Anonymous Poster

Neutral cable size

06/30/2008 4:15 AM

We use 5 X 300 sq.mm cable per phase and 3 X 300 sq.mm for neutral for 1 MW, 400v,50HZ generator. Why the neutral cable size is so large and what would be the minimum neutral cable size in this case?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Neutral cable size

06/30/2008 7:41 AM

Consider there being a load imbalance across the three phases. What would the maximum neutral current be? The answer to this question dictates the minimum conductor size.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2
In reply to #1

Re: Neutral cable size

06/30/2008 8:21 AM

Is the neutral not a conductor should it not be the same size as the other service wires. Neutral just being a name assigned to it as it's potential is at ground.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3

Re: Neutral cable size

06/30/2008 9:10 AM

Shucks, I've seen engineers specify double the size of the phase conductors for neutral conductors, claiming it's needed to reduce harmonics in the supply transformer.

I'm an electrical engineer, and I'm not ignorant in power transmission and distribution, but I never have been able to convince myself that large neutral conductors will do anythinng to reduce harmonics. Maybe someone else who reads this post can enlighten me and you.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#4
In reply to #3

Re: Neutral cable size

06/30/2008 6:56 PM

Bill; the harmonics are from the loads, they generate additional current & heat, not the transformer, years ago the neutral insulation in 12/5 SO flexible cords used in computer applications dried up & crumbled from the heat, thus the super neutral was born, typically the next wire size larger is used. perry

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#7
In reply to #4

Re: Neutral cable size

07/01/2008 11:48 AM

Note taken . . . I understand the reason for the up-sized neutral conductor, but it's not, as electrical engineers have told me (and I'm one too), to reduce harmonics in supply transformers.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Neutral cable size

06/30/2008 8:24 PM

Guest,

Depending on the installation method for the cables, I also am surprised at the arrangement. Sizing a neutral at 60% the ampacity of the phase conductors is not uncommon. The others posting to this correctly point to the need to consider the unbalanced load and the need for safely carrying the harmonic currents imposed by non-linear line-neutral loads such as computers or electronic lighting ballasts.

If the phase cables are in separate conduits then the neutrals should be divided in the same manner, with 5 such cables sized each at 60% of the ampacity of the phase conductors. Then each set of phase conductors would have a neutral in the same conduit. Even if the conduits are non-metallic and proper methods are used to avoid magnetic induction where the conduits enter enclosures, the method you mention should have all sets of parallel conductors exposed to identically the same conditions (same cable type, insulation type, length, etc. for each set of conductors, as well as same number of conductors in each set).

--JMM

Reply
Anonymous Poster
#6

Re: Neutral cable size

06/30/2008 11:06 PM

Although neutral in 3 phase star connection which is the case in Generator is used to provide zero potential point, but due to unbalanced load neutral also has to carry the unbalanced load current (vector difference of the 3 phase current).

The size of neutral as per standard is half of the phase conductor but as far as depending upon the unbalanced current calculation, appropriate size has to be used.

IEC 60947-1, IEC 60439 - 1 suggese the size of conductor depending upon current

unbalance current can be calcuated as per

Iunbalaced = Ir + Iy + Ib

positive, negative and zero sequence parameters has to taken in to account.

my email id is divyesh_om@yahoo.co.in

for more details on fault calculation contact on email

Reply
Anonymous Poster
#8
In reply to #6

Re: Neutral cable size

08/03/2008 2:45 AM

Hi i am electrical technician as my experience with electrical cabling .

the Neutral cable size just depend to Unbalanced load .so some where for reduce the cost for cabling they are using 1/2 size for neutral in three phase line .

but in this case if they cannot balanced the load they must to use TNCS ground configiration for solve the neutral cable with 1/2 size for protect the Neutral wire .

Mohammd

mohammadahmad.jafari@hotmail.com

Reply