Sprinkler System Pressure Requirements

12/04/2010 5:12 AM

We are installing a water supply for our future house that will have a domestic fire sprinkler system. This system has a required flow rate of 1L/s for two sprinkler heads at once. There is a known head of 50m, (the water storage tanks are that altitude up the hill from the house site), and a main supply pipe (polybutylene) length of 250m from the tanks to the house.

Because of project timing we would like to install the main supply pipe between the tanks and the house before we know the length of the (probably) 28mm polybutylene pipe within the house to the sprinklers (the house design is not completed...).

Is it likely that a 50mm main pipe will be sufficient?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: sprinkler system pressure requirements if know flow rate, don't know pipe length

12/04/2010 1:01 PM

You'll need to know how many sprinklers you will have. 50 m head is roughly 60PSI. I don't do metric. I don't think you'll have enough pressure. You may need a booster pump.

Register to Reply
Participant

Join Date: Dec 2010
Posts: 3
#2
In reply to #1

Re: sprinkler system pressure requirements if know flow rate, don't know pipe length

12/04/2010 4:35 PM

By my calcs 50m head ~70psi?

The system we are installing is a cheap domestic sprinkler with a design that expects only sprinklers in one space to be required at a time, therefore the maximum number of sprinklers in one space is the design load or flow, rather than the toal number of sprinklers. This is the reason for the "two sprinkler heads at once", but for an extra margin of error because an area may end up very large, we could allow for say 4 at once.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: sprinkler system pressure requirements if know flow rate, don't know pipe length

12/04/2010 4:54 PM

There's more information here than you will ever use:

  1. Pipe flow rate calculation | calculate pipe pressure drop with ...

I assume the spec calls out a required pressure, too.

Good Luck.

Register to Reply
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#18
In reply to #1

Re: sprinkler system pressure requirements if know flow rate, don't know pipe length

12/06/2010 10:32 AM

Well it is actually more, and 50 M of head is on the high side for domestic supply, possibly a little to high. Domestic supply can drop as low as 20 psi during fire demands. The sprinkler system should be sized to meet minimum flows at a lowest available design pressure for fire flows per code, typically 20 psi nationally though local agencies can vary to higher requirements. Reference the national fire codes, AWWA standards, and uniform plumbing code as needed.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#19
In reply to #18

Re: sprinkler system pressure requirements if know flow rate, don't know pipe length

12/06/2010 10:40 AM

Yes, I finally went back and did the math. There are people here who are more current than I in this field. I'm taking myself out of the discussion.

Thanks.

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#4

Re: Sprinkler System Pressure Requirements

12/04/2010 11:11 PM

The only sure way to find out what you need is to contact the local Fire Marshall (or whatever the local fire official is called in your country/region) and find out what the system capability requirements are. Such questions as: how many open heads are the system supposed to maintain supply to and for how long; what are the volume capacity requirements for the storage tank; etc?

I am familiar with the USA NFPA codes and my states requirements but they wouldn't be of much help to you if you are expected to meet some other location's requirements. What you don't want to do, especially in a residential installation, is to install what you you think is sufficient and correct and then have Mr. Code Guy come in and tell it is wrong and to redo it. Also in many locations an inspection prior to installing indoor wall/ceilings/floors is mandatory so they can see for themselves what is contained within the system.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Power-User

Join Date: Oct 2010
Location: Indian Mills,Southern N.J.
Posts: 140
Good Answers: 5
#5

Re: Sprinkler System Pressure Requirements

12/05/2010 1:03 AM

when in doubt a design factor of 3 will cover your butt. I would build the system so if you had all the heads on a 1 time the system could handle it. you can always install a pressure reducing valve.. In the beautiful state of New Jersey as per AWWA you can not have a sprinkler system coming off of a domestic water service,they have to be completely separate. i think its a cross contamination thing.

__________________
anyone can F--*#@% up a design.It takes a good Man to fix it. Macgyverism at its best.
Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#7
In reply to #5

Re: Sprinkler System Pressure Requirements

12/05/2010 10:02 AM

It is people like you who impede the safety and growth of building construction. He is building a residence that is being supplied with water from an onsite tank, for God's sake. He does not have to put any sprinklers in, does he. Why not build for a design factor that will supply all heads at one time? well, for one, it will cost three times as much, directly reducing the odds that it will actually be built, on the order of choosing between poured cast in place walls versus laid up block, ie one is superior, but not cost effective. Just ease up people, and consider reality when you are suggesting solutions. If money were no issue, I'm guessing he would not be posting on CR4.

