50-Amp AC Breaker Keeps Tripping

09/14/2009 12:51 PM

Hello Folks,

AC breaker 50amps Keeps tripping every 3 days If the circuit, the amperage, the size of wire is alright for this RTU, what could be making the circuit breaker which is a 50amp breaker, trip? What would be the risk of replacing it by a 60 amp breaker if the AWG allows it?

__________________
Naviero
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#1

Re: AC breaker 50amps Keeps tripping every 3 days

09/14/2009 1:06 PM

Circuit breakers wear out. If the current is close to the CB rating or if loads from a motor momentarily exceeds the CB rating on starting, this shortens it's life. Replacing it with a larger breaker is not a good idea unless the wire is large enough to handle that current. The breaker is on a 220 V circuit right! A 2-pole breaker should be powering only 220 V appliances. If you are tapping 110 V off the 220, you may be creating an imbalance that causes a higher voltage in one leg and a lower voltage in the other leg.

__________________
Mr.Ron from South Ms.
Register to Reply
Anonymous Poster
#2

Re: AC breaker 50amps Keeps tripping every 3 days

09/14/2009 1:32 PM

Also check the specifications on your air conditioner. If the label is worn off, you might be able to look it up on the manufacturer's web site. There should be a maximum breaker size specified, and you shouldn't exceed that even if the wiring can handle more current. If the breaker is tripping, but seems to be the correct size for the A/C unit, either the breaker or the air conditioner is worn out.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#3

Re: AC breaker 50amps Keeps tripping every 3 days

09/14/2009 2:10 PM

Have the same problem on a chiller (50 A class C MCB of its compressor) - suspect supply voltage at nights 1. goes up, or 2. goes down. Also, may be a bad contact somewhere in the contactor coil's circuit making the contactor pulsate frantically leading to the MCB's trip.

Register to Reply
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: 50-Amp AC Breaker Keeps Tripping

09/14/2009 4:32 PM

Take a clip on amp meter and see exactly what the load realy is.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Nov 2008
Location: Las Vegas
Posts: 16
#5
In reply to #4

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 12:10 AM

I just did it today, the loads variate in each face 16 to 17 amps, it's a 50 amp breaker. It trips every 3 to 5 days, I don't believe its the breaker I've had issues with breakers of this kind only 3 times, and they usually trip in a very short period of time after being turned on. In this case it takes days, also, there are no junction boxes in between the run, it's straight cable with no splices in between. I'm guessing something could be wrong with the AC unit, or roof top UNIT.

__________________
Naviero
Register to Reply
Active Contributor

Join Date: Nov 2008
Location: Las Vegas
Posts: 16
#6
In reply to #5

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 12:10 AM

*PHASE

__________________
Naviero
Register to Reply
Associate

Join Date: Jan 2008
Posts: 34
#7
In reply to #5

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 1:59 AM

Well, find out. Get a megger and test it, just to be sure.

Register to Reply
Commentator

Join Date: Aug 2009
Posts: 91
#8

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 4:39 AM

what i understand from this discussion that either to check the total current or increase it by 125% but make sure that it is less then the 80% capacity of the cable ....

---------------------------

__________________
Correct me if i am wrong i am learner
Register to Reply
Power-User
Hobbies - Musician - New Member Engineering Fields - Manufacturing Engineering - New Member

Join Date: Sep 2007
Location: Endless Mountains of NE Pa, USA
Posts: 298
Good Answers: 20
#9

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 5:11 AM

You could also rent a line analyzer/plotter that will plot voltage and current over time. Usually available at an electrical supply house in your vicinity.

Just another avenue to explore.

__________________
Courage is not the absence of fear, but the inner resolve to rise above it....or the inane lapse in judgement brought on by copious imbibitions....Egre Flagrus
Register to Reply
Anonymous Poster
#10

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 8:22 AM

Have seen the same problem befor. you need to change the breaker to a new 50amp and then instal a soft start kit on the compressor. some times when the compressor starts under high head pressure it will cause the breaker to trip. the soft start kit will stop this problem.

