Ammeter Used for Measuring One-Phase Current

02/26/2008 6:50 AM

While measuring current in one phase for small 3 phase motors (say 0.37kw) the ammeter is connected in yellow phase. I got an answer, I wish to get the understanding of my friends. Sparkstation, JReaf, Del and anyone can forward their view.

Thanks

__________________
BNDas
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#1

Re: Ammeter Used for Measuring One-Phase Current

02/26/2008 2:28 PM

So what was your question?

__________________
paulusgnome
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: Ammeter Used for Measuring One-Phase Current

02/26/2008 9:41 PM

Can you elaborate. You have made a statement.What do you expect ?

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: Ammeter Used for Measuring One-Phase Current

02/26/2008 10:54 PM

Why yellow phase is selected not Red or Blue?

__________________
BNDas
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#4
In reply to #3

Re: Ammeter Used for Measuring One-Phase Current

02/26/2008 11:36 PM

The 3 phases should be nearly the same.

if you have any significent difference, there is probably a bad winding.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#5
In reply to #4

Re: Ammeter Used for Measuring One-Phase Current

02/26/2008 11:52 PM

No, there is significance for using yellow phase.Will wait for some more view.

__________________
BNDas
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 4:16 AM

Traditionally, extensions to a distribution board where three phases come in and single phases go out usually place a greater load upon the red phase, as the electrician making the connections will habitually start in the top-left and end at the bottom-right. It just so happens that most UK distribution boards have been arranged with the red phase at the top, the yellow in the middle and the blue at the bottom. So the red phase traditionally carries more current and therefore will be at a slightly lower voltage than the yellow or blue. Would this have any bearing upon the matter, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 1:19 AM

The significance must mean something in your locality. It means nothing here, in fact "yellow phase" means nothing here in the US. I can think of no specific engineering reason to put a 1 phase CT on any particular phase of a 3 phase motor circuit. In any case it gives you a nearly useless representation of what is happening in the motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#7
In reply to #6

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 1:34 AM

JRaef,

Thank you for your view. But in many countries in Asia and Gulf, for 3 ph FHP motor one ammeter used in series of contactor to measure current and thus save cost of 3CTs & A/S or 3 ammeter. The reason is the yellow phase is gets affected if there is disturbance in other two phase. Say yellow phase is the winded in central core of upstream transformer. Remember magnetic balance test etc. This can be better explained by manufacturer.

__________________
BNDas
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#9
In reply to #7

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 5:31 AM

I am of the opinion is yellow phase gets affected if there is disturbance in other two phase. The yellow phase also the central winding of upstream trafo core.once there is some problem in red or blue, it will surely affect the flux density in central limb even if its small, than other limb. We can think more over it and if possible adopt mathemetical justification.

__________________
BNDas
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #9

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 6:25 AM

There is a "disturbance" with another phase any time a phase has a problem. Often the other phase(s), when a single phase is lost show a current somewhat similar to starting current, which can happily cause HRC fuses to blow and stop any further damage for example......

But picking out a particular (yellow) phase as being the "one to monitor" shows little understanding of the way 3 phase systems really work.The colors are usually arbitrary anyway, though not always.....

To really check things out in a correct and fundamental manner, all three phases need to be monitored at the same time.....nothing more, nothing less......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#11
In reply to #10

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 6:38 AM

We know how 3 phase system works. There are protections, monitoring devices etc. But, for an operator for a quick observation the ammeter will be useful. The yellow phase is a better choice than arbitrarily selecting red or blue.

Well tell me what's the norml choice of control voltage for MCC 240V AC or 110V Ac and which will be a better choice?

__________________
BNDas
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #11

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 7:46 AM

Why is yellow better?

Are you color prejudiced?

There is simply no reason that any phase is "better" than any other, unless you just believe in luck of course!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#13
In reply to #11

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 2:27 PM

It may be convention. Why is the phase color yellow? It could be something as simple as that is the phase that is always used for this particular purpose.

