03/03/2010 12:30 AM

For 120 KVA UPS how many nos of batteries i will require for 1 hr backup?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Uninterrupted Power supply

03/03/2010 2:24 AM

One combination (among many) that might work would be about 300 12-volt 60 amp-hour batteries.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Uninterrupted Power supply

03/03/2010 8:20 AM

If this isn't homework, it should be. I'd hate to think that someone who was getting paid to do the calculations would come here with that question.

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 15
#6
In reply to #2

Re: Uninterrupted Power supply

03/04/2010 11:02 PM

dear lynlynch,

it is not mandatory to rply for every question. We are here to share knowledge

plz. dont go off topic.

it is kindly for lynlynch. I thankful to other members who contribute to dis forum.

Register to Reply
Anonymous Poster
#3

Re: Uninterrupted Power supply

03/03/2010 8:30 AM

first of all

1- what kind of loads you are feeding

2- what speed you need to reach so no trouble will happen to your equipment

3- so maily you need to do calculation for the total power needed to feed your loads

4- finally you mainly need what I always use for that quiz

a paper and pencil

and sure with more information about the whole parts around you you will be able to answer.

thnx.

Eng. Nabil

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#4

Re: Uninterrupted Power supply

03/03/2010 8:49 AM

Here's a little something about batteries;

How much battery do you need to run your device? Here is how you estimate it.

Step 0. A little tutorial on measurements of charge. After all, it is electrons that are stored in the battery. In phreshman fisicks we all learned that the measure of charge is the coulomb and that a single electron has 1.602e-19 coulombs of charge. One amp flowing in a wire for one second will use one coulomb of charge.

Q = I*t

where Q is the charge in coulombs, I is the current in amps and t is the time in seconds.

The amount of charge passing through that wire (conducting 1.0 amps) in 60 seconds is 60 coulombs, and in one hour you would have had said "hello" and "goodbye" to 3600 coulombs of charge.

Batteries were evidently developed by engineers who subscribed to the "whatever's easiest" system of measurement. They got tired of pulling out their slide rules to divide by 3600 every time they wanted to know how long 24000 coulombs would last them and came up with the unauthorized unit of amp-hours. Later, when smaller batteries were used they came up with milliamp-hours.

Don't be confused by the hyphen. Amp-hours means amps times hours. Divide by amps and you get hours, divide by hours and you get amps. So it isn't amps, and it isn't amps per hour, it is amp-hours. And, by the way, I have even used the term amp-seconds because when you say "coulombs" everybody goes glassy-eyed on you.

Don't get me wrong, I love amp-hours for units, it is a handy rule of thumb. Amp hours is how much charge is stored in the battery. Since a battery changes voltage during the discharge, it isn't a perfect measure of how much energy is stored, for this you would need watt-hours. Multiplying the average or nominal battery voltage times the battery capacity in amp-hours gives you an estimate of how many watt-hours the battery contains.


E = C*Vavg


Where E is the energy stored in watt-hours, C is the capacity in amp-hours, and Vavg is the average voltage during discharge. Yes, watt-hours is a measure of energy, just like kilowatt-hours. Multiply by 3600 and you get watt-seconds, which is also known as Joules.

As long as we are in the prelude, I might also mention that since the charge in a capacitor is Q=CV that a battery can be rated in farads as well. A 1.5 volt AA alkaline battery that stores 2 amp hours of charge (that's 7200 coulombs) has the equivalent capacitance of 4800 Farads. Of course a battery makes an awfully weird capacitor because the voltage doesn't drop proportionally to the stored charge, it has a high equivalent resistance, and etc.

The following method assumes that you know how many amps you need from the battery. If you know the watts go to Step A below.

Step 1. Back of the envelope

If the current drawn is x amps, the time is T hours then the capacity C in amp-hours is

C = xT

For example, if your pump is drawing 120 mA and you want it to run for 24 hours

C = 0.12 Amps * 24 hours = 2.88 amp hours

Step 2. Cycle life considerations

It isn't good to run a battery all the way down to zero during each charge cycle. For example, if you want to use a lead acid battery for many cycles you shouldn't run it past 80% of its charge, leaving 20% left in the battery. This not only extends the number of cycles you get, but lets the battery degrade by 20% before you start getting less run time than the design calls for

C' = C/0.8

For the example above

C' = 2.88 AH / 0.8 = 3.6 AH

Step 3: Rate of discharge considerations

Some battery chemistries give much fewer amp hours if you discharge them fast. This is a big effect in alkaline, carbon zinc, zinc-air and lead acid batteries. It is a small effect in NiCad, Lithium Ion, Lithium Polymer, and NiMH batteries.

