277 volt lighting

10/04/2007 7:34 AM

Can someone tell me how/if you can install a 277 volt lighting fixtures to 480 volt supply.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 277 volt lighting

10/04/2007 7:43 AM

Is there a 'neutral' wire, electrically in the middle of each of the 480V phases?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 17
#2
In reply to #1

Re: 277 volt lighting

10/04/2007 7:58 AM

I don't think so. There are 480V HID fixtures on the circuit now. I wanted to add fuorescent fixtures to the circuit if possible. 277 ballast are more readily availble then 480V.

Thanks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: 277 volt lighting

10/04/2007 8:01 AM

Then the answer is no, they can't, because of the absence of the neutral conductor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Oct 2007
Posts: 17
#4
In reply to #3

Re: 277 volt lighting

10/04/2007 8:08 AM

So if I had a neutral wire, I would use one leg of the 480V and the neutral to get the 277V. Correct?

Thanks for the help

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: 277 volt lighting

10/04/2007 8:17 AM

Correct.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#7
In reply to #4

Re: 277 volt lighting

10/04/2007 8:50 AM

If you need some, I've got some 480V ones in one of my skips in Basildon. Come and get them if you like. £5 each and you take them away? <Splutter>

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#9
In reply to #4

Re: 277 volt lighting

10/04/2007 11:25 PM

If you want to use a wall switch, it has to be a 120 v operated relay for the 277. I'm sure the 480mis controlled by a relay already, but a separate switch would require the relay. The ground bus in your panel should be the neutral, except in the case of an isolation transformer. If ou plan on more than a single light in the circuit, then you shoould have an equal number on each phase, either 2 or 3 phases. They can share a neutral, and 3 phase will only carry harmonics, but they can be more than the neutral load, so don't push the loading.

RichH

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6
In reply to #2

Re: 277 volt lighting

10/04/2007 8:24 AM

277 line to neutral; 480 line to line. Very common. Ask an electrician.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#8
In reply to #6

Re: 277 volt lighting

10/04/2007 12:04 PM

Yes, It's very common! Or you could wire up a few in series! (I think that would work but I have never tried it!)

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#10

Re: 277 volt lighting

10/04/2007 11:36 PM

The 277 voltage would have to come from a three phase transformer that is connected in a 277/480 WYE connection which would give you 277 from the neutral to any of the hot legs. This is to better balance the load on the transformer.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#11

Re: 277 volt lighting

10/04/2007 11:53 PM

It looks like this...

http://www.patchn.com/wye.htm

Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#12

Re: 277 volt lighting

10/05/2007 7:43 AM

provide 480 v/ 277 volt transfomrer of equal VA

nascon

Register to Reply
Active Contributor

Join Date: Jul 2007
Location: Los Angeles
Posts: 23
#13

Re: 277 volt lighting

10/05/2007 9:53 AM

IF you only have one circuit than I don't know of a good way.

If you have a bunch consider this;

I see this in all the data centers - They use a 480 volt 3-phase, 3-wire Primary to 277/480 Volt secondary, 3-phase, 4-wire transformer - you create a neutral. I think the smallest is a 15 kVA. The output feeds your new lighting panel. You would ground the neutral in this panel, or the transformer. This separately derived system with help you avoid building ground fault issues