Motor Rewind Question

05/05/2009 10:03 AM

We purchased a homogenizer as part of lot of equipment from a business that purchased it from a dairy years ago (they got it with a "whole lot" purchase, too). It has been sitting unused inside for 15 years and maybe longer at the dairy, but I believe it was in use at the dairy.

The motor nameplate says GE 40hp, 404 Frame, 3ph. The original volts [230/460] and amps [(about) 97, 43] have been "xxx" out and new values have been stamped as 550V / 39.5A - so, I am assuming a rewind at some point. Motor looks good, I'm guessing that the rewind was to accommodate a voltage requirement (is 550 standard in some places? I'm familiar with 575)?

I need to use 230, 3ph here.

I'm looking for comments and advice on whether to rewind or buy new, or any comments you feel pertinant.

__________________
If you understand everything, you must be misinformed - Japanese Proverb
Register to Reply
Pathfinder Tags: advice motor Rewind
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Motor Rewind Question

05/05/2009 10:13 AM

If the motor has had a dubious, or even unknown, history, it may be worthwhile considering a replacement motor of the correct voltage, for warranty purposes alone. A machine breakdown may have an effect that is worth far more than the replacement value of the motor.

As always, the value calculation is to be performed locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4
In reply to #1

Re: Motor Rewind Question

05/05/2009 9:06 PM

Or the cost of a rewind. You make good sense with your statement.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Participant

Join Date: May 2009
Posts: 2
#2

Re: Motor Rewind Question

05/05/2009 6:35 PM

Hi, it seems that you have a medium size DC motor they run on that voltage 550

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Motor Rewind Question

05/05/2009 7:56 PM

Those voltages, 550 and 575, were very common industrial voltages in Canada in the old days. These systems were delta with either one phase grounded, called a "corner ground", or with no phases grounded. These systems have mostly been replaced with 347/600 Y 4 wire systems, but I bet there are loads of legacy 550 and 575 volt delta systems around.

If you do not wish to rewind the motor back to 230/460, you could always check with some of the Canadian surplus dealers if you need a transformer for use with this motor.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#5

Re: Motor Rewind Question

05/05/2009 10:45 PM

It might be wise to open up the ends and replace the bearings, as 15+ years of slow oxidation might give you a motor that starts and soon fails after the correct transformer is found.

What you need is a 3Ø transformer from voltage 1 to voltage 2 of the correct HP rating.

you might also want to have what is called "isolation", as this might be a requirement in the dairy business. I have heard of herds of cattle connected to milking machines all being electrocuted at the same time by a ground fault.

Check the cost of a fixed transformers cost, and see what variable 3Ø autotransformers cost. The variable will allow assorted voltages to be made for various motors you may find. It may be cheap enough to buy a new motor or ask a motor shop to rewind it as a custom motor.

Here is a link batch for that subject.

http://www.google.ca/search?hl=en&q=3+phase+transformer&meta=&aq=4&oq=3+phase

And times change, and sanitary equipment made 20-40 years ago might not be approved for direct food contact these days

__________________
Per Ardua Ad Astra
Register to Reply
Associate

Join Date: Jan 2008
Posts: 32
Good Answers: 1
#6

Re: Motor Rewind Question

05/05/2009 11:27 PM

A/B,

The 404 frame indicates a rather large frame size for only a 40HP. I am assuming that you are talking of using 230 3Ph AC; in this case, 404/405 frame motors start a low of 50HP (Siemens IEEE841). Also, you did not indicate RPM, and 404/405 motors are generally rated at 900 or 1200 RPM. 404/405's list a shaft size dimension of 2.875 with exception of the 404/405TS (short shaft / 3600 RPM), which is 2.125.

What is your application? Do you need a ball bearing drive end or tapered bearing drive end? Chemical environment? These are things that will determine if you have a "bargain" or need to look elsewhere. Incidently, if I were going to take a motor that had sat up for years and rely on it for production, I would most certainly have it rebuilt (including checking the iron, baking and stator checks)...and all of these, do not make for a cost effective solution for only a 40HP, unless of course it is a special application and a replacement is not available.

let me know if we may be of assistance / old golfer

Register to Reply Score 1 for Good Answer
Member

Join Date: Mar 2007
Posts: 6
#7

Re: Motor Rewind Question

05/05/2009 11:52 PM

Suggest you run the motor on no load and measure current if you have a supply of 575V

Remove the ensdshields and examine the leads that are connected to the winding. From the connections you will be able to see if the motor is converted to higher voltage by reconnecting the leads. If this is the case, motor can be reconnected to 230/460V.

Otherwise it has to be completely rewound which can be done.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: Motor Rewind Question

05/06/2009 4:32 AM

Buy a new replacement motor, whatever you pay out on the old one still means you still have an old one.....

Plus if the "repaired" one breaks and you have to buy a new motor, that "repair" money will be strongly regretted!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#9

Re: Motor Rewind Question

05/06/2009 5:41 AM

I am interested where you will get the new brushes for the motor.

I have and old meat grinder.

__________________
If you never do anything you never have problems.
Register to Reply Off Topic (Score 5)
Associate

Join Date: Jan 2008
Posts: 32
Good Answers: 1
#10
In reply to #9

Re: Motor Rewind Question

05/06/2009 9:04 AM

You can get brushes from www.helwigcarbon.com out of Milwaukee, Wisconsin; and they can be ordered online.

In the motor business, they are one of the primary suppliers for old DC components.

old golfer

Register to Reply Off Topic (Score 5)
Register to Reply 10 comments

"Almost" Good Answers: