TDS Levels and Cooling Towers

11/24/2009 3:35 AM

Please kindly explain the correct level of 'TDS' for blowing down a cooling tower?

Is there any standard for this level?

Thanks !

Register to Reply
Pathfinder Tags: TDS
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: TDS -COOLING TOWER

11/24/2009 4:00 AM

If possible, get recommendations from the equipment manufacturer. In the absence of specific info, one rule of thumb is to calculate the amount water evaporated in the cooling tower or condenser, and supply twice that amount (evaporating half and bleeding off half).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 17
#2

Re: TDS -COOLING TOWER

11/24/2009 4:05 AM

may be u can consider the TDS standards for Boiler

that may help u in cooling tower blowing down

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: TDS -COOLING TOWER

11/24/2009 7:35 AM

Discuss the issue with the tower treatment chemical supplier. They will err on the low side, as it is in their interests to supply more chemical.

It depends largely upon the composition of the make-up water as to the ideal blow-down setting. The remainder is based upon site-specific experience.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#4

Re: TDS Levels and Cooling Towers

11/24/2009 9:26 PM

Also depends on your local environmental effluent discharge standards. If your standard is < 3,000ppm, then you should blow down before it reaches this figure.

__________________
If only you knew the power of the Dark Side of the Force
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #4

Re: TDS Levels and Cooling Towers

04/04/2020 4:01 AM

Good point.

This in particular makes the set point site-specific.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jun 2009
Location: Between India & Australia
Posts: 71
Good Answers: 3
#5

Re: TDS Levels and Cooling Towers

11/25/2009 6:48 PM

As someone already pointed out, it depends upon the quality of makeup as well as your environmental restrictions if any. Not to mention the chemicals and the cost/availibility of water.

You got to start with analysis of your makeup - ca, mg. ,si, co3, so4, TDS etc. Then you need to figure out how much concentration you can allow of "each" of these consitutents. The concentration is inevitably caused by evaporation. If you serach the net you would find the limit of each of these constituent without chemical addition. This is called cycle of concentartion (COC), depending on your influent analysis the COC can be anywhere from 3 to 8. Then calculate the evaporation which depends on your cooling tower range. This can be done by heat balance, or you can use a conservative thumb rule " 1% of circulation rate evaporation for every 10°F temperature range across the cooling tower.

Once you have the evaporation, COC and the drift (assume .01% of circulation), then blowdown can be calculated (search for the formula it is widely avaialble).

Also if you find that your blowdown is too high, then you may think of adding chemicals. Before you use any propritory chemicals, first consider acid injection (typically 98% H2SO4). This will stabilise the pH as well as convert some of the insoluble co3 to more soluble so4, which means you can allow some more concentration before scaling starts. Having done this you may take professional help to find out what other chemicals you should inject (dispersent etc.) depending on the cost/avaialibility of water.

__________________
Continuous Learning
Register to Reply
Participant

Join Date: Jul 2018
Posts: 1
#7
In reply to #5

Re: TDS Levels and Cooling Towers

07/27/2018 10:12 PM

We have tried the new system with non chemical anti scaling device. we success to solve the fresh water inlet scaling and reduce the existing scaling issue.

we have tried till TDS of 8000 however scaling is not happening. we have save water blowdown quantity and chemical.

Register to Reply
Participant

Join Date: Feb 2020
Posts: 1
#8
In reply to #7

Re: TDS Levels and Cooling Towers

02/05/2020 6:23 AM

Hi John

We are also playing around with chem-free antiscaling approaches. May I ask for more detail on what exactly you are doing to achieve these impressive results?

Thanks

Register to Reply
Associate

Join Date: Oct 2019
Location: BANGALORE. INDIA
Posts: 54
Good Answers: 1
#9
In reply to #7

Re: TDS Levels and Cooling Towers

04/02/2020 1:45 AM

Dear Mr. John

IN this CR4- Link

https://cr4.globalspec.com/thread/46708/TDS-Levels-and-Cooling-Towers

You have posted a reply for a posting on TDS of COOLING TOWER WATER and the question and your reply is as follows:

Pl. post details suchas:

1. How you have maintained 8000 ppm in the cooling tower circulating water.

2. what is the Water circulation Rate in the cooling tower., What was the plant capacity, what was the Temp., limits of In and Out water of cooling tower.

3. What is the quantity and percentage of make up water used, How the blow down water was disposed and treatment details before disposal of blow down water.

4. What was the wet-bulb Temp., Raw water analysis, like TDS and pH and details of Dissolved Solids present in the raw water.

5. What was the COC maintained.

Pl. post the reply in this forum or post by mail by Personal Messaging option.

I have also posted a reply for this thread.

Thanks,

DHAYANANDHAN.S

The Original Quiery

Priyan

Active Contributor

Join Date: Feb 2008

Posts: 23

TDS Levels and Cooling Towers

11/24/2009 2:05 PM

Please kindly explain the correct level of 'TDS' for blowing down a cooling tower?

Is there any standard for this level?

Thanks !

john HMD

Participant

Join Date: Jul 2018

Posts: 1

YOUR REPLY

In reply to #5

Re: TDS Levels and Cooling Towers

07/28/2018 7:42 AM

We have tried the new system with non chemical anti scaling device. we success to solve the fresh water inlet scaling and reduce the existing scaling issue.

we have tried till TDS of 8000 however scaling is not happening. we have save water blowdown quantity and chemical.

__________________
DHAYANANDHAN.S
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: TDS Levels and Cooling Towers

01/10/2013 10:50 AM

Dear Mr.Priyan,

From your posting, it appears that you are taking only TDS is the criterion for the Cooling Tower Water, and its working.

It is NOT the TDS alone to be considered for the Cooling Tower Water, and TDS is one of the Several Factors.

There are several Factors to be considered, mainly for CORROSSION and SCALING EFFECT, in the system. Scaling will reduce the HEAT TRANSFER in the CONDENSER, and with in the cooling tower, the scale will get deposited in the fill bars and increase the load on Supports. CORROSSION will eat away the metal.

The water to be used is to be analysed for RYZNER FACTOR and LANGELIER FACTOR is to be considered and decide the treatment, which will control CORROSSION and SCALING, and elements like Calcium, Magnesium, Chlorides, Sulphates, Turbidity, Silica, etc.

However, to answer your question, the TDS of Make up Water should be 500 to 550 PPM and for Circulating Water Max. should be in the range of 3000 to 3500 PPM. If COC is to be indicated, it should be in the range of 4 to 4.5.

Thanks,

DHAYANANDHAN.S

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); dhayanandhan.s (1); DVader1000 (1); FranklyFrank (1); john HMD (1); monugoyal (1); PWSlack (2); sv13 (1); Tornado (1)

Previous in Forum: How do i connect chilled water supply pipes and return pipes?   Next in Forum: Hopper Design
You might be interested in: Level Sensors, Cooling Tunnels, Electronic Cooling Fans

Advertisement