
ahb
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: Boiler Feed Water Pump Heating

12/07/2018 9:51 AM

Please explain why the pump manufacturer can not, or will not, give appropriate advice either in the user manual that came with it, or over the telephone?

Please explain why the facility would prefer to put its trust in the hands of a bunch of anonymous strangers on the internet, who individually and collectively cannot see anything of the installation, rather than the original equipment manufacturer, who knows it intimately and whose representative may well have been present upon original commissioning?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

arshad bbc (2); Bazzer Englander (2); Crabtree (1); Dennis R. Levesque (1); dj95401 (1); JE in Chicago (1); lyn (2); PWSlack (3); SolarEagle (2); Suranjan Chattopadhyay (1); The Prof (1)