I would like to make a submerged heat exchanger using SS piping sunk into a small river. This is to replace the cooling towers that would normally be used in this application. I have about 100KW of power (heat) to dissipate with 5C of difference between the water flowing into the "exchanger" and the river's water.
The river's water speed is about 0.5m/S and the flow of water to be cooled is 60 m3/h.
Is it feasible ? How long should the pipe or parallel pipes (can split the line) be?
Do you have a link to a site with examples?
Thank you.
Re: Submerged Hear Exchanger
09/09/2010 1:25 PM
did you do an environmental study on this, on the effects it will have on the river?
Good Answers: 183
09/09/2010 1:49 PM
What is the river flow in m^3/h ?
You need -roughly (not exactly computed only estimated with a global coefficient of 1 kW/m²K) - 10 to 20 m² of area for the exchange.
It is important to estimate which will be the river temperature rise since the flora and fauna are sensitive to even not significant changes.
09/09/2010 2:18 PM
Hmmm, someone in the Pedantry depatment has brought the above to my notice.
I've passed it on the English Rose for further scrutiny as we feel it may be a contradiction in terms.
A bill for this investigation will be forwarded shortly.
United Kingdom - Member - Hearts of Oak Popular Science - Paleontology - New Member Engineering Fields - Mechanical Engineering - New Member
Good Answers: 75
09/09/2010 2:43 PM
Thank you Del, you are proving to be a quite competent investigator-cum-administration assistant. Keep this up and you'll so be eligible for the intensive training course prior to promotion to Pedant Third Class.
The correct order for the words in that clause you highlighted is:
flora and fauna are sensitive to not even significant changes.
This is an example of Morecambism, where all the correct words appear, but not necessarily in the right order. It is quite different from Malapropism.
A better way to phrase the idea, which is, of course, technically correct, would be:
flora and fauna are sensitive to changes in water temperature that you may not consider significant.
I will ensure that this excellent catch is recorded in your personnel file.
Chaos always wins because it's better organised.
09/09/2010 2:53 PM
I knew Del had a file.
09/09/2010 4:07 PM
Is "file" anything like "rap sheet"?
Good Answers: 150
09/10/2010 12:41 PM
How do you think he gets out of his cat carrier? =b
Who is John Galt?
09/19/2010 8:36 AM
You mean this carrier
Good Answers: 150
In reply to #74
09/19/2010 9:54 AM
I'm trying to figure out which direction the cat is to be facing, or if it really matters....
Does it come with chain mail gloves and kevlar sleeves?
Who is John Galt?
In reply to #75
09/19/2010 11:24 AM
It is prabably better with the head in the left hand end...........or for an expert opinion perhaps we should ask Del!!!!!!!!!
I am not sure how they carry him around, he would proabably know what is more comfortable.........haha!
Good Answers: 150
In reply to #76
09/19/2010 5:55 PM
I do believe I have found a clearer version of the ad.
Who is John Galt?
In reply to #77
09/20/2010 2:32 AM
Grrrr Ftttttzzz hiiissssss......
oooh
In reply to #77
09/20/2010 4:45 AM
Thanks for that...............did you hear anything?????
Good Answers: 130
In reply to #79
09/20/2010 8:28 PM
It is adjustable Mobi
In reply to #80
09/21/2010 10:15 AM
Let's tighten the screw a little.........and see what happens!!!!!!!
Good Answers: 130
#82
In reply to #81
09/21/2010 10:58 AM
Good of you to volunteer.
Might even solve this one?
Reports of "black panthers" in Australia
At the end of World War II, United States soldiers re-stationed in Australia reportedly brought black panthers as mascots. Within weeks of arriving in Australia, an unreported number of panthers supposedly escaped.[citation needed] Today, black panther sightings are frequently recorded in rural Victoria and New South Wales[9] and Western Australia. The Australian "phantom panthers" are said to be responsible for the disappearances and deaths of numerous cats, dogs and livestock.
Animal X Natural Mysteries Unit led an investigation into the phantom panther. They discovered that scat and hair found by locals and sent to a lab came back as scat from dogs that had feasted on swamp wallaby, and hair from a domestic cat. In an experiment, the Animal X team sent in leopard scat and hair collected from a private zoo. These samples came back with the same results.
#83
In reply to #74
09/21/2010 11:13 AM
Mine's electric. Even comes with it's own generator and lifetime guarantee. ~Grog
Save 9 lives. Be a cat donor.
Good Answers: 150
#84
In reply to #83
09/21/2010 11:30 AM
Uses the squirming of the animal to generate power eh?
Who is John Galt?
#85
In reply to #84
09/21/2010 12:02 PM
Well, no, actually. The power is externally applied, much to the cat's apparent displeasure (for my part, I don't see the problem. Maybe she's just being pissy. You know how cats are). What really turns her crank, so to speak, is the novel application for which I've found this assembly: mixing margaritas in a large galvanized bucket. Cats don't like being wet, of course, but all is not lost. She has since found ample compensation in cleaning her coat afterward... ;-)) ~Grog
Good Answers: 150
#86
In reply to #85
09/21/2010 12:17 PM
You do know they are both logged in as you in the other room watching what you post right?
Who is John Galt?
#87
In reply to #86
09/21/2010 12:29 PM
Yes, but they're in Kevlar restraints watching 'Adult Swim.' The Major Boobage episode of South Park, I believe.
09/10/2010 4:14 AM
Can you let me know when class gets to split infinitives ? Hyphons might be useful too. Gotta go, Star Trek is starting......
09/15/2010 9:24 AM
Quick, throw Del down the stairs his thesaurus! ~Grog
Good Answers: 183
09/10/2010 12:37 PM
As you know, I mentioned it several times I am aware that "my English" is by far not perfect since it is not - as for you - the language learned from parents and used for whole school and life from start to present times. English is for me a language among others (German, French, Russian,...) acquired by late learning (after childhood) with, as you can imagine, a lot of time and efforts.
If after a couple of years at CR4 with a majority of participants born and living in English speaking environments it is the only syntactic error one has to complain about I can be proud of the language I practice!
Thanks to you Del and to you English Rose.
09/10/2010 1:30 PM
It wasn't us, it was Kris.....
You know we are only teasing anyhow.
I'm ashamed to admit I don't really speak any other languages, except the tiniest bit of schoolboy French, but how often do you want your Aunt's pen?
Oh and I can ask where the railway station is in German.
09/10/2010 2:54 PM
Doing great Kris! With this bunch, I think you only have to be concerned if someone is not trying to jerk your chain.
09/11/2010 4:45 AM
Thank you, russ. Ever since the importance of getting 'a' and 'e' correct was explained to me, I've never been afraid of belling the cat.
09/13/2010 9:07 AM
When "belling" a cat, does it look like this?????
09/14/2010 3:41 AM
ROFL !
09/14/2010 11:05 AM
I am sure they used to cook cats in the coffee stalls in Hong Kong many years ago........in the sixties...........we used to drink there after the bars shut at 0200.........like I needed another beer.......but, I was never game to eat there. Guess what these dishes are
A Wanchai butcher......wiond dried meat!!!!
Good Answers: 150
09/14/2010 11:13 AM
It's the OTHER white meat.....
Who is John Galt?
09/15/2010 9:36 AM
"When "belling" a cat, does it look like this?????" Yes, it does - if you're the bell. What the pic doesn't show are the heated tongs and Kevlar restraints - nor the cocaine suppository about to be applied by a rather insensitive hydraulic device out of view of the camera and the SPCA. Within ten minutes they had renamed the cat "Carillon" as considerably more than one bell was involved. ~Grog
09/15/2010 9:59 AM
'Boarding the Lion' was truly horrific to see so Del tells me
09/15/2010 11:13 AM
Rumor has it that Mrs. Cat has her own account here, not that she posts much...
~Grog
(PS: 'Allo, mate. 'Tis I)
In reply to #60
09/15/2010 11:23 AM
No worries, I've sent Del some purple pills
Good Answers: 150
09/15/2010 11:46 AM
Did you say Purple? or Blue? Or perhaps you meant Red?
Who is John Galt?
09/15/2010 1:36 PM
If you value you're chastity, don't mess with hardened criminals dear Rorschach. Blot on the copy book might be the least of your worries.
Good Answers: 150
In reply to #63
09/15/2010 2:07 PM
"Hardened Criminals" indeed! =b
Who is John Galt?
In reply to #63
09/15/2010 2:36 PM
I suspect none of us here value our chastity, such as it is. We all have CR4 accounts, need I say more?
I myself am come to collect my fair share of abuse. Turns out those Baptists I was hanging with are just bantam-weights.
~Grog
09/15/2010 2:46 PM
They won't interest him unless they smell like fish. He's a cat. Cats aren't stupid. I suppose in a pinch you could attach little bells to them. (Here we go, back to belling the cat).
And speaking of pills, my cats got into my Viagra bottle (one of them, anyway), and now they're all strutting around, tails in the air. Good thing they got to them first; my attorney is already too tall.
~Grog.
09/16/2010 6:48 AM
Perhaps one could just use a rubber band??????
.........or is that too humane?
In reply to #67
09/16/2010 11:46 AM
My two cats, Velcro and Shelf-Life, think it's a great idea. Both also suggested that next time I post, for me not to have my tongue planted quite so firmly in cheek. "It conveys the impression," they mewed, "that you're a much worse Barbarian than you really are in the flesh. We haven't been fed this morning by the way, so get off that damn forum and do something about it!" Cheeky bastards. ~Grog
In reply to #68
09/16/2010 11:51 AM
Velcro and Shelf life?...damn, I know I'll reget asking.
In reply to #69
09/16/2010 12:42 PM
I had nothing to do with it!
In reply to #70
09/16/2010 1:16 PM
Yeah that's what they all say.
With that sort of attitude we could probably find you a position at KrisDelTM virtual components on the help desk.
"Good morning KrisDel products. Grognak speaking, howmayIhelpyou?Ihadnothingtodowithit"
In reply to #71
09/16/2010 1:47 PM
Del, you don't understand (and I must write this very quietly, so please turn off that air conditioner) what their razor-sharp claws were threatening, exactly, when I posted that last. V & SL are very private individuals, you understand. I'm not really at liberty to say much when they're around, bless their black hearts. ~Grog
09/11/2010 11:02 AM
I can order a beer in German..........that way one does not die of thirst........not much good if you are in China though.........numero uno, if in a country where German is spoken.
09/11/2010 11:41 AM
I remember my first trip to a job in Argentina - in a bar at the LA airport the bartender was busy making sure I could order a beer when I arrived in Buenos Aires - many thanks to him.
Good Answers: 75
09/13/2010 8:02 AM
Hi Nick name,
I didn't realise that English is not your first language, so that says loads about your ability.
As Del said, it was gentle teasing - mostly just us playing in our sandpit. No offense meant, it was a slow day....
Good Answers: 183
09/13/2010 8:59 AM
Thank you, as I wrote, your comments were for me a compliment I took it the right way.
09/15/2010 10:02 AM
"Slow day" my eye. Admit it, Rosebud, you don't recognize flags featuring fewer than three colors. C'mon, fess up. None of this 'slow day' business, pray. We know they don't let you see daylight very often at your job and that your thermostat at home doesn't work. Is it still full of dust bunnies? ~Grog the Reincarnate
Good Answers: 80
09/09/2010 4:36 PM
Thank you.
I had found ~800W/m2C some where on the internet but it was not a very scientific site... You are confirming that this number is in the ball park.
Good Answers: 80
Re: Submerged Heat Exchanger
09/09/2010 4:30 PM
Guys, don't worry about the river. Nothing lives in it and the average temperature will not budge.
As for the flow, it is thousands of m3/h.
Thank you.
09/09/2010 10:56 PM
Your concern for the river is reassuring. Generally a consent is required for such an application for the effects of heat addition to the river as well as the effects that rupture of the water pipes may have, with their corrosion inhibitor etc.
I assume you work in a largish plant given the energy you are trying to dispense with, so presumably you will be doing a FMEA on this project.
09/10/2010 5:55 AM
"... Nothing lives in it"
I find this assertion worrying on several levels.
a) I doubt very much if it's true, as there are micro organisms and insects which live just about anywhere.
b) If it is true then you should be very worried about your local environment.
Maybe by 'nothing' you mean anything big, obvious and cute. In which case I can assure you with some authority that cats don't live in rivers anyway.
09/10/2010 6:08 AM
What about catfish - last I heard they preferred rivers.
Good Answers: 75
09/13/2010 7:46 AM
Thanks to pollution and raised water temperatures, they're evolving at an accelerated rate. They're walking on 4 feet and their scales have morphed into a fur-like sunstance.
Be afraid. Be very afraid.
09/13/2010 9:14 AM
Is a "cat fish" going to look like..............like this one will shortly look like!!!!!
09/09/2010 7:01 PM
Note that the LMTD (logarithmic mean temperature difference) will be less than the entering TD of 5K. (Rough guess 3.5K.)
Good Answers: 80
09/09/2010 8:42 PM
Tornado,
I am just an electrical guy...
Please, can you explain this in more details.
Thank you
09/09/2010 10:18 PM
The "force" driving the heat exchange is the temperature difference between the two fluids. As the warm fluid enters the exchanger, the difference is 5K (or 5°C). As the warmer fluid cools, this difference decreases. Let's say that on leaving the exchanger the TD has decreased to 2.5K.
The effective average TD is not the arithmetical average (3.75K); rather it is the logarithmic average. One way to express this is (TD1 - TD2)/ln(TD1/TD2). This example works out to ~3.61K, which is your "driving force."
Q = K A (LMTD), where Q = heat transferred, K = conductivity coefficient, and A = heat exchanger area. K depends on the heat exchanger material, its thickness, and turbulence and boundary layer conditions of the fluids. (If you are familiar with R values of insulation, K is basically the reciprocal of R.) (K is the standard symbol; sorry about the ambiguity with K for Kelvins.)
Good Answers: 80
09/09/2010 10:34 PM
Thank you.
Marco
Good Answers: 150
09/10/2010 8:05 AM
Don't use SS, use Monel if budget allows, you'll have much less biofouling growing on your heat exchanger (think biological insulation) and without all the algae and bacteria growing on it, you won't have corrosion pits forming underneath the crud.
Who is John Galt?
09/10/2010 10:07 AM
You stole my thunder there..........it is truly amazing how many people opt for ss in so many applications.............it can and has been fraught with danger.
Although dearer your super alloys are far superior in many applications, especially in seawater and polluted river water..........I have seen so many problems associated with the use of ss in marine applications........propeller shafts are a good example.
If flow rates are kept below 3m/s another option maybe either 90/10 or 70/30 cupro/ nickel, the advantage of this is its thermal conductivity.........you could design a smaller heat exchanger than one made from ss
Good Answers: 150
09/10/2010 10:11 AM
Even better (and cheaper!) would be simple copper tubing. MUCH better conductivity and the copper will prevent biological growth. It isn't as erosion resisitant as Monel/Cupro-nickel (same alloy family) but it has higher conductivity and is easier to bend and terminate.
Who is John Galt?
09/11/2010 10:03 AM
As you said Rorschach the only problem with copper is its low resistance to erosion, and the rest of the benefits............howeve, myself I would opt for the 90/10 or 70/30 cupro/nickel because of the erosion problem with pure copper.
Good Answers: 80
09/10/2010 3:06 PM
Thank you! #17, 20, 21
09/10/2010 8:21 AM
Sounds like an enviro problem to me. You're in Canada, just across the border and your enviro laws aren't that much laxer than the US. We can't even put a decorative paddle wheel in a 2 foot wide wet weather run without an environmental study and a permit.
09/10/2010 9:58 AM
No matter how little the effect may be, an evironmental impact study is always done........and if a rare or endangered species are found in the area........forget it.
You have to take this serious or your gonna get spanked.
09/10/2010 10:59 AM
In Canada, the Department of Fisheries and Oceans is "responsible for regulating the impacts of development projects in and around marine and freshwater ecosystems across Canada". If your project falls under regular types of operations in lakes and rivers (dredging, docks, underwater cables, etc.) the you can follow the guidelines of an "operational statement" that DFO has already created. http://www.dfo-mpo.gc.ca/habitat/what-quoi/1-eng.htm
If you don't fall under these OS's, then you need to submit your project for review. You may well be correct that you HE will have no effect, in which case, no problem. But you might need to prove that it has no significant effect. I would suggest you talk to a qualified environmental professional (don't know who that would be - any suggestions?)
Good Answers: 80
09/10/2010 3:29 PM
Thank you
09/13/2010 9:40 AM
I don't see a problem................vessels,from small recreational craft to larger ferries etc that run in inland waterways...........these have either aluminium alloys, mild steel, ss, 90/10 cupro/nickel, or super alloys as keel coolers or heat exchangers, plus propellers and shafting (most props made from one of the bronzes).......all in contact with the water these vessels are floating in........ and.............. then you have plastic boats, wooden hulls, concrete hulls, etc...........and the heat exchanger will no doubt be manufactured from one of these many materials.
09/13/2010 9:53 AM
When I was working in the steel making plants almost all heat exchangers were 'admiralty brass'. Other alloys were not economical long term.
09/13/2010 10:12 AM
I have used admiralty brass on many occasions to make marine fittings including valve spindles..................never used it on heat exchangers, except maybe drain coolers...........which is still a heat exchanger.
Most keel coolers and heat exchangers I have worked on have been 90/10 cupro/nickel.
09/13/2010 11:31 AM
Fresh water is not that bad to work with.
09/13/2010 11:47 AM
I concur, but, polluted fresh water can be worse than sea water.
How many lakes and rivers are in pristine condition..........if they flow through towns and/or cities.
09/13/2010 11:58 AM
Here are some of the sacrifial anodes on a river ferry in the US
Good Answers: 80
09/13/2010 2:44 PM
Thank you Mobi. You have given many good info. GA.
09/14/2010 4:03 AM
That's a mean trick velcroing the welder's lunch packs to the hull
Good Answers: 150
09/14/2010 7:38 AM
Velcro? oh, no! he'll need a wrench...
Who is John Galt?
09/14/2010 9:06 AM
Was that a wrench or wench!!!!
Good Answers: 75
09/14/2010 9:23 AM
Here sir! At your service.
09/14/2010 9:46 AM
Shame! Shame! Shame! If nuts were meant to have round corners, manufacturers would have made them with round corners.........Please! Always use the correct size spanners.
Using these monstrosities can be extremely dangerous!!!!!
See I told you so!!!!!
Good Answers: 75
09/14/2010 11:18 AM
Tee Hee Hee!
It was the first thing to come up on Google Images. It's actually an adjustable spanner not a wrench...I was just humouring our colonial cousins.
I'm sure I have a pipe wrench in my handbag...hrumph...why's that wire stripper still in there...
09/16/2010 1:41 PM
"Humouring?" What! Vestigial Froggie yet lurks in the Queen's English even still? You could've called me first, you know, instead of parading it out in open before all these bloody Colonists. Please tell me you're not just pulling my gammy leg with those nuisance wire cutters of yours! You're not? Right. Well, then, give me the number of a good Linguistic Exorcist in your area. Last one I used expired in the throes of expunging a superfluous 'e' from the word 'haemorrhoids.' (I had to nix it and that accursed second 'h' myself, dammit.) ~Grog
09/14/2010 10:23 AM
Listen Felix, behave yourself!
09/13/2010 11:54 AM
I don't know the environmental impact, thats up to you, but it would be easy to do contact a Marine engine/genset supplier and ask about keel coolers