Split Phase Challenge

10/21/2007 12:19 AM

Lets assume that I have an electrical emergency and there is a washing machine that works on 220v single phase that I would like to power up using 120v single phase.

Now how could I do this with just one hot and one nuetral ?

That is using only basic components and no fancy gadgets.

__________________
When it comes to engineering, what we call ourselves is not supposed to matter. The only thing that matters is the knowledge we attain and the respect we give each other.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#1

Re: Split Phase Challenge

10/21/2007 4:09 AM

I don't think you can do it at all. You'd have to produce more voltage out of thin air. This doesn't seem to be a phasing question. Where does the phasing come into it?

If you were going the other way, say using the washing machine outlet to power the lower voltage outlet, you could just take half of it off by using either [e.g. the red or black] power side of the 220 together with its neutral and you'd have a functioning 110 supply with the benefit of a high amp cutout (breaker/fuse) for heavier use on the low voltage outlet (eg air conditioner, several microwaves, etc). Be sure the wiring you use to take off the 110 is rated for the higher amperage so it doesn't overheat and cause a fire when the initial drag that might be placed on it turns out to be a high one. This procedure is not recommended for tiny consumers because it will admit surges to the machinery on the low voltage outlet.

Your questions actually worry me about what you seem to be trying to do without the benefit of the knowledge or experience necessary to be doing them. Isn't there SOMEbody you can ask to do it for you while you watch and learn?

Mark

Register to Reply
Associate

Join Date: Dec 2005
Posts: 27
#2

Re: Split Phase Challenge

10/21/2007 6:05 AM

Ok I guess I made the statement a bit difficult.

How can I create the two L1 and L2 lines to power a 2 phase motor ( i.e. 220v ) from one phase ?

Any ideas ?

__________________
When it comes to engineering, what we call ourselves is not supposed to matter. The only thing that matters is the knowledge we attain and the respect we give each other.
Register to Reply
Anonymous Poster
#4
In reply to #2

Re: Split Phase Challenge

10/21/2007 11:55 PM

Voltage and phase have nothing to do with each other. The simplest solution is to buy a washing machine that will work on your currently available electric service. If you are interested in learning, and have access to a good public library, check out Electricity 1-7 by Harry Mileaf. Although it was first published in 1966, it is among the very best introductory texts for people who know nothing about electricity, and could save you time, trouble, expense, frustration, and might even save your life.

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#6
In reply to #2

Re: Split Phase Challenge

10/22/2007 2:56 AM

Watdefak asked: How can I create the two L1 and L2 lines to power a 2 phase motor ( i.e. 220v ) from one phase ?

Original question stated a washing machine that works on 220v single phase that would be powered up using 120v single phase.

Now which is it?? one phase or two? L1 and L2 refer to a 220V system as used in N. America. But its not two phase.

__________________
Elnav
Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#16
In reply to #6

Re: Split Phase Challenge

10/29/2007 3:28 AM

IT ISN'T??

I believe that in house wiring, we have red and black hot wires which are 180 degrees out of phase with each other. To run 110 v. appliances, we can use either red or black wires to neutral. To run 220v, we run from red to black, and the neutral is not used.

I learned (on CR4) several months ago that in Canada, kitchen duplex outlets are run with red to one outlet (lets say top) and black to the other (bottom) outlet. At the breaker box, the two breakers (for each side) are ganged together so that if one breaker goes, the other one goes too.

This allows a person to rig a cord with two 110v. plugs to run 220v equipment (typically imported). One each to top and bottom of the outlet.

Register to Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#3

Re: Split Phase Challenge

10/21/2007 3:52 PM

Use a step up transformer. Attach the 110V single phase to the primary, use the secondary side (with center tap as neutral) at 220v to power the machine.

Take care in calculating your wattage/current requirements. Whatever the amp load is on the seconday side, the primary side will be doubled.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#5

Re: Split Phase Challenge

10/22/2007 2:49 AM

Use a step up transformer. 120V in 220V out. Just make sure the KVA rating of the tranformer is sufficient for the load.

From your questions now and elsewhere it sounds as if you are trying to cobble together an off grid or grid backup electrical system. The scary part is you really need a lot more back ground knowledge to acomplish building such a system, than your questions suggest you have at present.

__________________
Elnav
Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#7

Re: Split Phase Challenge

10/22/2007 8:04 AM

Run a leg through a big enough capacitor bank?

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#8

Re: Split Phase Challenge

10/22/2007 9:15 AM

transformer

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru

Join Date: Aug 2007
Posts: 548
#9

Re: Split Phase Challenge

10/22/2007 4:05 PM

Step up transformer is the answer , you didn`t mention line frequency , is it 50Hz/60Hz , washing machine consume approx 800w of power , be very perticular about power rating of your gadget

Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#10

Re: Split Phase Challenge

10/22/2007 6:38 PM

Watdef** asked ' How can i create the two L1 & L2 lines to power 2phase motor (i.e 220v) from one phase?' Please analyz da question i.e 2 lines(phases L1 & L2) from a single phase line.Think about the phase displacement.

__________________
poy
Register to Reply
Associate

Join Date: Dec 2005
Posts: 27
#11

Re: Split Phase Challenge

10/22/2007 9:07 PM

A capacitor bank ..... That is simple.

the capacitors will cause the voltage to lag the source voltage. But would this somehow "create" another phase ?

__________________
When it comes to engineering, what we call ourselves is not supposed to matter. The only thing that matters is the knowledge we attain and the respect we give each other.
Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#12
In reply to #11

Re: Split Phase Challenge

10/22/2007 9:39 PM

I think by a 1/4 phase, so maybe 180v. Enough for an emergency.

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13

Re: Split Phase Challenge

10/22/2007 10:35 PM

LOL, so much misinformation...

You have SINGLE PHASE in both cases, never "2 phase", which is an entirely different beast and very very rare. Please don't call it that, there are semantics police in this forum who will hijack this thread for days trying to deal with that issue without answering your question. Move on...

Capacitors will NOT work. Holy smokes, what a concept! Where is the power to charge the capacitors going to come from??? Answer, the same 120V grounded neutral 1 phase source you already have! All it will do is discharge to the grounded side of the 120V supply. Sheesh people....

As others have said, just hook up a 2:1 transformer to your 120V circuit that transforms the 120V to 240V and you are done. The center tap for a new neutral may be an issue as mentioned above, because some of your appliance controls may be 120V anyway and now you would need to re-create that grounded neutral reference point. But just look at your existing appliance plug. If they did not have a neutral connection now, then you don't need one. In other words, if what you have now is a plug with 3 blades (L1, L2 and G), then you do NOT have or need a center tap for a neutral connection; your appliance isn't using it now. If you have a 4 prong plug then you do have a neutral and you will need one again when you use your 120V supply.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#14
In reply to #13

Re: Split Phase Challenge

10/27/2007 1:24 AM

Ok. So waddya think, guys...? You jump the voltage up to 220 via a transformer. Will the washing machine work?

Mark

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#15
In reply to #14

Re: Split Phase Challenge

10/27/2007 3:26 AM

Of course it will. I'm doing exactly that right now with some 220V equipment we built for European use. I purchased a small 2:1 ratio transformer to give me the required 240v from a 120V line. Many travellers to/from Asia also get voltage transformers to convert the local voltage to suit their equipment. It works as long as frequency is not an issue.

In the original question the issue seems to be voltage only and the local grid is stil supplying the same frequency at 120V.

__________________
Elnav
Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#17
In reply to #14

Re: Split Phase Challenge

10/29/2007 3:48 AM

Me too...

A transformer is the safest way to go. Although, run a "ground" around the transformer so the user doesn't get electrocuted.

Bill

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#18
In reply to #17

Re: Split Phase Challenge

10/29/2007 7:27 AM

You don't have a risk of electrocution when on the secondary of the transformer. This is why most hotels and motels had those special isolated " razor only" outlets next to the sink. The transformer provides the necessary isolation.

__________________
Elnav
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (1); elnav (4); JRaef (1); Kilowatt0 (1); MarkTheHandyman (2); NoSciFi (2); olivinak (1); Sciesis2 (2); vikas (1); watdefak (2)

Previous in Forum: Paralleling Generators   Next in Forum: Auto Tapping Transformer

Advertisement