Question About a Fan That Causes Shocks

03/20/2007 7:01 AM

In my house, the table fan produces a shock when the plug point is connected in one way. If the plug point is connected in the other way, no shock. Could you please explain the reason? Thanks for all.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#1

Re: about shocking

03/20/2007 7:10 AM

I think you should find an electrician , and fast ! It sounds as though your fan is not earthed (which it should be unless it is double insulated). Occasionally buildings are wrongly wired with neutral-switching. This will not prevent a device working , but can lead to some shocking results .

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply
Guru
Brazil - Member - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - RC Aircraft - New Member Hobbies - Target Shooting - New Member Hobbies - Automotive Performance - Hey there... interested in exchanging information about car performance? Hobbies - DIY Welding - New Member

Join Date: Jan 2007
Location: Porto Alegre - RS - Brazil 30deg01'39.73"S 51deg13'43.45"W
Posts: 831
Good Answers: 28
#2

Re: about shocking

03/20/2007 7:50 AM

As the colleague said, your fan is not earthed, and your wall plug comes out with 1 phase and 1 neutral wire. What happens one way is that the phase is routed to your fan housing, and the housing discharges through you to the building when touched. The other way, the neutral is being connected to the housing, and the current returns to the wall instead of you.

If you have some looseness in the wall connector, you'll get shocked either way.

Action item: fix your fan.

__________________
Humm... suspicious you are...
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: El Lago, Texas, USA
Posts: 2639
Good Answers: 65
#3

Re: Question About a Fan That Causes Shocks

03/20/2007 10:16 AM

All of these young bucks won't remember, but back in the day it wasn't uncommon to get shocked by metal appliances. What's happening is that one side of the plug is connected to the metal frame on the assumption that it will be connected to the electrical neutral. When it is, no shock. When you flip the plug, the hot wire is connected to the frame, so you get a shock. This is a poor design, but not that uncommon in older equipment.

You might open the fan and see if the connection to the frame is inadvertent - a loose wire or degraded insulator - and fix it. Another approach would be to replace the two prong plug with a three prong plug that can only be inserted one way - if you have three prong sockets in your house.

Calling in an electrician is a good idea, just in case. Bad electrical wiring could burn your house down.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Question About a Fan That Causes Shocks

03/20/2007 11:22 AM

"When you flip the plug..." is not possible on many countries' wiring systems. http://en.wikipedia.org/wiki/BS_1363 and http://en.wikipedia.org/wiki/BS_546 can't do this.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Manufacturing Engineering - New Member Hobbies - Target Shooting - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Charlotte, NC USA
Posts: 791
Good Answers: 17
#5
In reply to #4

Re: Question About a Fan That Causes Shocks

03/20/2007 11:36 AM

PWSlack

In the US, we only had two prongs of the same size until the mid 70's??? I think or was it later then that??? Until the change, plugs could and did go either way. After the change, the plugs now have one side bigger then the other and the socked changed to have one slot wider then the other. At that time they added a third 'hole' for a ground (earth) wire. Anyway, may household appliances are still around that have the older two prone of the same size plug. I agree with the comments above, I've see appliances wired with the neutral to the frame...

__________________
Be careful of what you wish for .....
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Question About a Fan That Causes Shocks

03/20/2007 11:43 AM

There is no information about the location of the problem in the post. One cannot assume the poster uses any of the plugs as described.

If the poster is not confident at her/his ability to solve the problem, then consulting a qualified electrician locally would appear to be the safest solution.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: El Lago, Texas, USA
Posts: 2639
Good Answers: 65
#7
In reply to #6

Re: Question About a Fan That Causes Shocks

03/20/2007 3:05 PM

One can assume that the plug is reversible, and that the shock comes from the metal housing, since these are both implicit in the post.

Register to Reply
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#13
In reply to #6

Re: Question About a Fan That Causes Shocks

03/21/2007 3:02 AM

Spot on. The user seems to lack the basic knowledge , and has not binned his appliance despite being shocked . It looks as though his sockets are only phase and neutral. His entire building may be fatally wired (as per my neutral switching point)

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply
Power-User
United States - Member - USA Engineering Fields - Control Engineering - Never enough money

Join Date: Feb 2007
Location: Oregon
Posts: 292
Good Answers: 4
#8

Re: Question About a Fan That Causes Shocks

03/20/2007 3:15 PM

This applies no matter what country you live in.

First step..... Get rid of the fan!!!!!!! It is not properly or safetly wired.

Second check your plugs wiring. If you live in the U.S. this will be very easy to do. Go to Home Depot, Lowes or just about anywere and purchase a $5.00 outlet/circuit tester. Follow the simple instructions for use and plug the thing into your outlets, if any of the lights show bad wiring CALL A QUALIFIED ELECTRICIAN to correct the problem.

If your home does not have the three pronged outlets installed I would strongly recommend having your home updated to todays standards.

Register to Reply
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#9

Re: Question About a Fan That Causes Shocks

03/20/2007 6:38 PM

If the shocks are coming intermittently then take your finger out of the blade. (sorry guys . . . couldn't resist). I crack myself up !

OK . . . everybody is right here about toss the fan and / or check house wiring especially if the house is a 1950 or earlier vintage.

__________________
If it eats, it's going to be trouble!
Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: May 2006
Location: Pittsburgh PA
Posts: 121
#10
In reply to #9

Re: Question About a Fan That Causes Shocks

03/20/2007 8:11 PM

Shouldn't you lick your finger first (I am sorry too.)

I would keep the fan as a nice suprise for "those" friends. Something about the 60 Hz shuffle.

Check wiring close, esp. if you got paper insul. Re-wire is probally best bet. If you are not sure, call an electrician.

And don't lick your finger

__________________
“There's a sucker born every minute, and I happen to be one of them”
Register to Reply
Power-User

Join Date: Dec 2005
Posts: 200
Good Answers: 8
#11

Re: Question About a Fan That Causes Shocks

03/20/2007 10:40 PM

The white or green fan wire is electrically connected to the fan housing. Locate and insulate or isolate the point of the ground from the fan housing to prevent electrical shock.

When the plug is clocked with the hot wire inserted into the common neutral receptacle, the fan housing becomes energized and the fan hot wire functions as a common electrical return (ground). The fan housing green ground wire is not properly connected. If so, the circuit breaker in the supply would safely trip the circuit to the "off" position if the electrical plug were clocked and inserted improperly.

Meanwhile to prevent shock and enhance safety, always insert the electrical fan plug clocked in such manner that the red or black hot wire of the fan matches the hot wire (phase A or B) or the electrical recepticle.

To enhance safety Install a three wire plug with a green wire attached to the fan housing on one end and the green wire attached to the receptacle ground. Problem is, the green ground may not be functional on the receptacle. The three prong wire plug can not be inadvertantly rotated and inserted improperly.

__________________
Corn Stoves
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#12

Re: Question About a Fan That Causes Shocks

03/20/2007 11:44 PM

The Windings-End which gives Shock; when connected to LIVE LINE of power has leakage to body of fan.

You can test it with a Multimeter [keeping for the highest Range for Ω position. Check between both points of Fan-Plug 1 by 1 & Body, The End shows less Ωs [k/MΩ] is the problem end. In test you may have to change range for more resolution.

Register to Reply
Commentator

Join Date: Jan 2007
Posts: 99
Good Answers: 2
#14

Re: Question About a Fan That Causes Shocks

03/21/2007 9:24 AM

You appear to have a 2 prong power plug and an older style power outlet that allows you reverse the plug connection. Since your fan has one of those power leads attached to the frame you have a potentially fatal situation, specially If children get involved.

1. Change your power outlet plug to a grounded 3 prong polarised type.

2. Attach a polarised power plug to your fan and or check for faulty wiring of the fan.

I agree with other postings, it was quite common to finf older appliances with one side of the power plug wired to the frame of the appliance.

I discovered this by accident one day in the kitchen. I had a deep fryer and a toaster plugged into the same socket. Both appliances were the older 2 prong unpolarised type of appliance with exposed metal frames. I tore off a sheet of aluminum foil and set it down on the counter. In the process the foil happened to touch the frame of both appliances at the same time and burned up in a flash that left me in disbelief as to what had happened. I went and got my Volt/Ohmeter and measured 120 VAC between the frames of both appliances, then ohmed out the power plugs discovering that both appliances had one side of the power plug attached to the frame. It could have been fatal had I placed my hands on both appliances at the same time as the current would have crossed through my chest and stopped my heart. I believe there are still some appliances with one power lead wired to the frames and even if you have a polarised power plug , If the power outlet is wired wrong you can end up with a LIVE frame. A cheap power circuit checker might save your life. I have found many miswired power plugs in the 3 houses I've lived in so far.

Register to Reply
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#15

Re: Question About a Fan That Causes Shocks

03/21/2007 10:02 AM

Anecdotes have their place here ;

When I was about 10 , the light bulb in my bedroom blew. The glass part of it broke as I tried to remove it . With the switch in the off position I put my fingers in the socket to remove the remains. If the house had been correctly wired it would have been no problem . The switch was on the neutral cable (which makes no apparent difference) , but that left the phase cable still live -'ouch' . Luckily because it was above my head I lived (electrocution causes mussels to contract , the fall resulting from shock broke the contact). Since then I have only been zapped once and lived because of size/contact area etc (a child would have died). Lessons .

Don't mess unless you understand.

Regard any circuit as live/potentially fatal.

Have due regard to the safety of others.

Never trust an unknown electricity source.

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: El Lago, Texas, USA
Posts: 2639
Good Answers: 65
#16
In reply to #15

Re: Question About a Fan That Causes Shocks

03/21/2007 10:15 AM

electrocution causes mussels to contract

This is why I always fire up Old Sparky when I make my Moules a la Mariniere.

Register to Reply
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#17
In reply to #16

Re: Question About a Fan That Causes Shocks

03/21/2007 10:59 AM

Belive me , I puckered like a ducks ****. Brit -speak misses out the 'a la ' bit but you're lips smack all the same. "viv la divranz"

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#18

Re: Question About a Fan That Causes Shocks

03/21/2007 1:33 PM

Akhill:

WHERE ARE YOU LOCATED???

There is alot of good advice here, but much of it is relevant ONLY to the US.

I would recommend disconnecting it from the wall... taking it apart... looking for frayed wires... and taping any bare wires with electrical tape. Particularly any place that could come in contact with the case of the fan.

If you do not feel comfortable doing this, I would throw the fan in the garbage and get a new one.

Sincerely

Bill

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#19

Re: Question About a Fan That Causes Shocks

03/22/2007 3:42 AM

Putting your finger in light socket to feel if there was power was the natural thing to do when i was young.

But I cannot get myself to do it now.

DONT TRY THISW AT HOME

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #19

Re: Question About a Fan That Causes Shocks

03/22/2007 5:04 AM

One could risk it at 120VAC and probably get away with it.

At 240VAC it is a practice that is not recommended. Been there. Done it. Secondhand T-shirt now for sale on eBay...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#21
In reply to #20

Re: Question About a Fan That Causes Shocks

03/22/2007 1:20 PM

PW

Is that T shirt the one with all the electrical burns on it? I thought of getting it, but then people might think I was an electrician.

Bill

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#23
In reply to #20

Re: Question About a Fan That Causes Shocks

03/23/2007 2:25 AM

It was 220Volt,

It only passes through the tip of your finger and we had wooden floors.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Anonymous Poster
#22

Re: Question About a Fan That Causes Shocks

03/23/2007 12:19 AM

Check whether the fan switch was connectec in phase or neutral. If it is connected in neutral then please connect in phase wire and check.

Register to Reply
Member

Join Date: Feb 2007
Posts: 6
#24

Re: Question About a Fan That Causes Shocks

03/23/2007 7:28 AM

ok.Now I Understand the reason behind it .Once thanks for all

Register to Reply