Cat 398 Generator w/ A Woodward egb-2p Governor /Actuator

06/04/2008 7:09 AM

Our orginal problem was that the generator breaker would trip offline but wouldnt secure the engine, long story short we swapped out the govenor and we couldnt get the gen. to start without lifting the governor arm and holding it in place. We swapped the gov. out again w/ another spare and the same issue. We tried to put the orginal gov. on and same issue. Here is what we have done so far. Any help would be greatly appreciated.

- On Sunday, 1 Jun, the #2 SSDG Switch Board breaker tripped off line, however the engine stayed running. We do not know the reason the breaker tripped.

- Engine appeared fine and switch board appeared fine. Tripped EG breaker and had #2 SSDG do a dead bus pick up. Engine responded fine and had no problem holding load.

- During resets, re-energized engine room supply fans. As fans were energized, frequency meter pegged below 58 Hz and then over shot to about 62 Hz before lowering back to 60 Hz.

- Paralleled #1 & #2 SSDG for night. No problems observed with maintaining load.

- Monday morning, EMs checked cables and connections for proper operation and loose wires. Found a couple loose wires and tightened. Ensured all governor controls were receiving and sending proper signals, no problems found.

- Singled up on #2 SSDG, with governor in electric mode. Stopped and started engine room fans, observed same behavior in frequency as night before.

- Paralleled #1 & #2 SSDG and repeated fan test. #2 SSDG and no frequency fluctuations.

- Repeated same test singled up with #1 SSDG with no frequency fluctuations.

- Singled back up on #2 SSDG & placed governor in mechanical mode. Repeated fan test, observed same behavior in frequency as Sunday night. The frequency dropped below 58 Hz, then overshot to above 62 Hz and then worked way back to 60 Hz.

- Because engine responded the same way in electrical and mechanical governor control, it was felt that the governor might be bad.

- Back round info... #2 SSDG just completed a center section overhaul on 25 April. Sent both #1 & #2 SSDG governors out to Sea Cost Fuel Injection (local company in Maine) for overhaul. No issues with #1 SSDG. Got u/w on May 18th and had no issues with #2 SSDG until 1 Jun.

- Pulled spare governor from stores & installed.

- Attempted to start #2 SSDG. Engine would not start. Air starter would spin engine up, but no fuel was being supplied.

- When started, governor actuator would not move the fuel linkage. Same situation in electrical or mechanical control.

- If you manually raised fuel linkage, engine would start, but as soon as you let go of fuel linkage, it would go back to min fuel setting.

- Thought governor could be bad, installed second spare governor with same results.

- Went back and installed original governor, same results happened as with spare governors.

- Disconnected fuel linkage from governor actuator. Started engine by manually holding fuel linkage. Governor actuator would eventually start to move after 3-4 seconds of engine coming up to speed.

- Broke oil supply line to governor and started engine. Appears to be sufficient oil flow to governor.

- Resealed oil connection at governor to ensure no air was being sucked in.

- It appears that the engine wants to start, but no fuel is being provided at start because the governor actuator appears to not be able to lift the fuel linkage. However, all electrical connections appear to be operating properly and the governor appears to have a sufficient oil supply.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2007
Location: Gulf Coast
Posts: 209
Good Answers: 7
#1

Re: cat 398 generator w/ a woodward egb-2p governor /actuator

06/04/2008 7:50 AM

Woodward is very particular about the oil used in their governors. What oil are you using?

__________________
In my many years I have come to a conclusion that one useless man is a shame, two is a law firm, and three or more is a congress. - John Adams
Reply
Anonymous Poster
#2
In reply to #1

Re: cat 398 generator w/ a woodward egb-2p governor /actuator

06/04/2008 8:08 AM

9250 feed from the l/o sump into an accumulator bottle then into the governor

Reply
Guru
Engineering Fields - Manufacturing Engineering - New Member Hobbies - Target Shooting - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Charlotte, NC USA
Posts: 791
Good Answers: 17
#3

Re: Cat 398 Generator w/ A Woodward egb-2p Governor /Actuator

06/04/2008 1:54 PM

I have a contact at Woodward, if you would like it, and I sent them a link to this post.

__________________
Be careful of what you wish for .....
Reply
Anonymous Poster
#7
In reply to #3

Re: Cat 398 Generator w/ A Woodward egb-2p Governor /Actuator

09/14/2008 1:08 AM

i am looking for a cat power unit if you know of some used ones please e mail me at

rascallfdrummer@yahoo.com

Reply
Commentator

Join Date: Nov 2007
Location: Western NC
Posts: 92
Good Answers: 3
#4

Re: Cat 398 Generator w/ A Woodward egb-2p Governor /Actuator

06/05/2008 8:11 AM

Sounds to me like the drive for the governer isn't right (something internal to engine that drives the governor). I can't say much more than that since my experience isn't with a Cat 398 (Cat 379B and GM DG sets) and it's been some time since I messed w/ a DG set (20 years). Is the governor gear driven or have a shaft that drives it that could be damaged, not letting the governor get up to speed? I would think it would be something with the engine itself since it has the same symptoms mechanically and electrically and with changing the governor.

Reply
Anonymous Poster
#5

Re: Cat 398 Generator w/ A Woodward egb-2p Governor /Actuator

06/05/2008 8:41 AM

Your tests were comprehensive.

It seems to be that you had an initial problem of maintaining 60HZ speed as load is taken up on the DG.

That problem may have progressed into another problem where the engine would nopt start.

What is your fuel filters condition?

Anf this may be a long shot on the frequency swinging problem: any checks on the voltage regulator?

What is the size of this generator anyway>?

Reply
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#6

Re: Cat 398 Generator w/ A Woodward egb-2p Governor /Actuator

06/06/2008 10:33 PM

Hi, Guest!

Fun in the engine room, eh? From what you have posted, I'm not entirely convinced this is an electrical problem. Here's what I would do:

Check the positioning of the governor with respect to the release of fuel to ensure it's defaulting at 15o before TDC before trying to readjust the arm. Also check the pattern of the injector spray in each cylinder.

Check & clean the splines on the oil feed.

Check the air supply to be sure it's unimpeded and (more than) adequate.

Check the fuel filters.

Check the heads (seals, burns, shape etc.) and rings (positioning & breaks/cracks) and condition of the cylinders (dirty, etched). Have you been using ether to start the engine? That'll kill the rings quicker due to banging from exploding fuel.

Mark

Reply