strainer

01/13/2008 1:54 AM

Dear All,

can we install y-type strainer in vertical pipe?if not then what will be affect on fluid filtraton.

regards,

malik

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#1

Re: strainer

01/13/2008 2:36 PM

Yes it dose'nt matter vertical or horizontal.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: strainer

01/14/2008 4:56 AM

One of the things to consider is what happens when there is no flow. Does the strained debris fall back down the pipe and mangle the components in a pump the next time it is started, for example?

Just because something could be done doesn't mean that it should be done......

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Spain - Member - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Oct 2007
Location: Madrid, Spain
Posts: 716
Good Answers: 25
#3

Re: strainer

01/14/2008 5:04 AM

I agree with Ducon.

Anyway I think our guest has the minimum amount of common sense to install the Y type strainer in the correct position. Even in horizontal piping you can install it with the non-alineated leg in the upper side!!!!

Ancient romans said "numerus stultorum infinitus est" and transfinite numbers theory wasn't developped by Kantor at that time.

__________________
It's stupid to discuss about AI: We´ve reached by the "B" way. We' ve producing men as clever as machines.
Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#5
In reply to #3

Re: strainer

01/15/2008 1:25 AM

"Even in horizontal piping you can install it with the non-alienated leg in the upper side!!!!"

I agree yours that Y-strainer can be installed in a vertical or horizontal position, but at horizontal position the non-alienated leg can not be oriented in the upper side, it must be at lower side.

__________________
It is better to be defeated on principles, than to win on lies!
Reply
Guru
Spain - Member - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Oct 2007
Location: Madrid, Spain
Posts: 716
Good Answers: 25
#7
In reply to #5

Re: strainer

01/15/2008 2:03 AM

Because of that I used the word "can" and not "must". Obviously, you "can" but you must not. And for the same reason I give some credit to the intelligence of our guest. I'm tired of seeing how some CR4 people treat guests as if they were stupid.

__________________
It's stupid to discuss about AI: We´ve reached by the "B" way. We' ve producing men as clever as machines.
Reply
Anonymous Poster
#4

Re: strainer

01/14/2008 1:47 PM

Sometimes you can use Tee-type strainer in a vertical line.

Tee>>>wn-flange with blindflange. V-shaped strainer.

Regards Freddy

Reply Off Topic (Score 5)
Anonymous Poster
#6

Re: strainer

01/15/2008 1:41 AM

Thank u very much every body for your positive response.

Reply
Anonymous Poster
#8

Re: strainer

01/29/2008 4:38 AM

i give a thought about the position, i think the position is depends to the flow, if the flow is going down, it is applicable. but if a vertical pipe line with upward flow, then the y strainer is not suitable there.is it right?