After charging 33kv/11kv transformer vcb not withstandind.

10/25/2007 12:31 AM

We are using 33kv/11kv transformer for distribution of power supply to various contractors,also we are having 11kv/440volt 3 phase distribution transformers.one day before ,there is lightening and rain due to that our main transformer is not withstands.we checked megger values on secondary side it shows 80Mohm at this time all rain condition.

If anyone can tell me systematic procedure for finding fault in breaker as well as transformer?

our power factor is also not in controll.It is upto 0.66 lagging how we can improve it?

with regards

C.B.Deshmukh

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#1

Re: After charging 33kv/11kv transformer vcb not withstandind.

10/25/2007 3:00 AM

Your power factor to be .9+ and with this improvement vcb will hold.

(sorry i'm not a Electrical guy, this I discussed with my Manager Power)

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: After charging 33kv/11kv transformer vcb not withstandind.

10/25/2007 3:29 AM

<our power factor is also not in controll.It is upto 0.66 lagging how we can improve it?>

Add capacitance at the user end of the cable.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#3

Re: After charging 33kv/11kv transformer vcb not withstandind.

10/25/2007 3:39 AM

80Mohm apply on secondary side winding or to ground resistance?

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: After charging 33kv/11kv transformer vcb not withstandind.

10/25/2007 10:35 PM

To improve ur pf is not a problem .Use and automatic pf correction using capacitors.As regds breaker not holding there could be many causes. Is it the breaker odes not hold after switching on 33kv transformer after a lightening strike?

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Anonymous Poster
#5

Re: After charging 33kv/11kv transformer vcb not withstandind.

10/26/2007 3:00 AM

You can also improve your power factor by replacing some of your induction motors with synchronous motors.

Is this breaker on the 440V side? 11KV? 33KV? This may not be a ground fault; it may be a phase-to-phase fault. I would take the affected transformer completely out of service and check everything. You could have a cracked insulator, punctured insulation somewhere inside the transformer, a fault in the wiring between the transformer and the breaker, etc. Check everything, and keep the results of all your tests in a notebook.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6

Re: After charging 33kv/11kv transformer vcb not withstandind.

10/28/2007 1:02 AM

The details given by you are not sufficient to trouble shoot.

1) Is it running Plant or new one.

2) Which vcb trips on 33 kV side or 11 KV side.

3) What protections are provided in each of the breakers?

4) When the breaker trips, is it instantaneous or after some time lag.

5) Is there any indication in the protective device about the fault?

I can study your electrical system and suggest suitable measures for improving trouble free operation, provided you send the details if you are interested.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Reply to Forum Thread 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cnpower (1); ducon (1); nesubra (1); PWSlack (1); ramvinod (1)

Previous in Forum: Voltage in a DC generator   Next in Forum: DC or AC High Voltage Control

Advertisement