discharge valve &suction valve fully open then flow control valve downstream of discharge is open i get 1100gpm once i open flow control more than 55 percent flow drops to 800gpm
pump is goulds 8196 suction is 16 inches and has no restriction pump does cavitate flow goes from 1200gpm to 800gpm when autmatic valve is opened more than 53 percent have to close automatic to get 1200gpm back thought mabey restriction on discharge but dont know if is possible to act this way all valves and fittings r original size worked before but not now
pump is goulds 8196 suction is 16 inches and has no restriction pump does cavitate flow goes from 1200gpm to 800gpm when autmatic valve is opened more than 53 percent have to close automatic to get 1200gpm back thought mabey restriction on discharge but dont know if is possible to act this way
You say suction is 16 inches. This is a booster pump, not self priming. It must have a positive pressure on the suction head. Has something changed on the supply side to change suction pressure? Is there a point anywhere in the suction side where the plumbing goes higher than the pump that an air pocket could develop? One bad joint or gasket on the suction side will let air in and cavitate the pump. Air could be coming in the shaft seal while running, won't leak water when stopped.