For lead acid batteries the rated capacity (i.e. the number of AH stamped on the side of the battery) is typically given for a 20 hour discharge rate. If you are discharging at a slow rate you will get the rated number of amp-hours out of them. However, at high discharge rates the capacity falls steeply. A rule of thumb is that for a 1 hour discharge rate (i.e. drawing 10 amps from a 10 amp hour battery, or 1C) you will only get half of the rated capacity (or 5 amp-hours from a 10 amp-hour battery). Charts that detail this effect for different discharge rate can be used for greater accuracy. For example the data sheets listed in http://www.powerstream.com/BB.htm

For example, if your portable guitar amplifier is drawing a steady 20 amps and you want it to last 1 hour you would start out with Step 1:

C=20 amps * 1 hour = 20 AH

Then proceed to Step 2

C' = 20 AH / 0.8 = 25 AH

Then take the high rate into account

C''=25 /.5 = 50 AH

Thus you would need a 50 amp hour sealed lead acid battery to run the amplifier for 1 hour at 20 amps average draw.

Step 4. What if you don't have a constant load? The obvious thing to do is the thing to do. Figure out an average power drawn. Consider a repetitive cycle where each cycle is 1 hour. It consists of 20 amps for 1 second followed by 0.1 amps for the rest of the hour. The average current would be calculated as follows.

20*1/3600 + 0.1(3559)/3600 = 0.1044 amps average current.

(3600 is the number of seconds in an hour).

In other words, figure out how many amps is drawn on average and use steps 1 and 2. Step 3 is very difficult to predict in the case where you have small periods of high current. The news is good, a steady draw of 1C will lower the capacity much more than short 1C pulses followed by a rest period. So if the average current drawn is about a 20 hour rate, then you will get closer to the capacity predicted by a 20 hour rate, even though you are drawing it in high current pulses. Actual test data is hard to come by without doing the test yourself.



If you know the watts instead of amps, follow the following procedure

Step A: Convert watts to amps

Actually, watts is the fundamental unit of power and watt-hours is the energy stored. The key is to use the watts you know to calculate the amps at the battery voltage.

For example, say you want to run a 250 watt 110VAC light bulb from an inverter for 5 hours.
Watt-hours = watts * hours = 250 watts * 5 hours = 1250 watt hours

Account for the efficiency of the inverter, say 85%

Watt-hours = watts * hours / efficiency = 1250 / 0.85 = 1470 watt-hours

Since watts = amps * volts divide the watt hours by the voltage of the battery to get amp-hours of battery storage

Amp-hours (at 12 volts) = watt-hours / 12 volts = 1470 / 12 = 122.5 amp-hours.
If you are using a different voltage battery the amp-hours will change by dividing it by the battery voltage you are using.

Now go back to Steps 2-4 above to refine your calculation

Now take two Tylenol and finish your homework.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #4

Re: Uninterrupted Power supply

03/04/2010 10:11 PM

Abhishekkatkar,

You have provided minimum information with which it is not possible to answer your question. However, I am trying to answer with these assumptions: Inverter efficiency = 85%, DC system voltage 120 V (nominal), Design factor = 15%, and Aging factor = 25%.

The DC system power = Inverter input power = 120 KVA/0.85 = 141 KW = 141,000 W

DC system current = 141,000 W/120 V = 1,175 A

Battery Ampere-Hour (AH) = 1,175 A x 1H = 1,175 AH

Considering aging factor and design factor, the required AH = 1,175 x 1.15 x 1.25 = 1,690 AH

If the battery voltage is 12 V (nominal), you need 120/2 = 10 batteries each having at least 1,690 AH capacity. They all have to be connected in series.

If you didn't find 1,690 AH capacity battery, rather find 900 AH battery. Then you need 20 batteries. 2 set of 10 series connected battery and then they are parallel connected.

This is one of the ways you can select batteries. There are other ways you can select it.

You can also see http://cr4.globalspec.com/thread/38821

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: UPS Batteries

10/13/2023 7:38 AM

What did the original equipment manufacturer say over the telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856