Dear All,
I was asked by my colleague regarding the working range of an RTD, I mean, upto what temperature can we use a RTD(PT-100) beyond should it be definetly thermocouple ?. Why cant RTD go upto high temperatures
Does it have anything to do with linearity of the platinum, i mean, does the resistance Vs Temperature scale is no more linear as higher temperatures?
Re: RTD Vs Thermocouple
03/18/2010 11:28 AM
It depends upon the manufacturer's recommended rating and the construction.
In the Endress + Hauser literature (usual disclaimer) for example, some types can span -200 to +600degC.
At high temperatures the components of an RTD assembly may start to melt or even catch fire, whereas a thermocouple doesn't have this problem so early, some being designed to go much higher than 600degC.
Re: RTDs vs. Thermocouples
03/18/2010 3:01 PM
The question is surprising. RTD and Thermocouple are entirely different devices that have absolutely nothing in common. RTD is a temperature sensing device used in temp control instrumentation. Thermocouple is a miniature electric power generator. Upon heating, a thermocouple provides current flow, used wherever required. One example would be a pilot flame gas supply valve. The gas valve is a electro-magnetic valve, whose coil is energized by the current from a thermocouple, heated by the pilot flame.
03/19/2010 10:30 AM
OK. A couple of things:
Not true; they are both used for temperature measurement.
The current from a thermocouple's generated voltage is so small that it would never be able to actuate a solenoid. Maybe you're thinking of a bimetallic thermostat. Even so, the bimetallic strip is only used to close a contact. A separate power source is used to actuate the solenoid.
For basics of thermocouple theory, see here.
03/19/2010 11:07 AM
Sorry Mikerho, The current from a thermocouple's generated voltage is so small that it would never be able to actuate a solenoid. Maybe yo.......
The above is wrong, a thermocouple held in the pilot flame used to hold open the safety valve in most gas appliances, they can and do generate high currents but only at milliVolt levels.
I agree with your first part though... :-)
PS where is the formatting features of the comment box gone????
03/19/2010 12:56 PM
Do you know where I can see a diagram of the gas appliance using the thermocouple?
I can see my formatting stuff - what browser are you using?
03/28/2010 9:50 AM
Guest,
You got a "Bad Answer" mark, but you are right in every line that you've wrote in your posting. That will teach you, the n-th time, that no good deed goes unpunished
They are, both, used for measuring temperature.
The RTD is a "passive" devices, that changes its resistance as the temperature varies. That change is quite linear on a small scale. Though on a larger temperature range it is not very linear.
The thermocouple is an active devices. It generates electricity as it is heated. The electricity generated by a pilot flame is enough to keep the gas valve "on". A Google search over the subject would eliminate any controversy
Bridge rule #1: Nobody is as good as he thinks about himself nor as dumb, as his partner thinks...
05/07/2010 7:57 PM
RTDs Vs. Thermocouples ! They are BOTH used to measure temperature.
I have always wondered how to select one over the other for a given application.
That is, what is the difference to the user? Is there a difference in accurancy? I know Thermocouples are very accurate. Is there a difference in range? I know one type Thermocouple can measure very cold things, and a different type (as designated by letters J, K, and others,,,) can measure hot things, like the tubes in a furnace(!). Is there a big difference in durability? Thermocouples last a long time (yes, I know they can fail,,, but how often do you see that?). Is there a big difference in cost ? I think RTDs cost more.
Sooooo, why do we select RTDs?
Just curious.