Problem With Simultaneous Use of Generator and Motor

07/29/2009 12:03 PM

I installed a 110kw motor with a Star/Delta panel, but when ever it was switch on it will shut down the 250 KVA 397Amp generator.Reading high amps at 400amp. It happens because of moisture, so I took it and it was rewind, but when connected again its reads High amps at 360amp. What will you advise

Regards

Aishaamadumariama

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: Problem With Simultaneous Use of Generator and Motor

07/29/2009 12:26 PM

Its a fair chance the motor starting power and current is beyond the maximum capacity of the gen set. Many induction motors take 3 -6 times their rate amps while during that initial start up period.

As I learned it many years ago if a motor does not have a soft start or some type of controlled ramp up to limit its starting surge the generator needs to by about 4 times larger (some times even more) than the motor its running.

I have a old military surplus 10 KVA three phase gen set that has a 15 KVA surge rating but it can just start a 5 HP (3.7 KW) motor under normal load. However once the motor is up to speed the generator doesn't even notice it. If I run the power through a VFD unit and limit the starting power the old gen set can easily start and run a 10 HP (7.5 KW) motor at full load.

Its likely your gen set is not able to start that big of motor with what ever load its carrying or your over current protection system doesn't have a large enough surge capacity or time lag to allow for a full start cycle to happen.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Jul 2009
Posts: 33
#4
In reply to #1

Re: Problem With Simultaneous Use of Generator and Motor

07/29/2009 1:34 PM

What is this VFD Unit you are talking about and do you go about to connect it if available and secondly can wrong connection of the Mains cable cause the motor to read high Amps?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: Problem With Simultaneous Use of Generator and Motor

07/30/2009 3:21 AM

The term VFD is an abbreviation for Variable Speed Drive. It is a piece of electronic equipment that can be programmed to start a 3 Ø motor slowly, and if correctly programmed will enable the selected generator to start the selected motor. They are available off-the-shelf in many places and retail outlets on the web are manifold.

The problem is very unlikely to be related to the way the mains cabling is connected, as any problem would reveal itself by opening the circuit protection device(s).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #1

Re: Problem With Simultaneous Use of Generator and Motor

07/31/2009 9:21 AM

GA from me......Well described as well.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#2

Re: Problem With Simultaneous Use of Generator and Motor

07/29/2009 12:26 PM

How did you come to conclusion earlier that it was happening due to moisture?

110KW in what mode star or delta?

How your panel is starting motor with star or delta?did you checked?

whats the starting load on motor?

Is motor picking it rated speed? if yes in what time?

Did you tried motor by removing coupled load on it?

Did you checked actual motor current with a clamp tester on each phase?

Register to Reply
Associate

Join Date: Jul 2009
Posts: 33
#3
In reply to #2

Re: Problem With Simultaneous Use of Generator and Motor

07/29/2009 1:27 PM

In answering to your question, the area were the motor is house was overflooded with water thus covering the motor and it was switch on after the water had been clear failng to service the motor, thats brought about its rewinding.11okw is at the mode of 380-415v. The panel starts motor by switching on with a press botton for Star and after 4sec or what ever sec you set it its switch over to Delta state and the starting load is 223amp. It does not run to its pick speed after which the Generator goes down, but during that starting time we check each of the cable with a Clamp meter and also the Panel Amp meter indicates the same amperage as the Clamp On meter 360amp

Register to Reply
Member

Join Date: Apr 2010
Posts: 5
#12
In reply to #2

Re: Problem With Simultaneous Use of Generator and Motor

04/14/2010 11:24 AM

Respected sir,

Thank you very much for your guidance.

I come to know the factors to be consirdered.

Thanking you.

S.S. Magdum

Register to Reply
Participant

Join Date: Jul 2009
Posts: 1
#5

Re: Problem With Simultaneous Use of Generator and Motor

07/29/2009 3:23 PM

A 110kw motor will have an average of full load current of 150A. Now that at starting it will require atleast 4 times its full load current. Hence only a Genset rated 600A and above will be able to handle it

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6

Re: Problem With Simultaneous Use of Generator and Motor

07/29/2009 11:14 PM

General rule of thumb in selection of DG sets for motor application, the starting current of the motor should not exceed 2 times the full load current of the DG set.

May be in your case while 110 kw motor starts the the starting current is more and in effect the DG set is bound to deliver more than 2 times the full load current, in which case there will be voltage dip and motor trips.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#8

Re: Problem With Simultaneous Use of Generator and Motor

07/30/2009 7:46 AM

The question is:

Did the generator work with the generator before the unit was flooded?

If the answer is yes, then what is damaged that was allowing it to come on line before the flood? I would look for a capacitor bank or some sort of control device.

If the answer is no, then read what everyone else is trying to tell you.

I agree with Tcmtech, good answer by the way, but remember he stated you could use a VFD or some other method of soft start or ramping up. A soft start device could be less expensive than a VFD and might be better suited to a genset type setup.

Register to Reply
Associate
United States - Member - Member Engineering Fields - Power Engineering - New Member

Join Date: Jun 2007
Location: Texas
Posts: 52
#9
In reply to #8

Re: Problem With Simultaneous Use of Generator and Motor

07/30/2009 12:01 PM

A fairly simple thing you could try is to use an uncoupled motor as a flywheel. A running motor will have an amount of stored energy proportional to its stator magnetic field and its mechanical inertia. When the second motor is started the first will help to supply a small part of the inrush current. Plus having a load on your generator will get the governor up off of minimum. Most gen-sets are very sluggish and sometimes even sticky when they are at minimum output.

Register to Reply
Associate

Join Date: Jul 2009
Posts: 33
#10
In reply to #9

Re: Problem With Simultaneous Use of Generator and Motor

07/31/2009 1:59 AM

Gentlemen thanks for your valuable contributions, as they help me a lot arriving at a conclution after series of test. The Generator can not withstand the starting torque/starting current of the motor. its small for the motor.

The said motor had never been run with the 250KVA Gen.set. Its only after it had been flooded with water that they try to switch it, when open its still fill with water. Now that it has been rewind, I switch on/off, on/off, three times and on the fourth tme after it gain its speeds, it run it for 4-5 minutes then Gen.set start to go down gradually, then OFF.

Our recommendation is to go for 500KVA -- 650KVA Generator when considered the rapid growing of the company

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aishaamadumamariama (3); Andy Germany (1); dennis mandalazi (1); GRAY HAIRED OLD GOAT (1); jconn_ETEC_05 (1); magdum.shirish (1); PWSlack (1); rakesh_semwal (1); ramvinod (1); tcmtech (1)

Previous in Forum: Dielectric Withstand (Hi-pot) test spec?   Next in Forum: Rotor Insulation IEEE 43

Advertisement