Conversion of Voltage of Frequency

05/21/2008 5:04 AM

I want to convert 415V, 50HZ, 3Phase supply to 460V, 60HZ, 3Phase Supply. The approximate load is 2500KVA. What is the method?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Conversion of Voltage of Frequency

05/21/2008 5:10 AM

Inverter + step-up transformer, though note that the higher voltage is only 11% of the incoming. Check the tolerable voltage of the load equipment and it may be that a transformer is unneccessary.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Conversion of Voltage of Frequency

05/21/2008 5:18 AM

Hello lmrmohan

The cheapest present method is a motor/alternator combination, which is able to cope with transients better than some large electronic frequency converters.

Refer: http://www.hzfrequencyconverter.com/

There are other makers of such equipment, and you could look here: http://electronic-components.globalspec.com/SpecSearch/Suppliers/Electrical_Electronic_Components/Power_Supplies_Conditioners/Frequency_Converters?SrchItem=1&frmqry=frequency%20converters%2050Hz%20to%2060Hz&kqid=53476264

You would need to register (free and 30 seconds) at globalspec.com, because that above Site is on a different Webserver from the CR4 Forum.

If you need further advice, please

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Conversion of Voltage of Frequency

05/21/2008 9:06 AM

The best method will be to use a MG set by using a motor to run from 60HZ supply and take an output from the coupled generator of 415V50Hz.This will give a cleaner supply as compared to a static system of rectifying and inverting.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Conversion of Voltage of Frequency

05/21/2008 8:38 PM

That's a lot of power to convert en-masse like that. I would evaluate each and every load on the 480V side to see if it really needs conversion. For instance, motors may or may not need conversion if you can live with the slower speed. I mention motors because you mention 460V, which is a motor utilization voltage, not a distribution voltage. 480V is the typical distribution voltage.

So that said, if you have some motor loads which will not run well at the slower speed, consider putting step-up transformers and VFDs on just those motors, even if you don't need to vary the speed.

Other loads, such as lighting, heating elements etc., or anything with a Switch Mode Power Supply (such as computers, consumer electronics etc.) will not care about frequency and may not care about voltage within 10% of nominal rating.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Conversion of Voltage of Frequency

05/22/2008 3:53 PM

That's a huge load to try and convert this way. Is your 460V load tolerant of running on 50Hz, if yes then you can just use a large transformer (about half the size of a 20 foot shipping container), if no then you really are left with a motor generator arrangement (say about the size of three or four 40 foot shipping containers).

This isn't a small or cheap project. Have you got your figures right? What's the actual application and load?

__________________
jack of all trades
Register to Reply