Register to Reply
2
Member

Join Date: Sep 2009
Posts: 9
Good Answers: 1
#11

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 11:28 AM

Hola

As far as I know, these breakers are Thermomagnetic devices.

The thermal part of these breakers are to protect a device against a constant electric current flow around 50 amperes in this case. if this is the case, trip.
the thermal part of the breaker, which is a bimetal, may be deteriorated over time. This deterioration is due to the constant heat, not overheating, but by the constant flow of electric current. (Change their physical characteristics).

The magnetic part of these breakers are to protect a device against instantaneous electric currents over 50 amps in this case. if this is the case Trip.
the magnetic part of the breaker, is a small coil,

so probably the "bimetal" which forms the thermal part of these breakers may have deteriorated over time. so now fails. (Every 3 days Trip).

You can check this breaker but you need measurement tools.

Otherwise you can rent, as they recommend, a plotter to plot the current and voltage. to verify what happens to the electric circuit. but if the plotter has a poor response may not be plotting current or voltage peak.

May also be occurring to the pipe through which pass the wires have water or moisture which would make sporadic small electrical short circuit. so the breaker trip.

Also, the device Protected by this breaker could have some electrical problems which cause the breaker will trip.

I hope to contribute to the solution
greetings

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#12

Re: 50-Amp AC Breaker Keeps Tripping

09/15/2009 1:57 PM

I recommend that you diagnose the problem before taking corrective action.

Yes, increasing the breaker size might cause the breaker tripping to cease for a while, but if you have only masked over a developing problem, you may have only succeeded in delaying what will become a much bigger and expensive repair when the problem fully develops.

You have been presented an opportunity to prevent a larger problem, sort of like a doctor that catches cancer in the early stages from a few small indicators, and rather than prescribe a pain killer to mask the symptoms, he sends the patient in for a few tests.

Some of the available methods have been suggested. I also recommend a thermal imaging camera, or in the least a non-contact thermometer (much less expensive).

From the evidence, it seems you are dealing with an overload that requires time to build up sufficient thermal action in the breaker, so you could periodically check the breaker temperature. Also, in the few minutes immediately following a breaker trip, you can check for excessive heat in the major devices, motors, compressors, controllers and switches etc.

Shade tree (back-yard) mechanics change out parts by pure guess until the problem goes away. Professional mechanics let the diagnostic tools do the guessing for them.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply Score 1 for Good Answer
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#13

Re: 50-Amp AC Breaker Keeps Tripping

09/17/2009 4:15 PM

naviero1 - I don't know if you fixed problem yet, but, will post anyway. I noticed you are from Lost Wages where it is still possibly very warm. Please use the simple approach first, before you redesign the system. The condenser could be dirty enough to raise the amperage. If single phase, capacitor could be bad slowing fan down. Bearings in fan motor could be starting to wear (raising amps & discharge temperature). See what i mean? More than likely the breaker was installed per design along with wire sizing. Though i have seen electricians cut corners and/or engineers not considering Nevada temps in design, etc.

Register to Reply
Active Contributor

Join Date: Nov 2008
Location: Las Vegas
Posts: 16
#14
In reply to #13

Re: 50-Amp AC Breaker Keeps Tripping

09/17/2009 5:30 PM

Yeah, it could be, right now I have an AC tech checking his equipment, I'm in charge mainly of the electrical systems before the AC. It's a straight run with no splices in between the breaker, which is a 3 pole 50 amp, and the breaker at the AC unit. I've had really good answer pointing that it could be the breaker itself, I'm not quiet sure yet.

__________________
Naviero
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#15

Re: 50-Amp AC Breaker Keeps Tripping

09/22/2009 1:47 PM

One other thing I would check; is the breaker commercial or consumer grade? I believe there is a difference in the cycle life. A mil-spec device will last much longer than a consumer device. Take wall switches or receptacles for example. You can buy one for 29¢ or $5.

__________________
Mr.Ron from South Ms.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: 50-Amp AC Breaker Keeps Tripping

08/22/2024 7:26 AM

Replace it like-for-like. Destroy the old one; it's knackered.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard