difference between 1000/5A C.T & 1250A/5A C.T

10/16/2008 2:32 AM

what is the difference between using 1000/5A C.T & 1250A/5A C.T, while measuring the output from a 1000A ACB

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: difference between 1000/5A C.T & 1250A/5A C.T

10/16/2008 3:53 AM

SORRY,

CAN YOU EXPLAIN WHAT YOU MEAN?

THANKS

Register to Reply
2
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2

Re: difference between 1000/5A C.T & 1250A/5A C.T

10/16/2008 4:14 AM

The reading at your meter will be different by up to 20%.

The 1000A/5A needs 1000A to deliver a 5A Full Scale Deflection (FSD) to measure on your Meter.

The 1250A/5A needs 1250A to deliver a 5A FSD to measure on your Meter.

So if you are using a 1250A/5A on a 1000A circuit you get a vaulue of 4A at the meter, using the 1000A/5A on the same circuit you get a value of 5A.

Obviously the actual figures will depend on the scale of the Meter as I would expect it to be calibrated to the values being read

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply Good Answer (Score 2)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#5
In reply to #2

Re: difference between 1000/5A C.T & 1250A/5A C.T

10/16/2008 5:35 AM

Hello Sapper

from me

Your answer says it all.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#3

Re: difference between 1000/5A C.T & 1250A/5A C.T

10/16/2008 4:52 AM

#2 is right. they have different ratio. and the later has a little more precision than the front and get less current from line.

Register to Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#4

Re: difference between 1000/5A C.T & 1250A/5A C.T

10/16/2008 5:13 AM

Hi drajesh1985,

The difference between using 1000/5A & 1250/5A CTs in metering shall result in correct/incorrect direct reading on the meter.

For example: Let us assume the load current is 600A, and the scale of your ammeter is 1000A;

Case # 1: Using 1000/5A CT

The Primary Current (Ip) = 600A

The Secondary Current (Is) = 3A, corresponds to 600A primary current. Accordingly, the meter shall indicate 600A, (correct direct reading).

Case # 2: Using 1250/5A CT

Ip= 600A

Is = 2.4A, corresponds to 600A primary current. Accordingly, the ammeter shall indicate incorrect direct reading. Therefore, you have to multiply the ammeter reading by a correction factor to get the correct one.

Regards,

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6

Re: difference between 1000/5A C.T & 1250A/5A C.T

10/19/2008 1:54 PM

There is no difference.You can use 1250/5 ct on 1000 amps Circuit.Only thing is the instrument connected to the CT should be calibrated for 1250/5 ct ratio,now a days the digital meters can be programmed for any CT ratios at site.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cnpower (1); ramvinod (1); Sapper (1); Sparkstation (1); TITO60 (1)