Unexplained Hot Spot in Cable

04/09/2010 11:17 PM

Recently we had conducted a thermography test in one of the installations. The cable connecting the transformer and the switchgear showed some hot spots even when there is no load on the transformer. But when the switchgear was switched off the hot spot was not visible. I am not able to understand this as to how the temperature of the cable will go up when there is no load? There is no current flow in the cable (we have measured with Tong tester). Can any one explain this? Thanks in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#1

Re: Unexplained Hot Spot in Cable

04/10/2010 6:17 AM

Do yourselves a favour and replace the cable.

Afterwards take a scalpel and peel of layer by layer of the cable and document what you find.

And report back.

__________________
Never do today what you can put of until tomorrow - Student motto
Reply
Anonymous Poster
#2

Re: Unexplained Hot Spot in Cable

04/10/2010 7:31 AM

The noload current of transformer is always flowing, and in case of something really bad, that can heat up the cable. Do as the #1 said unless you want a potential catastrophe.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Unexplained Hot Spot in Cable

04/10/2010 10:36 AM

For a possible related topic, study up on "arcing ground faults."

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Active Contributor

Join Date: Aug 2009
Location: India
Posts: 12
#4

Re: Unexplained Hot Spot in Cable

04/10/2010 8:09 PM

Check for possible loose cripming of cable lugs or loose joints of busbar.

__________________
Mind is like a parachute, no use if you do not open it
Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#5

Re: Unexplained Hot Spot in Cable

04/10/2010 11:14 PM

Do as #1 said and replace the cable. Replace all phases and neutral if applicable.

Internal "treeing" within the cable insulation will cause a fault. Outdoors in winter they locate the cable fault by looking for the spot without snow cover, due to the short circuit heat.

Corona on the jacket of the cable can also cause a 5-50F temperature rise, and it may only be present during damp night conditions thru 8am.

The corona is due to an insulation defect in the cable causing a locally instense electrical field.

The type of cable may also have outlived it's normal lifespan ?

If I had the pic's on this computer I could post them and show what you are describing.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Reply
Anonymous Poster
#6

Re: Unexplained Hot Spot in Cable

04/11/2010 7:08 AM

Hi, Pl some details are required, What type of cables three core or single core, cable voltage rating, armored or unarmored cable, how they connected, pl check the cable insulation with respect to armored. And what protection relays you are using in the circuit.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7
In reply to #6

Re: Unexplained Hot Spot in Cable

04/11/2010 7:19 AM

The cable is Aluminium armored,3 core 300 sq.mm 33kV connecting the 33kV switch gear and 1600 kVA Dry type Indoor transformer 33/0.415 kV

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#8

Re: Unexplained Hot Spot in Cable

04/11/2010 7:50 AM

There are other explanations, however, my guess is that your tong measuring device is missing the current that is causing the temperature rise. I think you need to use the tong over each phase individually instead of over the whole cable.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#9
In reply to #8

Re: Unexplained Hot Spot in Cable

04/11/2010 8:16 AM

Please note that we know how to use the tong tester, and tong tester was inserted on individual phases.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#10

Re: Unexplained Hot Spot in Cable

04/11/2010 9:37 AM

Please search your topic at IEEE Xplore where there are probably several papers describing your problem.

You may wish to report back.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#11

Re: Unexplained Hot Spot in Cable

04/11/2010 11:35 AM

To have hot spots there has to be current flowing from somewhere as you have noted it disappears when the gear is out, also a cable in good condition should not have localised hot spots it should be uniform.

__________________
Dont get on to the roundabout if you dont know how to get off
Reply
Anonymous Poster
#12

Re: Unexplained Hot Spot in Cable

04/12/2010 1:42 PM

There has to be current flow to create the hot spot(s). There is definetely a problem with the cable, the hot spots are most likely areas of increased resistance. Replace the cable.

Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#13

Re: Unexplained Hot Spot in Cable

04/12/2010 3:08 PM

If you are measuring temperature gradients in a cable when no current is flowing, then maybe there is another heat source, sunlight, etc. or you may have emissivity gradients in the cable jacket that appear to be hot spots.

Reply