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#14
In reply to #13

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 2:52 PM

Here we use

Brown

Orange

Yellow

in panels

drop cords are generally

Black

White

Red

Green=ground

The white is hot & can be confusing, having 277v on the neutral is not a good thing.

If there is a difference between the 3 phases (current reading] there is a problem. There is no master winding on a 3 phase motor.

Certain industries, localites or regulatory bodies may have a convention they would require, but operationally there is no difference on a 480 3 phase set up.

There are some older 240volt 3 phase where there is a "stinger" Leg with a higher voltage, I can't quite remember the details? 205 to ground, 120 on the other 2?

So I guess I should ask, what is the voltage measurement between the phases & also the measurements to ground, neutral?

Register to Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#15
In reply to #14

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 3:25 PM

I was trying to illustrate convention, though very poorly. Yes, he uses yellow for his current monitoring, but it may be because everyone there does and not for a specific engineering purpose.

By the way, I assume you were speaking of the white conductor in a cord assembly or romex as possibly being used as a hot?

Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #15

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 3:30 PM

Anyone who believes as he seems to, that a particular phase is "different" or "better" does not understand electricity at all......

But you and the other posters seem to understand that better than he does.....thank God!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#18
In reply to #16

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 11:37 PM

That's already justified with reasoning. Well, let me give you another example, if you do magnetic balance test of transformer putting a low voltage on say, R phase, you will see little less voltage in yellow ph and much less on blue. Just think over how it will affect in case of disturbance.

I requested a suggestion with reasoning on selection of 240vAC or 110V AC for control voltage in MCC. I got some reasoning if you have, can please forward.

Thank you for communication.

Regards

__________________
BNDas
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#23
In reply to #18

Re: Ammeter Used for Measuring One-Phase Current

02/28/2008 1:31 PM

Depends on the situation.

In the US small power tools & computers run on 110vac, so that is the natural chioce.

If 240 is the norm, that would be the best choice.

Boilers & HVAC many times use 24vac, which is a good choice for safety reasons.

Having all equipment use the same control voltage, helps keep the inventory of spares low & reduces the confusion in regards to troubleshooting to a minimum.

The other question is for control signals is source or sink for switches & proximity devices. Again consistency helps keep inventory & confusion to a minimum.

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#17
In reply to #15

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 3:33 PM

Yup, cords exactly

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#19
In reply to #14

Re: Ammeter Used for Measuring One-Phase Current

02/27/2008 11:54 PM

· NEC National Electrical Code

· UL 508A Standard for safety for Industrial Control Panels

gives color coding of cables. Pleaserefer.

__________________
BNDas
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#22
In reply to #19

Re: Ammeter Used for Measuring One-Phase Current

02/28/2008 1:04 PM

I was refering to what you actually find in common use.

I've seen plenty of panels where all the power is black & all the controls red.

If you're lucky there may be numbers.

Register to Reply
Anonymous Poster
#20

Re: Ammeter Used for Measuring One-Phase Current

02/28/2008 12:36 AM

For your query the current in one phase can be measured using the clamp on meter. In the panel there will be current terminal for each pahse from the CT secondary. Let usconsider a case of 2000/1 A CT. The secondary current in one phase will be measured with the neutral being connected to the earth terminal.

This can be seen in the practical application in which we canmeasure the single phase current in the Control & Realy anel orthe CT Junction Box itself or in the Marshalling Kiosk provided in the outdoor yard.

Regards,

N.Suresh

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#21
In reply to #20

Re: Ammeter Used for Measuring One-Phase Current

02/28/2008 12:45 AM

I wrote for fhp motors only. Any way, we had good discussion on this topic. thanks to everyone who shared their view and knowledge.

Regards,

__________________
BNDas
Register to Reply
Register to Reply 23 comments
Copy to Clipboard

Users who posted comments:

Andy Germany (3); Anonymous Poster (1); biswanath.das (8); Garthh (5); JRaef (1); Lendog (2); Paulusgnome (1); PWSlack (1); ramvinod (1)