3 Pole Circuit Breaker On Single Phase System

08/31/2010 6:04 PM

I have an existing 480V Y connected panel board and it has a spare 3p circuit breaker that I would love to reuse for a 480V 2p application. Can I land the conductors on A and C or A and B? or is this not legal?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 3 Pole Circuit Breaker On Single Phase System

08/31/2010 6:56 PM
  • Wire one phase to inlet A, the other phase to inlet C.
  • Wire outlet A to inlet B.
  • Wire the load between outlet B and outlet C.

"Simples!ξ"

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#12
In reply to #1

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 8:15 AM

On a typical bolt in or stab-lok style of distribution panel, where all 3 poles of the breaker must contact a phase bus, won't this be a tad bit difficult?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Associate

Join Date: Jun 2010
Posts: 34
#20
In reply to #1

Re: 3 Pole Circuit Breaker On Single Phase System

09/03/2010 3:15 AM

I second PWSlack. Most workable solution and I have applied it without any problem for quite sometime.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 3 Pole Circuit Breaker On Single Phase System

08/31/2010 7:13 PM

(The purpose of the foregoing is to make sure that all three poles of the CB "see" the load current, as necessary for proper sensing. The same princlple applies to 3-pole motor overload relays used on 1-phase motors.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: Aug 2008
Posts: 25
Good Answers: 1
#3
In reply to #2

Re: 3 Pole Circuit Breaker On Single Phase System

08/31/2010 7:44 PM

I saw an installation like this and wondered what was going on.

Shouldn't any pole that exceeds its rating pull all three out (hence the bar that mechanically interlocks all 3 breakers)?

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #3

Re: 3 Pole Circuit Breaker On Single Phase System

08/31/2010 8:34 PM

IEC circuit breakers and overload relays have a feature called a differential trip bar. This is used to help the device trip quicker if there is a loss of phase. All that is necessary is that current is flowing on all 3 legs.

In typical North American design circuit breakers this is usually not necessary, that feature is not part of the trip mechanism. But being that many NA companies are now owned by companies that also make IEC products, that is changing. If you are unsure which type it is, there is no harm in doing the loop-through technique on a NA designed breaker.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Associate

Join Date: Aug 2008
Posts: 25
Good Answers: 1
#6
In reply to #5

Re: 3 Pole Circuit Breaker On Single Phase System

08/31/2010 9:05 PM

Thanks. Seems I've some googling to do.

Reply
Anonymous Poster
#4

Re: 3 Pole Circuit Breaker On Single Phase System

08/31/2010 8:31 PM

methinks Mr. Slack shouldn't be wiring in the US

Reply
Anonymous Poster
#7
In reply to #4

Re: 3 Pole Circuit Breaker On Single Phase System

09/01/2010 2:38 AM

Why?

Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#8
In reply to #4

Re: 3 Pole Circuit Breaker On Single Phase System

09/01/2010 2:40 AM

And why not? With thinking nobody here gets wiser. Please tell us why?

If as the OT posts there are 6 terminals on that breaker, to connect with 6 wires.

He will only have 4.

His proposal goes wrong only when it is a plug- in system, and still then 1 phase is missing to create a short cut.

I did it also with using just 2/3 of the breaker with a cut of the connection handle, that unlocks the non- used one.

__________________
Plenty of room here
Reply
Anonymous Poster
#9
In reply to #4

Re: 3 Pole Circuit Breaker On Single Phase System

09/01/2010 2:49 AM

Why do you assume PWSlack is male?

Reply Off Topic (Score 10)
Anonymous Poster
#10
In reply to #9

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 2:53 AM

simple. based on pwslacks sexists and condescending manner towards women it is most probable that pwslack is an older male (>50years) or else a really really angry recently dumped lesbian who is getting her own back on other women.

Reply Off Topic (Score 10)
Anonymous Poster
#16
In reply to #10

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 1:41 PM

My money is on Lesbian.

Reply Off Topic (Score 10)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 1:43 PM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 10)
Active Contributor

Join Date: Jul 2010
Location: NJ
Posts: 19
#11

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 6:12 AM

PWSLACK's method of wiring the 3 pole breaker for two pole usage has been used in the US for years. This is also how larger DC motor systems are wired.

__________________
Quick, hurry up and wait!
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14
In reply to #11

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 11:25 AM

Just to be clear, the reason DC is wired that way is because it is much more difficult to interrupt the arc with DC, so using multiple poles in series increases the cumulative air gap so that a reasonable DC voltage can be used. It has nothing to do with the current sensing, again with regards to NEMA designed MCCBs.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Active Contributor

Join Date: Jul 2010
Location: NJ
Posts: 19
#15
In reply to #14

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 12:54 PM

Thanks, I did not know that.

__________________
Quick, hurry up and wait!
Reply
Participant

Join Date: Oct 2009
Posts: 2
#13

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 10:37 AM

20100831132300.pdf‎ (39 KB‎)

Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#18

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 4:34 PM

A circuit breaker is just an overcurrent and short circuit circuit protection. you dont have to use all 3 Phases and the loads dont have to be balanced. You could just use 2 phases on a 3 phase circuit breaker, with no problems.

Think about it, you could have a 3 phase circuit breaker feeding a sub main board, the load connected to the sub main board may not be balanced, but it wont trip the 3 phase CB unless the is an overload contition.

Cheers

Joe

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19
In reply to #18

Re: 3 Pole Circuit Breaker On Single Phase System

09/02/2010 8:09 PM

Joe, read my post. For those of us here in the US, you are right, it makes no difference. But for people outside of the US (and this is a very international forum) it does make a difference. THEIR style of breakers may nuisance trip if you only use 2 out of 3 poles.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#21
In reply to #19

Re: 3 Pole Circuit Breaker On Single Phase System

09/03/2010 6:17 AM

JRaef Sorry mate I was only giving my input, but now that we are on the subject.

I would like to ask you a question: I have a main distribution board the is suppling various sub boards within a factory. The Sub boards have single phase loads these may not be ballanced are you saying that I would have to ensure that loads are always ballanced, that is a croc!

You could for instance have oh, lets say an injection molder that has single phase heating loads connected, these are temperature controled they will switch of an on depending on the actual temperature, loading on each phase will change dependent on what is heating, current will change on each phase dependant on what is on not heating, are you going to say that because we have an inballanced load that this machine is going to switch off?

Circuit breakers are circuit breakers they are designed to trip at a point of over-current over a given time, they do not discriminate on ballanced load. They only look at overloaded conditions and short circuit conditions or anything in between.

I do realise that this is an international forum, I have traveled the world but I have not been to all destinations, but I have been to many destinations that you would never put on your holiday list, even though they may not have the same standards as we would have circuit breakers are the same; Please advise me where circuit breakers are not circuit breakers as we understand.

Best Regards

Joe

Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#22
In reply to #19

Re: 3 Pole Circuit Breaker On Single Phase System

09/03/2010 6:25 AM

By the Way JRaef

I dont live in the US, I live in New Zealand, that is if flying from LA you will pass over it just before you hit Australia

Cheers

Joe

Reply
Participant

Join Date: Aug 2010
Posts: 1
#23

Re: 3 Pole Circuit Breaker On Single Phase System

09/04/2010 6:42 AM

You should put all the 3-poles in series for better functioning of the tripping mechanism of the 3-pole breaker when using it for single phase application.

Reply Score 1 for Good Answer
Guru

Join Date: Feb 2008
Posts: 638
Good Answers: 45
#24

Re: 3 Pole Circuit Breaker On Single Phase System

10/04/2010 3:22 PM

Replace the 3-pole breaker with a 2-pole breaker.

__________________
This moment is as it should be.
Reply
Reply to Forum Thread 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

007 (2); Anonymous Poster (5); dvmdsc (1); gfmlcka (2); Humayun A Chaudhry (1); JGE (1); Joe Sparky (3); JRaef (3); neelutamrakar (1); Phys (1); PWSlack (2); szwasta (1); Tornado (1)

Previous in Forum: Transformer Modeling   Next in Forum: Cost Information of Electro-Mechanical Eqpt.

Advertisement