Restriction Orifices Installation

01/23/2007 3:02 PM

I'm looking for standards that apply to install restriction orifices (not orifices plates), specially concerning the diameters downstream/upstream to take in care.

Regards,

Register to Reply
Pathfinder Tags: instrumentation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#1

Re: Restriction Orifices Installation

01/24/2007 8:03 AM

For what purpose?When you do not specify in detail, the orifice in my vien supplying blood to my brain restricts the blood flow from the upsteam to the downsteam and diminishes my power of thinking to answer your question.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#2
In reply to #1

Re: Restriction Orifices Installation

01/24/2007 8:31 AM

Oh dear.... another information packed question...

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Participant

Join Date: Jan 2007
Posts: 3
#3
In reply to #1

Re: Restriction Orifices Installation

01/24/2007 10:11 AM

We are commissioning a main filtered water system for a blast furnace's refrigeration in Argentina. During the tests two restriction orifices had severous cavitation problems.

We re-cheked orifices calculation with instrucalc moving process variables to critical operation but the flow remained estable and no warnig was present in the program.

RO's are installed in 20" lines at 1 diameter from an elbow downstream each one, we suspect that tey're in a wrong position but we haven't standards to support it.

Does anybody knows if restriction orifices has the same installation treatment that orifices plates?

Register to Reply
Guru
United States - Member - Engineering Consultant Popular Science - Evolution - Understanding

Join Date: Nov 2006
Location: Bay Shore, NY
Posts: 715
#4
In reply to #3

Re: Restriction Orifices Installation

01/24/2007 5:53 PM

What is the pressure and temperature of the water downstream of the the orifice?

Higher temperatures and lower pressures will tend to cause problems. Depending on velocity, being too close to an elbow could also cause problems of course.

Does the restriction orifice have sufficiently long tapered sections on both sides of the minimum diameter?

Too sudden an enlargement can produce cavitation.

__________________
"The more I learn, the more ignorant I realize I am."
Register to Reply
Participant

Join Date: Jan 2007
Posts: 3
#5
In reply to #4

Re: Restriction Orifices Installation

01/25/2007 7:10 AM

Here's process conditions:

Inlet pressure: 59.7 PSIG to 102.4 PSIG

Outlet pressure: 17.06 PSIG to 24.17 PSIG

Flow max.: 660430 Gallon/hour

Flow min.: 237754 Gallon/hour

Temperature: 86°F to 104°F

Bore diameter:8.02"

Cavitation starts close maximun pressure and flow that's the normal operation conditions.

Register to Reply
Guru
United States - Member - Engineering Consultant Popular Science - Evolution - Understanding

Join Date: Nov 2006
Location: Bay Shore, NY
Posts: 715
#6
In reply to #5

Re: Restriction Orifices Installation

01/25/2007 11:06 PM

valvactur:

Understanding that sitting here, I cannot give an exact answer but only general guidance/comments on your question based on the information you present, I offer the following:

The ratio of absolute outlet pressures don't conform to the other min/max parameters of absolute inlet pressures and flow. The outlet pressure at max flow seems way too low (or, the pressure at min flow is way too high).

Can you describe the geometry leading to and from the restriction, how and where you are taking your measurements, and what is downstream of the restriction outlet?

__________________
"The more I learn, the more ignorant I realize I am."
Register to Reply
Anonymous Poster
#7

Re: Restriction Orifices Installation

04/13/2007 5:08 PM

there are no requirements. A restriction orifice does not require recovery, it is dealing with the actual pressure loss.

Jack Beadling

auguastaeng.com

Register to Reply