Trip Protection for 3-Pole Circuit Breaker with GFP

12/13/2009 1:07 PM

How to prevent the nonsense tripping of a 3-pole circuit breaker, with ground fault protection (GFP). The ground fault protection was achieved be a microprocessor trip unit installed in the circuit breaker. (This trip unit have the protection against overload, short circuit instantaneous & and with time delay). Our system is 3-pole, 4-wire.60Hz.220V. If we connect, a 3-pole circuit breaker in this system with a ground fault protection the breaker gives a nonsense tripping, while if we make it a 4-pole circuit breaker with ground fault there will be no more nonsense tripping. Moreover, due to space restriction I am forced to use 3-pole circuit breaker. So I am seeking a way to prevent the nonsense.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/13/2009 7:51 PM

What size breaker? Is the GFP adjustable?

Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#2

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/13/2009 8:33 PM

Sounds to me that you need to make space for what works properly.

__________________
You don't get wise because you got old, you get old because you were wise.
Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#3

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/13/2009 11:06 PM

Are you sure you are wiring the Ground Fault Breaker into the panel correctly? There should be a fourth lead that connects to the ground bar inside the panel. If this is not properly connected, the GF breaker will trip on a false ground fault.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/14/2009 3:12 AM

If the breaker is wired to the three phases and not the neutral, and the load is unbalanced, then of course the thing will trip, as the unbalance current is that flowing in the neutral.

Check the manufacturer's instructions and wire the thing up accordingly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5
In reply to #4

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/14/2009 9:06 AM

GA, PW!

GFP is just like any other differential protection scheme. It will only work properly if you monitor every in and out of the system (4 wires = 4 points must be monitored).

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#6

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/14/2009 1:04 PM

I wondered about the same things both CW, and PW mentioned, but you indicated you do not have the problem using the 4-pole.

Hence the reason for my reply.

__________________
You don't get wise because you got old, you get old because you were wise.
Reply
Anonymous Poster
#9
In reply to #6

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/15/2009 9:07 AM

The only problem i have with 4 pole CB is the space, because we don't have much space left to add too much cubical.

put in the comments above i saw a few comments that might solve my problem, so we i will try to add a monitaring relay with toride to monitor the 3-pole & the neutral all togatherto see what is the result, & will come back to you.

Thanks Transcendian, and thanks for every body commented in this topic.

Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#7

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/14/2009 1:32 PM

I attempted to amend my post, but ran out of time.

Suspect same as others and look towards neutral.

Had a case where in attempting to run an HMI light the arc of the light was sensed by the GFault protector, as a short. Had to find an outlet that was not Ground Fault protected to run that light.

Can't imagine what you might be running on the circuit that replicated that problem.

__________________
You don't get wise because you got old, you get old because you were wise.
Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#8

Re: Trip Protection for 3-Pole Circuit Breaker with GFP

12/14/2009 2:21 PM

If 4 pole does not trip nonsensically,then u need to check yr load balancing under the 3 pole and mostly check yr neutral and how it should be connected.Pls seperate and connect yr neutral properly to make a healthy cct.

Concentrate on yr neutral link.Change yr connection.

Patrick Whowha

__________________
Patrick Whowha
Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cwarner7_11 (1); Patrick Whowha (1); pwr2thepeople (1); PWSlack (1); Transcendian (3); wareagle (1)

Previous in Forum: Generator Sets - Comparing Efficiencies   Next in Forum: Here is a more sensible question
You might be interested in: Circuit Breakers, Circuit Protection Devices

Advertisement