Anonymous Poster

Running of 3 phase motor by using two phase supply

10/19/2007 10:35 AM

hi

I need such a circuit idea which convert 2 phase supply to 3 phase automatically.

daily i will get a supply of 2 phase for 6 hour in a day from electricity board. and remaining time i will get 3 phase. when 2 phase power is there daily i manually connect a one terminal of capacitor to any one line of supply line and other terminal to 3rd line in of motor. i don't want do this daily. so i need circuit idea which automatically identify that 3phase or 2phase. if 2 phase is present it automatically convert the 2 phase to 3phase and start motor automatically.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - I am a Yankee Doodle Boy. Engineering Fields - Manufacturing Engineering - Old School is the best school. Safety - ESD - Safety Mgr that keeps the peace Hobbies - DIY Welding - My Motto:

Join Date: Jan 2007
Location: Broken Arrow, OK, USA
Posts: 838
Good Answers: 26
#1

Re: Running of 3 phase motor by using two phase supply

10/19/2007 2:22 PM

Not sure where your at that this kind of thing could happen daily.And I have never heard of a device that can do what you are asking.

However you could simple wire a switch inline which would have both wiring configurations going to the motor and simply flip a switch when this occurs.

Since your working with both 3 phase and 2 phase I would suggest using a 3 pole double throw switch and wire one side for the 2 phase configuration and the other for a 3 phase configuration. That is if the ampacity of the both configurations can be handled by the one switch.

Hope this isn't too confusing.

__________________
If necessity is the mother of invention then is laziness the mother of necessity?
Reply
Guru
Hobbies - HAM Radio - New Member Hobbies - Model Rocketry - New Member

Join Date: Jan 2007
Posts: 787
Good Answers: 52
#2
In reply to #1

Re: Running of 3 phase motor by using two phase supply

10/19/2007 2:56 PM

I also have never heard of this, nor a device for it, but Perhaps he can run with your idea of a switch, and instead use a relay that is controlled by the 3rd leg.

Reply
Active Contributor

Join Date: Sep 2007
Location: Troy, NY
Posts: 10
#3

Re: Running of 3 phase motor by using two phase supply

10/19/2007 4:26 PM

Make your own phase converter

rectify the pases coming in

use a 3 phase PWM to recreate the 3 phase

this is how VFD's and normal phase converters work

since its rectified it shouldn't care if 2 or 3 phases are coming in since it is just making DC

Analog Devices makes an Arm7 with a 3phase PWM block built in

you'll have to spec out transistors or FETs to suit your power needs

Reply
3
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4

Re: Running of 3 phase motor by using two phase supply

10/19/2007 4:47 PM

Here's a pretty simple design that should work. It's basically the same design I give my customers to ensure their motors don't get damaged in case they lose an incoming phase. (In their case, if a 27 relay drops out, the motor turns off.)

You didn't say if the same phase always goes out, so I used 2 voltage relays (27-1, 27-2), to cover all 3 phases. I showed the Capacitor Relay powered from phases 1 and 2, but it will need to be powered from whatever source is always on You could also use 3 Capacitor Relays (powered from phases 1-2, 1-3 & 2-3), with all 3 NC contacts paralleled and all 3 NO contacts paralleled. If the same phase always goes out, you only need one 27 relay and one Capacitor Relay.

When all 3 phases are present, both 27 relays are energized, closing their contacts and energizing the Capacitor Relay. The Cap. Relay opens the contact in series with the capacitor, and closes the contact connecting the line directly to the motor.

If any phase is lost, one or both 27 relays deenergize, opening their contacts and deenergizing the Cap. Relay. The Cap. Relay contacts reverse, placing the capacitor in the circuit and disconnecting the line to the motor.

Hope this helps.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply Good Answer (Score 3)
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#5
In reply to #4

Re: Running of 3 phase motor by using two phase supply

10/19/2007 9:30 PM

clear, comprehensive.

Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#10
In reply to #4

Re: Running of 3 phase motor by using two phase supply

10/22/2007 3:13 PM

PLEASE DISREGARD THE DRAWING IN MY PREVIOUS POST, AND REFER TO THE DRAWING BELOW. I was in a hurry Friday and connected the capacitor to the dead phase, which does nothing. The capacitor needs to be connected (via relay contact) from a good phase to the motor's third leg.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#6

Re: Running of 3 phase motor by using two phase supply

10/20/2007 2:19 AM

you need to understand@ the 3 phase Ac power i.e electrically phase displaced by 120 degree.

Your problem is for power cut by grid,at which instant , the grid supply remain between any of two phase., i.e for lighting /fan (Single phase load) supply can be used between phase and neutral during that time .

