Anonymous Poster

4 core cable

12/23/2007 11:37 AM

hello

i would like the specefication of the cable .for generator 640 kw.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: 4 core cable

12/23/2007 12:45 PM

What is the operating voltage ?

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2

Re: 4 core cable

12/23/2007 9:15 PM

Standard answer is 42!

Unless you provide some real basic information, no one will be able to help you!!

Is this a control cable, a HLI (High Level Interface) cabel or output cables for the Generator???

The answers to any or the three (3) options will vary by orders of magnitude.

No knowing where you are asking from also makes it difficult to answer your question as every country, state and local supplier will have different requirements.

For a Generator of this size in Australia, you would run a separate single core cable for each phase, neutral and earth for example, not a single four core.

Details Please????

Sapper.

__________________
It's all about the Boom! - MythBusters
Reply
Anonymous Poster
#7
In reply to #2

Re: 4 core cable

12/25/2007 8:40 AM

dear sir:

The cable that i need is output power cable(single or 4 core).the dectance between the generator and DB : 15m

rating voltage : 400 Vac

Reply
Associate

Join Date: Dec 2007
Posts: 27
#3

Re: 4 core cable

12/24/2007 12:16 AM

sir you have to explain that which cable you want to use copper or alluminium both standard is different please explain. thanks

Reply
Member

Join Date: Aug 2005
Posts: 8
#4

Re: 4 core cable

12/24/2007 2:47 AM

I think you requires the cables of rated LT voltage, you need to calculate the full load current rating and select the cable size accordingly. it is advisable and economical to select aluminium cable for higher current rating. while selecting cable size, consider the points like short circuit current, ambient temperature, temp. rise, cable route, etc. for proper de-rating of the cable. you may find more information in the technical catalogues of cable manufacturers and the local standards.

__________________
Friends are the angels, who lift us to our feet when our wings have trouble remembering how to fly.
Reply
Anonymous Poster
#8
In reply to #4

Re: 4 core cable

04/11/2008 2:29 PM

Hello

I have answered your Post/comments,

Generally best to use the Cable Maker of your particular cable, but try:

http://relemaccables.com/

If you are still needing help, reply with

Kind Regards....

Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#5

Re: 4 core cable

12/24/2007 12:28 PM

Assuming these:

  • India
  • 415/240 V 50Hz ,cosΦ=0.8
  • Standby Generator
  • Power Output Cable hung out in the open sun~45°C max.
  • 3 1/2 separate Cores PVC - unarmored

Then 3 cores -- each 630mm2 Aluminium

The half size core--300mm2 Aluminium

MM

Reply
Associate
Jordan - Member - New Member

Join Date: Aug 2007
Location: Saudi Arabia
Posts: 25
#6

Re: 4 core cable

12/25/2007 5:17 AM

dear GUEST , I will try to help you but as they mentioned above that according to lack of data submitted by you , nobody can help , so my answer will depend on the following :I considered that :

1.voltage : 3 phase 220V

2.distance from generator to switch gear or main DB : around 20 mtrs

3. maximum load is the generator ratings which you mentioned

4. temperature around 30 C degrees

the total current @ 220 v and power factor 0.8 is : 2100 A

It's preffered to use single core cables not multi-core ones , so you can use 3*630mm2 single core cable (3 per phase ) ( each 630mm2 cable cand carry around 800 A , so when you use three cables you will be at the safe side ).

don't forget my friend that we are talking in general , there are many variables should be taken into consideration if you need a precise figures.

Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#9
In reply to #6

Re: 4 core cable

02/04/2011 6:59 AM

You meant to write 3X1CX630 mm^2 XLPE/SWA/.... for phase and another 1CX300 mm^2...for grounding (?). The three phase voltage he has mentioned above is 400V?

__________________
--
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#10
In reply to #9

Re: 4 core cable

02/17/2011 5:43 AM

I apologize for not pointing out earlier that you might need us to do all calculations for you and post it here (cut and paste).

By taking 640 KW or 800 KVA (when, PF = 0.8) and using the three-phase formula;

I = (KW X 1000)/(1.73 X V X PF) = (640 X1000)/(1.73 X 400 X 0.8) = 1124 A

Breaker size (adding some % age) = 1200 A

At 1200 A @ you would need : 7 X 1C X 630 mm^2 XLPE/SWA/PVC/CU

+ 1C X 300 mm^2 PVC/CU/ECC

OR

3X 4C X 300 mm^2 XLPE/SWA/PVC/CU

+ 3 X 1C X 150 mm^2 PVC/CU/ECC (grounding)

__________________
--
Reply
Reply to Forum Thread 10 comments
Copy to Clipboard

Users who posted comments:

abasins (2); Anonymous Poster (2); joginder pal singh (1); MUKULMAHANT (1); os708090 (1); ramvinod (1); Sapper (1); Sonu (1)

Previous in Forum: Losses of capacitive power factor   Next in Forum: AC DRIVE
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement