DP Gas Flowmeter

03/30/2009 9:08 AM

i have dp type gas flow meter i use 1151 dp transmitter which calibration range is 760mmwc.

actually my gas passes through 3.8 kg/cm2 at 33 deg. c. but reading in dp transmitter shows -0.4%. i check manifold and isolation valve also it is ok.

theoroticaly if we calculate for our gas consumption base it will appx. 292 mmwc. can you any body says why dp transmitter not shows reading.

i check dp transmitter also it is working perfecly if i isolate and give pressure for calibration range

thanks

hitesh

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: DP Gas Flowmeter

03/30/2009 9:30 AM

Is it installed the right way round?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#2

Re: DP Gas Flowmeter

03/31/2009 12:25 AM

Ditto to PW, seems like it might be hooked up backwards.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#3

Re: DP Gas Flowmeter

03/31/2009 2:10 AM

i check manifold and isolation valve also it is ok

Could you check them again? I once had a similar problem and I asked one of my technicians to check the manifold valves. He declared them as okay. Still the problem existed.

Later I learned that he had only checked if they were open or closed. During the next shutdown, I led another technician to pull out the manifold and inspect it.

The equalizing valve was broken. It was allowing the pressure in both ports to equalize (more or less).

And just to give me peace of mind:

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

betomachine (1); PWSlack (1); Vulcan (1)

Previous in Forum: Solenoid Valve (SOV) Signal Options   Next in Forum: Compressor Load Sharing

Advertisement