Pumps Getting Too Hot

04/15/2008 7:58 AM

good day all,

i m using a pump here that is have a problem in working hot, i mean i used only for water pumping ( as a booster point to my water line)

but the motor' surface is getting hot also it suppose to runs 15 amp but i found it to be 19 amp

wonder if any body know what could be the reason?

or if there is any idea ..how to solve this problem?

thank you

__________________
An Engineer Creats the World that which never was. Theodore Van Karme
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: pumps

04/15/2008 8:07 AM

<....what could be the reason....>

Here are some:

  • Too much flow?
  • Not enough flow?
  • 3-phase pump is connected and running backwards?
  • Unwanted materials in impeller volute - plastic bag? Dead bird?
  • Gland or seal too tight?
  • Alignment not correct?
  • Wrong supply voltage or frequency?

<....how to solve this problem....>

  • Change the flow.
  • Change the direction of rotation.
  • Clear the impeller volute.
  • Service the gland/seal.
  • Correct the alignment.
  • Correct the voltage and frequency of supply.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Dec 2007
Location: Franklin, NC
Posts: 111
Good Answers: 5
#2

Re: Pumps Getting Too Hot

04/15/2008 7:52 PM

If the pump uses packing there should be a small leakage. People often tighten the gland too much because they don't realize this.

__________________
Peace be upon you.
Register to Reply
Power-User

Join Date: Mar 2007
Location: South East of Las Vegas just far enough to see the lights but far enough to not hear the coins falling
Posts: 282
Good Answers: 8
#3

Re: Pumps Getting Too Hot

04/15/2008 11:13 PM

From the field: put your amp probe one of the pump leads, start the pump, make sure rotation is correct and start closing the discharge valve slowly. As you close the valve you may find that the pump was trying to pump to much water causing to run off the end of it's pump curve. Position the valve in the sweet spot for amps...the lowest amp draw that you can get. Let us know what you find. I am certain if this does not help you following PWSLACK'S check list will solve it.

Mike

__________________
Rule number one; Never ask a question unless you are prepared for an answer that you may not like.
Register to Reply Score 1 for Good Answer
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#6
In reply to #3

Re: Pumps Getting Too Hot

04/16/2008 8:34 AM

Agree. Your pump and motor are probably not matched.

I'm not a pump guy but I've seen this happen one time too many. Someone decides to increase the pump capacity but forgets to change the motor size.

Your pump wants to push more water and demanding more power from the motor. Motor draws more current and eventually either trips or burns out.

miketheboilerguy's suggestion will work. By throttling the outlet valve, you effectively lower the pump's capacity resulting in less power requirement. Of course, it results in less flow. I'd prefer to have the motor changed to match the pump.

I'm not discounting PWSlack's suggestions, however, as they could also be probable.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Anonymous Poster
#7
In reply to #3

Re: Pumps Getting Too Hot

04/16/2008 9:10 AM

thank you all for your advice it is all wealth,

put i have to tell that the pump doesn't show any signs of cavities, or vibrations

which to me means good alignment, seal,and even nice coupling

is that means may i have an electric problem only?

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Mechanical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: May 2007
Location: Parallel 45
Posts: 226
Good Answers: 21
#4

Re: Pumps Getting Too Hot

04/16/2008 1:23 AM

One more action added to all suggested checks:

- uncouple the motor and ckeck the amp. If motor operating uncoupled has no any truble should have about 30% amp from nominal value.

Hope this help

__________________
Look over to the next challenge
Register to Reply
Anonymous Poster
#5

Re: Pumps Getting Too Hot

04/16/2008 2:07 AM

hello i am khaled

pump getting hot

you can try to test the chek valve

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: May 2007
Posts: 22
Good Answers: 2
#8

Re: Pumps Getting Too Hot

04/16/2008 9:53 AM

If there is no additional load being applied to the motor then its likely that your motor windings are going bad. The wire used in the windings are coated with a thin layer of insulation and when it begins to break down it allows some current to flow to ground.

At this point it is not a complete short to ground since the motor still runs. It would be a high resistance short to ground.

This condition is easily checked with a megohm meter, but it cannot be checked with a regular ohmmeter. The megohm meter puts a high DC voltage across the winding when measuring the resistance.

Register to Reply
Anonymous Poster
#9

Re: Pumps Getting Too Hot

04/16/2008 1:58 PM

another check you could do

1-Check for adequate ventilation. Be sure motor vent holes (or fan blades) are free of obstructions.
2- Use a shorter or heavier gauge extension cord.

Register to Reply
Associate

Join Date: Mar 2008
Posts: 25
#10

Re: Pumps Getting Too Hot

04/22/2008 7:29 AM

thank you all for your help,

i found the problem,

the motor was miswires, and when we rewire it correctly,

it works fine and we never have such problem again

thank you all

__________________
An Engineer Creats the World that which never was. Theodore Van Karme
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#11
In reply to #10

Re: Pumps Getting Too Hot

04/22/2008 8:01 AM

Well, billybolbol, I'm glad you've found the cause of your pump motor problem.

Note, however, that nobody mentioned it as a possibility. I guess it's because it's not easy to miswire a motor. I hope your motor technician or electrician has learned his lesson.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Associate

Join Date: Mar 2008
Posts: 25
#12
In reply to #11

Re: Pumps Getting Too Hot

04/22/2008 8:15 AM

he is very experienced person a lot of knowledge,

but hey...every body makes mistakes

thank you again

__________________
An Engineer Creats the World that which never was. Theodore Van Karme
Register to Reply
Power-User

Join Date: Mar 2007
Location: South East of Las Vegas just far enough to see the lights but far enough to not hear the coins falling
Posts: 282
Good Answers: 8
#13
In reply to #11

Re: Pumps Getting Too Hot

04/22/2008 1:28 PM

From the field: If one of my Tech's had wired the motor and it burnt up my company would have been responsible for it's replacement. The installer may have talent but he has zero follow-up. An amp draw check after would have caught the problem. You are very lucky the motor did not burn up.

Its a good thing this was not a 200hp critical application.

__________________
Rule number one; Never ask a question unless you are prepared for an answer that you may not like.
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); billybolbol (2); mfiedler56 (1); miketheboilerguy (2); PWSlack (1); Skelley (1); user-deleted-1104 (1); Vulcan (2)

Previous in Forum: LPG System Calculation   Next in Forum: water jet tools with the capacity for 1meter+ deep stone cutting

Advertisement