Loop Testing Procedure for Non-SMART Transmitters

09/17/2009 5:44 AM

Dear All,

I read a standard with reference to the "Loop testing procedure for NON-SMART Transmitters" and it states the following steps,

  1. Disconnect the signal wiring at the transmitter terminal and connect a 4-20 mA signal generator to the signal wire.
  2. Simulate 0, 50, 100% signals and confirm the reading at the receiving end.
  3. Restore the current wiring to normal after the test.

I just wanted to know if this procedure is the correct one and the only one available since we ISOLATE the transmitter and it is more of a continuity test than a loop test (especially when we compare it with a SMART Transmitter one).

Thnx in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Loop testing procedure for NON-SMART Transmitters

09/17/2009 7:59 AM

How else would you check loop integrity, regardless of isolated transmitters or not?

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#2
In reply to #1

Re: Loop testing procedure for NON-SMART Transmitters

09/17/2009 8:11 AM

What i meant was that if you look at the SMART transmitter loop testing, we connect the HART COMMUNICATOR with it and we do not isolate the transmitter by disconnecting it.

But for Non-Smart we always have to disconnect the transmitter.

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3
In reply to #2

Re: Loop testing procedure for NON-SMART Transmitters

09/17/2009 8:21 AM

Maybe I didn't understand your original question . . .

Are you testing the 1) loop, or 2) Non-smart transmitter, or 3) Smart transmitter?

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply Off Topic (Score 5)
Active Contributor
Egypt - Member - New Member

Join Date: Dec 2006
Posts: 18
#6
In reply to #2

Re: Loop testing procedure for NON-SMART Transmitters

09/19/2009 6:12 AM

hi,

who told you that you don't disconnect the SMART transmitter in case of loop testing using the Hart communicator, don't you change the status of the loop from automatic mode to manual mode!!!, thats is disconnecting the transmitter!

the same steps are used in the two types but in different modules

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#4

Re: Loop Testing Procedure for NON-SMART Transmitters

09/17/2009 8:42 AM

There is no difference to the nature of the loop testing procedure done on Smart or Non-smart or FFB transmitters. The non-smart transmitter can be loop tested using pressure calibration equipment to simulate process conditions and verify/confirm the output at the system end. In this way the integrity of the instrument and the loop wiring are checked.

The current simulation is also acceptable, it is a matter of preference and what is specified in the contract since simulating process conditions using pressure calibrators involves increased man-hours and additional equipment.

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5

Re: Loop Testing Procedure for Non-SMART Transmitters

09/19/2009 12:17 AM

Yeap, These procedure are correct. In the old days, Loop testing procedure for NON-SMART Transmitters" is the following steps,

  1. Disconnect the signal wiring at the transmitter terminal and connect a 4-20 mA signal generator to the signal wire.
  2. Simulate 0, 50, 100% signals and confirm the reading at the receiving end.
  3. Restore the current wiring to normal after the test.

I have been using this step for last 10 years until we replace it with a Smart Transmitter.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#7

Re: Loop Testing Procedure for Non-SMART Transmitters

09/21/2009 1:36 AM

There is no reason why a non-smart transmitter cannot be loop tested using the same method as a smart transmitter i.e. using pressure simulating/calibrating equipment such as hand-pump and test gauges or a druck pressure calibrator.

Another advantage of this is that an ammeter can be placed in series with the transmitter (connected in the field) so that

1. it can be identified if the calibration is off and,

2. calibration adjustments can be made on the spot.

With the smart transmitters this is achieved using the HHT such as HART 375, with the non-smart transmitter the only way of identifying this is using the ammeter to measure the 4-20mA (or to wait until the operator complains).

Again this is a matter of preference and/or what is specified in the contract or by the client/owner/operating company.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Loop Testing Procedure for Non-SMART Transmitters

09/21/2009 10:25 AM

All the suggested procedure is doing is checking that when a 0%, 50% and 100% signal goes in at the transmitter end, that a 0%, 50% and 100% signal comes out at the other. If the loop has too much resistance in it, it might be a bit shy at the higher percentages, in which case it needs to be reconfigured either to reduce the loop resistance or increase the loop supply voltage. Of course, this is the purpose of the test.

Nothing here is HART transmitter-specific. In fact, it shouldn't matter whether a HART or a non-HART transmitter is present; the procedure is valid for all 4-20mA current loops.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#9

Re: Loop Testing Procedure for Non-SMART Transmitters

09/22/2009 8:27 AM

Just Make sure the loop is open ,

For Closed loops u have to consider the Final Element also

Regards

Jose

Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#10

Re: Loop Testing Procedure for Non-SMART Transmitters

09/28/2009 1:36 AM

Hi there,

Whether we are testing a smart transmitter or not - this is the procedure we follow. I will use a simple pressure transmitter as an example. This procedure verifies the trasmitter calibration as well as the wiring.

1. Disconnect impulse leg from process line.

2. Attach pressure pump to transmitter leg

3. Check zero

4. Use pump to induce pressure

5. Check 50%

6. Check 100%

7. Release pressure slowly

8. Check 50%

9. Check zero.

Depending on your transmitter type - you could have your multi-meter in series and measure the current - and/or talk to your operations personnel monitoring the control system.

Purely using a current source at one end does not verify the transmitter calibration or that the transmitter is working correctly.

The pressure pump we use is a Beamex or something similar.

Regards,

Craig

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bill (2); craigza (1); dabdool (2); josej (1); omar (1); PWSlack (1); Simon Wan (1); Usman Nazar Rathore (1)

Previous in Forum: Wokring Principle of Level Transmitter   Next in Forum: double acting actuators
You might be interested in: Smart Cameras, Smart Card Chips

Advertisement