Clogged Pipe Sensor

08/08/2010 2:15 AM

I want to install clogged pipe sensors on gravity flow sewer/waste pipe(dia 3"-8") to be laid at 1% slope.What type of sensors to be used-Probe, optical, ultrasonic or else. I feel like getting alarm at 40%, 50% and 60% pipe full and also when velocity of flow is at or bellow 2 ft./sec. Please let me know if anybody has the solution. Also also relevant web links for methodology and sensor manufacturer.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Clogged Pipe Sensor

08/08/2010 8:37 AM

At 1% slope, they aren't needed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Member

Join Date: Aug 2010
Posts: 7
#2
In reply to #1

Re: Clogged Pipe Sensor

08/08/2010 3:18 PM

Hi Guru, Thanks for response.So far space constraints in ceiling is concerned,I feel it may not be possible to attain 1% slope in some section of pipe. I would appreciate to know if such system is in use anywhere and manufacturer producing such sensors.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #2

Re: Clogged Pipe Sensor

08/09/2010 3:25 AM

Not in the UK. Wastewater drainage requires a minimum slope and this value is contained within the Building Regulations. Drainage systems are inspected by the local Authority's Building Inspectors, before back-filling, as part of the planning process that encompasses building construction. Failure to obtain approval before back-filling will require re-exposure of the drainage system for inspection before a Completion Certificate is raised. Without the Certificate, insurers can refuse to provide indemnity and fire cover, and the building owner will be unable to sell, as well as exposing him/herself and/or the builder to prosecution for failing to follow the Regulations.

So such a sensor is still unneccessary.

Anyway. The hypothetical sensor says the hypothetical pipe is 60% clogged. What happens next?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#3
In reply to #1

Re: Clogged Pipe Sensor

08/08/2010 8:42 PM

(GA) Sir Slack, that explains why your are paid the big bucks.... Lol

__________________
klearzen
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#4

Re: Clogged Pipe Sensor

08/09/2010 12:24 AM

You might eliminate the need for such instrumentation by putting a more realistic pitch on the pipes. 1% slope is only 1/8" per foot. In the USA most plumbing codes require a minimum of 1/4" per foot (approx. 2% slope). More pitch would increase the velocity which would make the system more self-cleaning and therefore less likely to get clogged.

Without more information concerning proposed flows, you may never get up to a velocity of 2ft/sec with a 1% pitch.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Clogged Pipe Sensor

08/09/2010 8:42 AM

Don't forget to unclog them first!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#7

Re: Clogged Pipe Sensor

08/09/2010 12:33 PM

"Clogged pipe sensors" ????

In the middle of a gravity system???

I don't understand what a monitor in the middle of the piping system is going to tell you ? When the pipe clogs, it will clog rapidly....you will have no time to react

What about a "float" sensor/alarm in the floor (or what ever) that is being drained ?

How about a flow switch at the terminus......it will tell you when there is no more flow ?

__________________
We have met the enemy....and he is us. POGO
Register to Reply
Member

Join Date: Aug 2010
Posts: 7
#8

Re: Clogged Pipe Sensor

08/11/2010 9:44 PM

Thanks to all the participants. What I can conclude from the comments received is that its better to take care at design stage by maintaining proper gradient, pipe dia and self cleaning velocity so that clogging does not occur and requirement of clogging alarm does not arise . Please correct me if am wrong With thanks to all of you again.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abcplmb13feb (2); Andy Germany (1); klearzen (1); MJCronin (1); old salt (1); PWSlack (2)