To use connected load on third phase for lighting / fan (Single phase load) either you can have COS linked with electrical /mechanical interlocked. IN no case the Two phase you referring which means electrically 180 degree phase displaced power can be distribute by grid. And motive power should not used with with 2phase i.e 415 volt two wire, against the original requirement of 3 phase , 3 wire requirement.

nascon

Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Australia - Member - New Member

Join Date: Aug 2007
Location: Childers, Queensland
Posts: 412
Good Answers: 5
#7

Re: Running of 3 phase motor by using two phase supply

10/20/2007 5:25 AM

Hi there.

I'm not an electrican, however, years ago, I had a friend that ran a 3ph mill press from a 1ph supply through an inverter. The inverter was an early model and only produced (so I am told) 2.5 ph. To correct this problem, he had a spare 3ph motor between the inverter and the mill press running on idle (no load) that genereted a true third phase. Perhaps an electrical mind could jump in here and work it out.

__________________
"A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools!" Douglas Adams 1952-2001. E&OE!
Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#8

Re: Running of 3 phase motor by using two phase supply

10/20/2007 6:02 AM

You only have to oversize the motor and it will be able to run on two phases as an Arno-motor.

__________________
Aged man is not old man...
Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#9

Re: Running of 3 phase motor by using two phase supply

10/22/2007 2:37 PM

Not sure of your supply, but a 3 phase service, that loses a phase, does not create a 2 phase service. For the sake of argument, let's say you've got a 3 ph, 480 volt service. If you lose a phase, you have 480 volt, single phase. Any 3 ph motor will run on single phase power, but it will eventually burn up.

Load Controls Incorporated, is a co. that has a unit that monitors horsepower, which will also let you know of a phase loss. This unit has a selectable output (0-1mA, 4-20mA, 0-5 or 0-10 volts), which can be incorporated in the circuit design to activate a switch, changing the power ckt from 3 phase to single phase.

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Running of 3 phase motor by using two phase supply

10/22/2007 9:59 PM

Just for clarification...

Some people have gone off on the tangent of explaining to you that if you lose 1 phase of a 3 phase supply, that is not called "2 phase" because 2 phase is something entirely different and very rare. When you lose 1 phase of a 3 phase supply, the result is called "single phase". Your mis-naming of the issue is a very common semantic mistake, but don't worry about it. While this is technically correct, I think they are missing your point. As I interpret your issue, you have a 3 phase supply and occasionally lose one phase, but you want to keep your motor running nonetheless.

The capacitor method described above will work, but there is a concern. The LOAD on the motor must be reduced by the square root of 3 (reduced to 58% of normal) in order for this to work without causing the motor to lose torque, drop into higher slip and overheat. If your motor is already considerably oversized, this will work fine. If not, it may not work at all unless you can shed load.

A better alternative, if this is a pervasive problem, is to use a VFD for the motor all of the time, even if you never change the speed. A VFD changes the incoming line power to DC, then re-creates an AC pseudo-sine wave for the motor. In the conversion process (going from AC to DC), it can do that with 3 phases or 1 phase, as long as the components are sized properly. If the motor is equal to or less than 2.2kW @ 240V, most VFDs can do this without de-rating. If it is larger, you must double the size of the VFD for the motor so that the VFD can adequately handle the extra current and extra ripple on the rectifier side when it has to draw all of the incoming power (1.732 times normal) through only 2 of the phases instead of all 3. So by using a properly sized VFD as the motor controller, your motor would never know that a phase on the input side had been lost, it would continue on running seemlessly.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#12
In reply to #11

Re: Running of 3 phase motor by using two phase supply

11/05/2007 3:23 PM

What a great answer,cut through all the cr*p and mumbo jumbo,and the third phase at about 160 deg or worse or with pilot motor brigade. No contactor,nasty big capacitor,phase failure detection etc etc. VFD/inverter ia always the best solution to single to 3 phase conversion.Even covered the down rating when operating on two phase.Just one little caveat,some drives will drop out when detecting phase loss,just check that the drive doesnt or the programming can be set to ignore,or use single phase drive only for less than about 3kw.By the way in UK we refer to the loss of a phase to a motor as 'single phasing',youve got me wondering why when it should be 'two phasing'.

Reply Off Topic (Score 5)
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#13

Re: Running of 3 phase motor by using two phase supply

11/05/2007 4:31 PM

The use of a VFD is truly an option, if money is no object.

As far as a tangent goes, I believe someone needs a Websters. It's called single phasing because the energy is generated thru 1 winding.

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Reply
Reply to Forum Thread 13 comments