Three Wire RTD Connection

04/24/2009 2:22 AM

Three wire method of connecting an RTD is popular as the calibration is relatively immune to the distance of the RTD from the signal conditioner (henceforth refrred to as SC). The method utilises the drop in one line to cancel the drop in another line. Consider that a two wire RTD is all that you have and is at a distance of 1 metre from the signal conditioner. Consider that it is excited by a current Iexc. (Bridge method is discussed later). Normal measurement will result in error due to the resistance of lead wires W1 from SC to Hi and W2 from SC to Lo of RTD. If you now have an additional wire W3 to the low end of the RTD, which is used to "return" the current Iexc (fed to RTD) at SC end, you have a three wire conifuration that yields two voltages at the SC end, from the RTD, viz, "elow" through W2 from the lo end of RTD, and "ehi" from the Hi end. If elow is fed to high impedance amplifier, there will be very little current in W2. This is how this three wire works!!.

The aim is to measure the voltage Vrtd across the RTD.

This is obtained as ehi - 2*elow. At the SC end twice elow is subtracted from ehi to get the voltage Vrtd across RTD without error. The assumption, a very valid one, is that resistance Rw3 of wire W3 is equal to resistance Rw1 of Wire W1.

Example: If Res of RTD is 175.8 ohms and Iexc is 1mA, Vrtd will be 175.8mV. If Rw1 = Rw3 = 1ohm, then elow will be 1mV being Iexc*Rw3. However

ehi = Iexc*Rw3 + Vrtd + Iexc*Rw1

since the excitation current flows thorugh W1 and returns through W3. The voltage returned by W2 is elow. This is same at both ends.

elow = Rw3*Iexc.

The operation at SC, ehi - 2*elow yields Vrtd if Rw1 = Rw3.

RTD end SC end

Loside = Rw3*Iexc elow = Rw3*Iexc

Hiside = Rw3*Iexc+Vrtd ehi = Rw1*Iexc +Vrtd+Rw3*Iexc

Note: If a bridge configuration is used, RTD forms one arm and a resistance say Rx is used at SC end to form an equivalent arm. In this case Rx should be connected to W2 at SC end while W3 "returns" the total current back from the RTD end. If each arm of bridge carries 1mA, current in W3 will be 2 mA. For zero error, Rw1 should equal Rw2 in this case. The bridge output after conditioning in SC remains unaffected by low (but equal) values of Rw1 and Rw2.

__________________
Consultant
Register to Reply
Pathfinder Tags: three wire RTD
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: Three wire RTD connection

04/24/2009 3:11 AM

If you could post a drawing, I might be able to understand what you're getting at.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Participant

Join Date: Apr 2009
Posts: 4
#2
In reply to #1

Re: Three wire RTD connection

04/24/2009 4:31 AM

Figure showing connection of an RTD at a distance of 1metre

A current of 1mA flows from SC to RTD Hi through W1. At eHi, voltage is higher thatn at RTD Hi by the drop in this wire. (RTD Hi has a voltage of Vrtd +elow.

The same current returns through W3 to common of SC (which provided the excitation current)

W2 just provides the same voltage as available at RTD Lo to signal conditioner! No voltage drop in this wire!!This voltage is Iexc*Rw3.

__________________
Consultant
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Three wire RTD connection

04/24/2009 5:32 AM

Er, and?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Apr 2009
Posts: 4
#4
In reply to #3

Re: Three wire RTD connection

04/24/2009 7:04 AM

Current source operated and bridge configured RTD's with

3 wire connection :

__________________
Consultant
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#5
In reply to #4

Re: Three wire RTD connection

04/24/2009 8:12 AM

I've found that people find it easier to understand when you present them with a simpler concept. I usually use this one:

Just measure the resistance across A and B (RAB) and then measure the resistance across B anc C (RBC). Then subtract the two resistances and the result is the resistance of Rrtd.

This is valid only if R1, R2 and R3 are all equal, which is why they always say that the three wires in an RTD circuit should be the of the same length to ensure that they have equal resistance.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Three wire RTD connection

04/24/2009 9:13 AM

Now, that makes a lot of sense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Three wire RTD connection

04/24/2009 9:13 AM

And?

Come on. Where's the punch line?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#9
In reply to #3

Re: Three wire RTD connection

04/24/2009 9:35 AM

Ahhh . . . I finally figured out that venku isn't asking a question! He's just spreading his knowledge around for the rest of us!

Thanks!!!

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Associate

Join Date: Jul 2007
Posts: 26
Good Answers: 1
#13
In reply to #2

Re: Three wire RTD connection

01/15/2012 10:35 PM

Hi ,

We have a 12.5 MVA 34.5 kv / 4.16 kv Power transformer , which has a 3 Wire RTD for Oil temperature monitoring . The transformer is working fine about 65 % only loaded , no abnormal current raise , no faults on the load side recently , the temperature of oil is about 54 Deg C for the last two weeks , as displayed in the DCS trend.

The problem is the transformer tripped on Oil temperature high ( Trip set at 90Degs C ) , though the DCS trend couldn't capture it but the DCS alarm summary has a record stating that the oil temp went high to 106 Deg c suddenly for a fraction of a second and returned back to normal temperature .

During the investigation found all ok with the trip circuit loop , no abnormality of loose termination or a malfunction of Temp monitor controller etc.,. Only thing which was noticed is that though the 3 wire RTD ( 10 Copper ) is connected properly , the cable shield is left ungrounded .

The question is , Can this signal wire pick up stray noise and make the temperature raise to 106 Deg C momentarily and that resulted in a trip ? Is it necessary to ground the shiled of the signal cable ?

Can we conclude the non-earthing of the RTD cable could be the cause for the trip of transformer ? Otherwise , the electrics are perfectly ok .

Request those experienced to offer valuable feedback .

Thanks and best regards,,,,,

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#8

Re: Three Wire RTD Connection

04/24/2009 9:19 AM

Are you selling something, or is this just a random outburst?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Anonymous Poster
#10

Re: Three Wire RTD Connection

04/25/2009 11:21 AM

Thanks Venku about RTD Informartion...........

Register to Reply
Participant

Join Date: Apr 2009
Posts: 4
#11
In reply to #10

Re: Three Wire RTD Connection

04/27/2009 1:53 AM

Wow! Thanks. That makes the whole effort worthwhile.

A point to note is that this technique is useful not only for unknown (but equal) lead resistances but also for their temperature variations. Generally copper wires are used, and copper has a positive temperature coefficient of about 0.4% per degC. Since all wires will have a higher value at a higher temperature, temperature effects are also minimized by this philosophy.

__________________
Consultant
Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#12

Re: Three Wire RTD Connection

04/27/2009 5:55 AM

??

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (1); JohnDG (1); naveen_menon (1); PWSlack (3); venku (3); Voltamps (1); Vulcan (2)