04/24/2008 7:55 PM
I'm sorry if this is too basic for all of you, but a friend of mine said I would be able to get an answer here. I have a float switch in my storage tank that tells my well pump to turn on at low level and off at high level. A couple days ago it stopped working and the only thing I could think of was that the wire has gone bad, or been eaten by vermin. Now I'm trying to find an easy way to figure out where the wire has gone bad, but its about 1.5 miles from the tank to the pump. The contractor that installed the well wants to charge me an entire days work to find the problem, and that doesn't cover fixing it, which he claims will take another days work at least. There has to be an easier way. Any good ideas? There should be a way to turn my pump on and off without having to run wire, but I asked the contractor and he was clueless.
Thanks,
Rob
Re: The wire that controls my pump has gone bad. Any good ideas on how to fix it?
04/24/2008 9:43 PM
When you say it stopped working, how do you mean? Are you saying that when the tank reaches low level that the pump does not kick on? Or do you mean that when the tank is full the pump does not kick off? Can you kick on the pump manually? Is there a breaker that might have taken the pump out?
I would suspect the float switch in the tank rather than the wire...
Might be at the connection to the pump... A continuity check with a 20 dollar multimeter from Walmart should be good enough to check the float switch.
Good Answers: 230
04/24/2008 11:22 PM
Hello rrb
I haven't seen the schematic of your system.
But if you have electric power at the pump, plus a separate control pair of wires run that 1.5kM to the header tank float switch, there is a far easier way to do the job, without any control wires to the header tank at all.
At the header tank, place a float valve (Ball-cock) so that when the tank is full the float shuts off the water inlet pipe from the pump.
Down below, at the well/pump location, install a pressure switch in the pipeline to sense water pressure in the pipe.
Some short calculation is needed to establish the normal pressure of a filled pipe, with the tank end open.
Set the pressure switch to cut out at some 25lbs per sq inch above the pressure of a full column of water.
Set the cut-in pressure of the pressure switch a few pounds per sq inch above that pressure of a full column of water.
Thus the situation could look like this:
Static water column pressure = 50 psi (pipe open at tank end)
Pump cuts out at 75psi
Pump cuts in at 55psi
As you can see, when the float valve/ball-cock shuts off, when your header tank is full, the pressure at the pump will swiftly rise, opening the pressure switch, the pump will stop.
As the water level drops, the float valve/ball-cock opens, allowing pressurised water to enter the tank, pipeline pressure is lowered, the change is sensed by the pressure switch at the pump, the pump switches on, and the re-fill cycle commences.
Dependent on your local situation, you may need to experiment, perhaps with a larger differential in switch settings.
If you use this system, ensure that a second pressure switch is wired in series with the first one above, as a safety measure, and the setting of that safety switch to open 20psi above the other.
The second (safety) pressure switch is to save pump motor burnout, in case of a malfunction with the normal pressure differential switch.
If you find the pump is cycling too rapidly, then you could use a variable time delay relay (experiment for local settings) in the control circuit, so that the tank water drops somewhat, before the pump switches on to fill the tank.
I've used this above system in many situations, over many years.
Trust I have interpreted your problem correctly, to give you an easy and cheap solution.
Kind Regards....
Good Answers: 19
04/25/2008 12:25 PM
Sparky - you spark. Yes this is alternate & cheapest way. He can first install a pressure gauge at the pump end and check both the pressure when tank full(cut off) and tank empty (cut in) and accordingly install a pressure switch to on/off the pump.
After acouple of trys he can get accuracy.
04/25/2008 12:42 PM
Sparkstation,
Thank you for your response. I think you have understood my problem and your solution seems logical enough (I kind of feel dumb for not thinking of using a pressure switch). I also wanted to know your thoughts about this: http://www.remotecontroltech.com/Applications/pumpcontrol.aspx
I did a search for wireless pump control and this seems like it would also work. Could you advise me on the differences between your solution and this solution?
Also, I think i need to find a new contractor.
Thanks,
Rob
Good Answers: 230
04/25/2008 7:10 PM
Hello again rrb
I've looked at that Wireless system, and it appears to be a good one.
Potential snags:
  1. Cost - considerably more than the pressure switch solution.
  2. Need for either electric Power to be run to tank, or solar power unit at tank.
  3. Solar power may be interfered with, by snow, dust, birds roosting, or debris on the panels.
  4. Ensure proper encryption of the transmitted information, otherwise nearby wireless transmissions could interfere with your pump controls.
I have always considered it's best to remember Murphy's Law, and use the lowest possible technology to achieve the desired result. As Systems become more complex, the chances of failure or mal-operation increase exponentially.
That's why I offered the pressure switch solution as the cheapest and best for your situation.
Visual checking System:
If your tank is visible in the daytime from your house or pump or easy access location, you could place a float with a wooden/plastic smooth-sided "marked with sections in different colours" rod/tube fixed to it, that rod/tube running inside a tube fitted to the tank lid.
