DC amp. sensor - digital 24VDC output.

04/20/2008 6:07 AM

I am making some kind of an alarm system and I need something that can give 24vDC output (that will be used as an input to PLC) when a 24VDC bulb fails(15-50w). So basically I need a "DC current sensor-unit" that will give 24VDC output when a DC amperage goes to nearly 0Amp in a DC circuit. I will need many units so the price is also an issue. Do you have any suggestions?

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Pathfinder Tags: DC current sensor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Member

Join Date: Apr 2008
Posts: 8
#1

Re: DC amp. sensor - digital 24VDC output.

04/20/2008 6:57 AM

Mr. Jankly,

You can put a shunt resister in series to the load. It will offer a millivoltage drop, whenever current flow through it. If the bulb or any load gets open circuited, there will be no flow of current and thus no voltage drop across the shunt.

So the millivolt can be fed to a differential op-amp (may be LM-741) and connect one relay to the output of the opamp to operate alarm circuit.

Register to Reply
Associate

Join Date: Apr 2008
Location: 66°N (almost)
Posts: 46
Good Answers: 1
#5
In reply to #1

Re: DC amp. sensor - digital 24VDC output.

04/20/2008 8:04 PM

Thank you for your comment. A shunt, op-amp and 12V relay, I believe it will work. I have not heard about this op-amp before, seem to be a nice thing. But as I have to monitor many circuits - I was hoping to find a cheaper system, I have to sell this system approximately 100-200 pieces./year for a comparable price and make a profit out of it. A shunt for every single bulb is a bit to expensive. I was thinking if there is somewhere some kind of an amp-sensor a clamp or a ring that will sense if there is any DC current running in the circuit at all. I don´t need analog monitoring, only something to tell the PLC with a +24VDC input if there is any DC current running or not - "No current=bulb fail".

As I mentioned before the price is an issue in this case, I am competing with another company with a solution for this problem.

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#2

Re: DC amp. sensor - digital 24VDC output.

04/20/2008 7:52 AM

Put a 24 volt bulb across the fuse and mount it on the front panel with a legend saying 'fuse blown' or something...

Works pretty well and is cheap!

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Associate

Join Date: Apr 2008
Location: 66°N (almost)
Posts: 46
Good Answers: 1
#3
In reply to #2

Re: DC amp. sensor - digital 24VDC output.

04/20/2008 9:11 AM

This is not about blown fuse, that is no problem, what I need to monitor is the bulb-failure, or any other load-failure i.e. open circuit.

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#4
In reply to #3

Re: DC amp. sensor - digital 24VDC output.

04/20/2008 9:41 AM

Okay, if you need a simple and cheap load failure.

How about using a reed relay with a low resistance wound coil, to only drop ½ a volt or whatever, in series with the load, so any load holds the relay closed, when the load fails the relay opens?

What you do with the relay contacts is up to you?!

Cheap, simple, reliable, what more could you want?

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - New Member

Join Date: May 2006
Location: Montreal, Canada
Posts: 632
Good Answers: 11
#6
In reply to #4

Re: DC amp. sensor - digital 24VDC output.

04/20/2008 11:02 PM

Would a current mirror such as http://www.zetex.com/3.0/3-3-2b.asp?rid=120 work?

See this app. note: http://www.maxim-ic.com/appnotes.cfm/appnote_number/746/

Or High-side current sensing in Google.

__________________
''What the hell has my a** got to do with magic?" Don Quixote
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7
In reply to #4

Re: DC amp. sensor - digital 24VDC output.

04/21/2008 6:59 AM

You beat me to it again!!!! I wanted to write that!! All the other answers are simply too complicated for what is required.....

I gave you a GA for speed, not for the answer!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#16
In reply to #4

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 10:20 AM

What will the voltage drop be?

What is the Z of the coil?

What is the wattage rating of the coil? Can it handle a 50W load?

If you add a low ohm load in series, arent you adding load? and using more power?

Register to Reply
2
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#17
In reply to #16

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 11:06 AM

Crossfire, if the reed relay needs say 5 At to operate and you have a circuit with a minimum of ½Amp flowing you will need to wind 10 turns of copper a round the reed relay...

10 turns of thick copper wire has virtually no voltage drop.

The Z of the coil doesn't matter as its a dc system.

The power rating of the coil is immaterial due to being wound out of heavy duty copper wire.

Your last sentence is answered by the above!!!

John

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply Good Answer (Score 2)
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#18
In reply to #17

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 12:02 PM

Greetings Elecroman,

Please forgive me as I am unfamiliar with the reed relay you are referring to. The factory made, store bought relays I am failure with will not handle a 50W load in the coil circuit.

The input module jangkly is using is a Sinking DC input, so a relay or switch is a better solution than a direct input from a shunt. Contact closure is all that is required to satisfy the input as the module supplies the 24V used for current sink input.

BMXDDI3202K Modicon M340 Discrete DC Input, (32) 24 VDC, Sink (positive logic), IEC Type 3, 1-FCN type connector (40 points)

Register to Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#19
In reply to #18

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 2:20 PM

Ahh no problem Crossfire... the reed relay I mentioned is just a glass envelope with two contacts inside in a vacuum (very reliable), the contacts make a connection when in a magnetic field of a certain number of ampere-turns and so the coil can be wound to suit the application.

I've used them in all sorts of automotive sensing applications, for instance to sense when the cigar lighter is actuated - as the cigar lighter can easily take 15 amps, the coil around the reed relay can just be one turn of the supply wire - so very easy to fit, without breaking the supply wire etc...

John

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#21
In reply to #17

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 7:05 PM

Good answer, well put.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#20
In reply to #16

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 7:05 PM

You can actually switch a reed relay with a few turns of the wire going to say a lamp. Just the current of the lamp will activate the relay, almost unnoticeable in reality.......

Naturally, the thickness of the wire needs to be correct for the current as do the number of turns for activation....but they do not need much.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Apr 2008
Location: 66°N (almost)
Posts: 46
Good Answers: 1
#23
In reply to #4

Re: DC amp. sensor - digital 24VDC output.

04/23/2008 8:32 PM

Thank you Electroman, this seem to be a good solution. I was really looking for some unit that is ready to go -plug and play, but they all seem to break the 100$ barrier ae. Using reed relay´s I would need to make a circuit board and solder 6 relay´s on it and wire-connectors for the wires from the light switch and to the lights and for the wires for the switch´s on the relay. then put this in a box or some other suitable protection. This will take me a few hours and my time is money. Maybe it is possible to have this circuit made in china, Japan or somewhere over there for less. Do you have any recommendations for a company that will make a circuit like this? about 20 units pr. year.

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#24
In reply to #23

Re: DC amp. sensor - digital 24VDC output.

04/24/2008 8:52 AM

If you only need 20 a year I doubt if going to China would be economically feasible!

However, my business is used to making short production runs, whether its out-sourced or not, I'm sure I could quote a reasonable price...

It will depend so much on the environment they will be used in as well as safety aspects etc...

Contact me if you want me to look at a quote for you.

John www.marchdesigns.com

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#8

Re: DC amp. sensor - digital 24VDC output.

04/21/2008 12:29 PM

Try wiring a 8 Ohm resistor in series with the lamp. Now measure the voltage across the resistor with the light in the socket and energized, it should be around 5Volts with a 15 watt bulb that has 38.4 ohms and a current draw of .625A.

The addition of the 8 Ohm resistor will bring the loop total up to 46.4 so the lamp may not be as bright as before, but it should still light up.

A higher watt bulb will yield a higher voltage across the shunt, so you may need to add a small solid state voltage regulator to the output of the shunt to protect the PLC input channel.

The resistor is a shunt and will satisfy a 5Volt discrete input to a PLC. Write the logic so that it compares the input to the output, if both are high than all is good. If output is high and input is low than you alarm that a possible power supply or lamp faults.

If you must have the input high when the shunt is in a low state, use an interposing relay and a separate power supply to the N.C. contact and the input.

It may be a cheap fix.

Register to Reply
Associate

Join Date: Apr 2008
Location: 66°N (almost)
Posts: 46
Good Answers: 1
#9
In reply to #8

Re: DC amp. sensor - digital 24VDC output.

04/21/2008 5:28 PM

Yes this will work, but as you mentioned it will affect the voltage to the bulb´s and the bulb´s in this case are navigation lights on a boat so I don´t like to dim them down. Another thing in your solution is that my PLC is asking for 24VDC discreet input, this is Telemeanique Modicon M340 - BMX DDI 3202, the min voltage is 11VDC to ignite the input on this computer.

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Associate

Join Date: Apr 2008
Location: 66°N (almost)
Posts: 46
Good Answers: 1
#10

Re: DC amp. sensor - digital 24VDC output.

04/21/2008 5:33 PM

I thank you all for your comments but I think I found the best solution on www.a-a-c.com they produce DC-current detector with a internal relay contact.

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #10

Re: DC amp. sensor - digital 24VDC output.

04/21/2008 8:28 PM

Then you either did not read post #4, or you did not understand it!!!

That is the cheapest fix, the simplest fix and the one that uses less power than the others, basically no power at all!!!

It reminds me of the old proverb:-

You can lead a Horse to water, but he must drink on his own!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#13
In reply to #11

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 8:18 AM

Ah well Andy,.... "some words fell on stoney ground..." huh?

John

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #13

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 8:38 AM

Dead right.

The reason being I feel may be that the younger generation cannot imagine that such a simple fix is possible, without electronics, without extra power supplies etc etc....

I have used such relays in the 60s and 70s together with a small beeper to allow me to know if:-

1) Car Brake lights are both going on, or should I say, if one is on and the other is blown then beep.

2) Power is being applied to the brake lights when the pedal is depressed (to catch a blown fuse or similar). Beep if no power to brake lights.

It could not detect both lamps blowing at the same time, but as that is highly unlikely, I accepted that!! Nowadays cars have detection systems already built in!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - New Member

Join Date: May 2006
Location: Montreal, Canada
Posts: 632
Good Answers: 11
#15
In reply to #10

Re: DC amp. sensor - digital 24VDC output.

04/22/2008 8:39 AM

These look large and rather expensive.

__________________
''What the hell has my a** got to do with magic?" Don Quixote
Register to Reply
Associate

Join Date: Apr 2008
Location: 66°N (almost)
Posts: 46
Good Answers: 1
#22
In reply to #15

Re: DC amp. sensor - digital 24VDC output.

04/23/2008 7:08 PM

True, the price for those bastards is 120 - 150$ that is far to expensive for my application. They are also rather clumsy but I have enough space for 6 peaces.

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#12

Re: DC amp. sensor - digital 24VDC output.

04/21/2008 10:29 PM

What about of a Photo-resistor/diode or similar v. cheap light sensor which will watch Real Function of a Bulb, i.e. light production? Be sure to make logic with situation where Bulb is OK but is not energized (by PLC Output).

Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (5); CrossFire (3); Electroman (6); gigaconcept.com (2); jangkly (6); peterjohn (1); southern123 (1)

Previous in Forum: Transformer protection and CB discrimination   Next in Forum: 3 Phase power factor corrected rectifier

Advertisement