Hi,

If we have an absorption chiller say with a capacity of 100l/s chilled water flow rate & 7 deg the supply temp/outlet temp from the chiller. From this 100l/s if we take one branches of 25l/s to an electric chiller in series & drop down the temperature for this 25l/s flowrate from 7 to 4 deg c. After this if the both both flow rates that is 25l/s @4 deg c & the remainig 75l/s @ 7 deg c from absorption chiller if mixed again in one header to take it to the AHU'S/END USER What will be the temperature of this mixed flow.

With your answer. please give the formula that is been used.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Temp for mixed flow - Chilled water.

09/05/2009 6:22 AM

((75 x 7) + (25 x 4)) ÷ 100 = 6.25° (assuming the temperatures are still 7° and 4° where the mixing happens).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#2
In reply to #1

Re: Temp for mixed flow - Chilled water.

09/06/2009 8:33 AM

and it is assumed that the density and specific heat remains unaltered for the coolent at 7C and 4C. This may not be the case for water. However, this calculation sure is a good rule of thumb to get neat to actual value.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Anonymous Poster
#3

Re: Temp for mixed flow - Chilled water.

09/06/2009 11:24 AM

If there is no hitch in this problem, then the temperature of the mixed flow will be

(75*7+25*4)/100= 6.25 deg.

Regards.

Anant

Register to Reply
Guru
Brazil - Member - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - RC Aircraft - New Member Hobbies - Target Shooting - New Member Hobbies - Automotive Performance - Hey there... interested in exchanging information about car performance? Hobbies - DIY Welding - New Member

Join Date: Jan 2007
Location: Porto Alegre - RS - Brazil 30deg01'39.73"S 51deg13'43.45"W
Posts: 831
Good Answers: 28
#4

Re: Temp for mixed flow - Chilled water.

09/07/2009 6:21 PM

Consider calculating it in absolute units, this is the way it should be done.

(75 l/s x 280.15K + 25 l/s x 277.15K) = 100l/s @ 279.4 K or 6.25 degC

COnsidering no losses, fluid properties constant, etc.

__________________
Humm... suspicious you are...
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#5

Re: Temp for mixed flow - Chilled water.

09/08/2009 8:34 AM

Am I the only one who thinks this sounds like homework?

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Temp for mixed flow - Chilled water.

09/09/2009 7:12 AM

Ignoring the variation of density of water with temperature, 61/4degC, by simple proportion.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bhrescobar (1); JohnDG (1); Mikerho (1); PWSlack (1); Shyam (1)

Previous in Forum: Pressure Vessel designing?   Next in Forum: job opportunities for mechanical engineers..??

Advertisement