As the water level lowers, the rod/tube will slide down through the fixed tube, and as the water level rises, the marked rod/tube will progressively extend upwards from the plastic tube so the rod/tube may be seen via binoculars from quite a distance.
Here we mark the rod/tube sectionally, top section of rod is red, next is amber, bottom part is green.
That way you can easily see the colour band, and extent of rod/tube above the top of the tank, which relates directly to the water level inside the tank.
A good pair of binoculars can see the status of the marked rod/tube, from several miles away, on a clear day.
Kind Regards....
04/25/2008 10:17 PM
Sparkstation,
Thank you for your help. The company that makes the wireless system said the MSRP for the system I would need was $1650. Luckily I do have utility power at the tank, but unfortunately I do not have a good line of sight from either the pump or my house otherwise the rod/tube idea would have been genius. Except I would still have to trek down to the pump to turn it on / off. How much do you think the pressure switch solution would cost? What about the point another poster (Steve i think) brought up about leaks between the pump and the tank?
I'll let you know what I decide to do.
-Rob
Good Answers: 230
04/26/2008 1:13 AM
Hello again, rrb
Twin Pressure Switch solution:
  • 2 No. Pipe tees.
  • 5 no. Pipe Nipples to suit.
  • 1 No. Pipe adaptor bush (if required to alter pipe size from switches to main pipe or point of sensing pressure at pump site).
  • 1 No. Roll Ceelon (PTFE Threadseal) tape.
  • 1 No. Pressure switch - Differential type.
  • 1 No. Pressure Switch - Safety type (cuts pump out at a higher pressure, if Differential Switch jams "On" with ball-cock valve closed at tank.
  • Electrical Cabling, and flexible conduit to Suit.
  • 2 to 3 Hours work by intelligent Electrician, to fit Pressure Switches, plus Wiring, and set up all.
  • Travel Costs for Electrician.
  • your own Costs for travel etc to obtain parts.
Cost estimate would be $100 to $120 for Materials, plus Electrician's Cost, and your own costs.
You say the tank is not visible from the house - Have you thought of installing a mirror, or two, to give you a view of a tank indicator rod, should you decide to install one. (Think laterally).
<"What about the point another poster (Steve i think) brought up about leaks between the pump and the tank?">
Yes, but there is always a leak potential problem in every plumbing situation, including your existing arrangement.
You could calculate your "normal" usage once the replacement system was set up.
Calculate how long the pump needs to operate, to completely fill an empty tank (Or up from the minimum you select).
Then add a timing relay, the setting of which disconnects the pump after 200% of that filling time has elapsed, and causes a light/hooter/alarm of some description to alert you that something is wrong - In other words, it makes a call for an intelligent person = your good self, or a useful neighbour.
If you were able to advise tank size, pump size, and place a few photos here, it would be easier to analyse your situation more correctly, and advise more completely.
Kind Regards from far away....
Good Answers: 25
04/26/2008 7:37 AM
Remote Control Technology might be expensive for your application, you need sytem for personal use. Spark's suggestion sounds economical also no electronics are involved which may give you problem latter on.
04/25/2008 1:07 PM
Sparky,
I like what you have suggested, but what if you get a small leak in the piping system? The pump might end up running all the time, whereas with his current rig it only pops on when the tank level is low...
04/25/2008 1:14 PM
I can turn the pump on manually, and the float switch seems to be working fine.
04/25/2008 1:43 PM
What did you do to check out the float switch? Are you saying that by pushing down on it the pump comes on? Or did you disconnect the wires, hook a multimeter to it and check that there was no continuity at high level position and continuity at low level position
I am sorry to be pesky, but one line answers on an internet forum are not helpful.. If we were talking face to face we could work through things efficiently, but here you really need to provide as much detail as possible so we don't have to guess and so we don't have to play 20 questions..
A good thorough description of the system would be a good start, including a schematic. You can put images in your post with the camera icon in the message screen.
04/27/2008 10:19 AM
Damned elegant that!
04/25/2008 4:31 AM
Like Steve S says..it's most likely the switch or a connector that has failed. Or a point where the wire is exposed...
You can check the whole wire run by dissconnecteing it completely at both ends.
Check with a multimeter that it is not short circuit (e.g resistance between the two wires should be high (greater than say 1Mohm)
Connect a 9volt battery to the two wire at one end...go to the other end and check the voltage with your meter...it should be somewhere near the 9v.
Good Answers: 19
04/25/2008 5:39 AM
Yes and your contractor is dumb.
BUT
Expensive
LS7000 RF Point Level Switch
Previous page
Description: The LS7000 is an excellent general purpose level control device. It can sense all liquids and the "difficult to measure" dry materials.
Operation: The probe uses a radio frequency balanced impedance bridge to detect the presence or absence of a product. Upon contact with the product, the probe's frequency is altered therefore signifying the presence of the product. The probe is supplied with an adjustable delay on or delay off timer. The timer is used to ignore wave action in a tank or control a pump using a single probe.
Specifications
Range:Function of mounting
Accuracy:Field adjustable
Temp range:Probe: -30 deg F to 450 deg F
Electronics: -40 deg F to 185 deg F
Temp compensation:N/A
Power source:115VAC, 50/60 Hz, 2 Watts Standard
(24VDC optional)
Output:2 Form C contact, DPDT relays
Mounting:1" NPT
Enclosure:Sensor: 316SS (Halar coating available)
Electronics Enclosure: explosion proof, copper free, cast aluminum
Pressure rating:1500 PSI @ 75 deg F
Enclosure approvals:Class I, Group D
Class II, Groups E, F, G
PDF Literature:
LS7000 RF Point Level Switch Specifications
Specifications subject to change without notice.
Good Answers: 266
Re: The Wire that Controls my Pump Has Gone Bad. Any Good Ideas on How to Fix it?
04/25/2008 10:42 AM
If i understand you right that your storage tank is a mile and a half from the well head. You suspect the wires running from the well head to the tank are bad. First I would check continuity of the wires between the well head and the tank. To make sure that is the problem.
I would find another contractor as i would have thought that the wires would have been buried deep enough to keep vermin from them.
It most likely quicker to run another line then to look for the break in the old one.
04/28/2008 2:25 PM
Why is vermin going around messing up this guys wires? I would think all that bouncing around would keep him busy.
I know the rumour is true. I started it and I don't think I would lie.
04/28/2008 6:29 PM
What do you think that fuzz ball is made of? Frayed wires...
04/25/2008 3:59 PM
Hey Del ..
Your idea is really clever...
Whoops..forgot to log out...
04/25/2008 4:35 PM
Hey Del, your idea is really clever... That guy Steve seems to be really helpful as well... I wonder why it is that Sparky gets all the glory. Maybe because he uses multiple emoticons and other graphic devices per post....
04/26/2008 3:17 AM
Hey Steve maybe we should quit this gig and go for a beer?
04/26/2008 9:16 AM
A wonderful idea... Especially if you are buying!
04/26/2008 6:01 AM
Why do you all want to make it so complicated?
You do not need an electrical float switch at all.
Assuming that you still have power for the pump at the pump itself (lay a new cable yourself if needed!!! or correct that problem in some way....) , buy an adjustable pressure switch, install it on the pipe going to the tank between pump and tank. Connect the pump motor to the pressure switch contact so that if pressure exceeds a certain (adjustable) limit, the pump will be switched off.
Put a non return valve between the pump and the pressure switch to stop water backing up when the pump switches off.
Install a toilet float valve in the tank at the level you want the water to get to, this will block off the flow when this level is achieved. Good ones are adjustable as well if needed. All are dead cheap.
Adjust pressure switch so that when the float seals off the water supply, the increase in pressure shuts off the pump.
Forget radio and contacts, go the simple way.
By the way, this system is used in many caravans and similar, the expansion in the hoses supplying a small reservoir of pressure to even things out. Even some houses in Germany where the mains pressure is not enough to have a proper shower, "suck" the mains to improve pressure in a similar manner, they have a built in adjustable pressure switch and one way valve!
Some caravans have a small plastic air pressure vessel to keep a larger volume of air compressed if needed in a more rigid system, to stop any possibility of water hammer....I do not think that you will need it with 1.5 miles of pipe!!
You may (should) have a non return valve already installed if you are pumping uphill, to stop the pipe (and the pump) emptying itself every time the motor stops, you may need to check this part out before going shopping!!!
Good Answers: 93
04/26/2008 8:43 PM
There may, or may not be, an easy cheap way to fix your problem.
The contractor that installed the well is professional enough to say he doesn't know exactly what the problem is.
Frankly, I don't either.
I don't know how old the pump is. Is the pump getting power or not?
Typically wires do not of a sudden go bad.
I first would ask the contractor to fix the problem for free if he discovers it was his fault that the pump quit working.
I think SparkStation knows what he is talking about when it comes to electricity.
Typically electricians are blunt and eccentric.
Do you know how to meter a circuit yourself?
It is likely that your electrician, or electrical contractor has a license to work.
It is likely he knows how long it takes to fix a problem if he has been working for a few years.
I doubt that the wire has gone bad. Sometimes it does happen that a wire is cut, or broken, but it is actually rare. Aluminum wire is more likely to be broken than copper.
If the pump is getting power from the wire, then the pump is suspect.
Of course the electrician does not know how to make the pump work without power.
A generator is an option to supply power to the pump without running a wire from the main breaker box.
The electrician may have thought of that on his way home, or later, but why should he call you with that option, since you seem to distrust him?
It takes what it takes and costs what it costs.
You don't get wise because you got old, you get old because you were wise.
04/28/2008 3:47 AM
Just a small thought. How high is the well head compared to the storage tank? In other words could you manage the water level entirely at the well end?