60 l min = 15.7 gpm

28 mm is more than adequate, sufficient at 60 psi, as long as you don't have more than average friction loss. As you increase flow rates, your supply duration will reduce. If you increase pipe diameter, your psi will remain constant, your flow rate can increase (sprinkler head quantity) but duration will be reduced. If your heads are heat activated, you really have very little downside, because success of the heads results in fire containment. 90 % of all fires are contained with one sprinkler head activation.

By the way, NJ has no requirement to have a separate sprinkler water supply system. A simple backflow preventer is usually all that is required. Of course, in this case, he won't need that.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Power-User

Join Date: Oct 2010
Location: Indian Mills,Southern N.J.
Posts: 140
Good Answers: 5
#16
In reply to #7

Re: Sprinkler System Pressure Requirements

12/06/2010 1:44 AM

hey et , eit ,pfr or what ever they refer to you at work when you walk away.why do you have to bring god into this. how exactly do i impede safety and growth of building construction. if you do not have to install sprinklers but choose to it doesn't give you the power to install the system any way you think it should be done. if you do it you have to go by the rules and regs. not the ones floating in your head. how much is 3 times the cost. poly pipe,a small pump,pressure valve and pressure reducing valve for this size system is peanuts. the reducing valve would prevent head fogging. in stating a design pactor of 3 i was being a bit fascias. what % for error would you use. i guess you wouldn't and your design would fall short again and cost the home owner more money for the change order to have a properly functioning SAFE system . it was not my intent to have all the heads on at the same time but the ability to do so if needed. I guess to you it is more important to have good water pressure in the shower than when your 3 year old is engulfed in flames do to the lack of sprinkler performance. in new jersey you can not have a domestic water service off of a fire service. i miss spoke. a commercial fire service has to be a completely separate line coming off the main. tested @ 200 psi for 2 hours with zero loss.(write that down) the awwa dictates public water in the r.o.w. and no one else. as far as poured in place walls versus 16"cmu's have you ever properly did a cost break down of this or did you use an old bid tab again. so how much is a 16" block. how many can a mason lay in a day. how much is his total package,how long will it take a crew of 4. how much is a cy of 3500 psi concrete,how much will you need,what is the total cost of the concrete,how much re bar and what size do you need,how much are the forms to rent,what is the cost difference per day and for the job.who are you getting your concrete from,are they state certified. what state are they from.what block company did you price the block,cement and sand from. do you have to take concrete test cylinders,how many per truck,what do the breaks cost. what type of cement do you use for the block. i will give you a hint. its type 1 , 2 or 3.how about in the concrete. was it from lafarge,o yea what plant. where the blocks weigh lites or super weigh lites. what was the cost difference. were you allowed to use them. what type do the masons like to use,why. so give me your break down. i guess you have to let your computer warm up because you have no clue to do a proper cost break down, you just punch numbers into a program that some one else set up 10 years ago with out updating cost change. did you add in for the lime,what %. how about the dura wall,how many feet. every how many courses. do you have to fill the webs.do you have to apply curring agent to the poured walls,what kind,how much,how soon after the wall is poured,what is the mix ratio. did you remember to put sleeves in the walls,oops another change order.well do you have your break down yet. never mind you took to long and your company lost another one. what type of filter media do you spec for pressure filters .do you use a backwash with an air scour,what do you do with the back wash water. do you spec layne products. do you like ford or Mueller curb stop and corp valves,compression or flared,why. how many turns does it take to fully open an 8" resilient gate valve. what psi do you test your 8"dip @.for how long. what is your allowable loss. what is your spec on taking water samples. do you use cl52 cement lined,do you use the same when needed for sanitary. do you like griffin,or us pipe. yup you do not know your job. you just run your mouth

__________________
anyone can F--*#@% up a design.It takes a good Man to fix it. Macgyverism at its best.
Register to Reply Off Topic (Score 6)
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#21
In reply to #7

Re: Sprinkler System Pressure Requirements

12/06/2010 11:25 AM

Actually, the PSI will not necessarily remain constant as you increase pipe diameters for transmission pipes.

Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#23
In reply to #21

Re: Sprinkler System Pressure Requirements

12/06/2010 4:35 PM

Actually, psi at head point does remain constant until flow is initiated. After flow is initiated (ie consumption) the larger diameter pipe will have less psi degradation.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#24
In reply to #23

Re: Sprinkler System Pressure Requirements

12/06/2010 4:59 PM

Well that makes very little sense, as static pressure would be constant at any point along the system that was static and the sizing of the pipe doesn't have any relationship to static pressure except wall thickness. For that matter under static conditions the sizing of the pipe doesn't actually effect the flow rate either, because the flow would be 0 for any pipe size in that condition. Change the pipe size and you change the head losses during flow.

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#9
In reply to #5

Re: Sprinkler System Pressure Requirements

12/05/2010 12:16 PM

A separate water supply IN NOT REQUIRED IN NEW JERSEY. As I stated in post #3, The only sure way to find out what you need is to contact the local Fire Marshall (or whatever the local fire official is called in your country/region) and find out what the system capability requirements are. The requirements of a sprinkler system are mandated by the NJ Fire Code (which is usually based on the NFPA standards) and the local building code (which is usually based on the NJ Building Code). To build a system based on a factor of 3 and with all heads working at the same time would be astronomical in cost and overkill. As others have stated, the operation of a residential fire sprinkler is based on one or two heads opening and containing the fire.

The installation of modern residential system is very simple in NJ and is accomplished with CPVC pipe and residential heads with an additional cost of $3-5,000 for new construction in a 3,000ft2 house. Retrofit is about 50% higher.

If you would like to benefit all NJ homeowners get on your state legislators/senators to pass the residential sprinkler law.

I am a fire chief in the "beautiful state of New Jersey" and I am seeing more and more minor fires which did not become "room and contents" or structure fires because the home owners were smart enough to install a sprinkler system. That one head can contain many fires and same both lives and property.

To learn more about residential sprinkler requirements call the fire marshal/fire inspector. Why spend money when it isn't needed or when it won't do the job you want it to do?

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#6

Re: Sprinkler System Pressure Requirements

12/05/2010 9:04 AM

50m appear to be good head for sprinklers. Even after the pressure drop due pipe and fittings friction you should get around 50 psi at sprinkler inlet, sound good enough.

50 mm sounds lot bigger for this requirement alone. 50 mm could be a good chaise.

50 mm pipe has 3 times the cross section of 28 mm pipe (not just double), which means 3 times the flow.

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply
Member

Join Date: Dec 2010
Location: St Johns, Newfoundland, Canada
Posts: 5
#8

Re: Sprinkler System Pressure Requirements

12/05/2010 11:17 AM

Yes,

You have a head of 50 meters. approx. 65 psi at the house; city pressures are usually closer to 100 psi.

Should a fire occur; the sprinkler heads in that area will be the only ones to erupt.

Therefore you could have enough volume / pressure to extinguish a ""One Room Fire"".

However, you can have a system designed, with pipe sizes, pumps, stymies connection for fire dept hook-up etc. that will eliminate gray areas and worry.

The majority of this system can be installed by yourself; the piping material and fittings are a form of plastic with primer and glue application.

This will also reflect favorably for you in House Ins. Premiums.

Not enough people are thinking as you are, if this were the case; the cost would be considerably less.

I hope this sheds a little light on your project.

Jim

__________________
Jupitor
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#10

Re: Sprinkler System Pressure Requirements

12/05/2010 4:25 PM

You don't say what the water supply is but only that the pressure tanks have 50 meters of head to overcome. If you are using a submersible pump you may want to consider the new constant pressure pumps now on the market. These pumps ramp up rpms to match the output. You will need to know your total demand and total head to match the pump. Generally, you will use this system but you need very little in terms of pressure tank capacity. Any decent pump installer should be able to match a system for you and this looks like an ideal case for constant pressure. I would strongly recommend them and is the system of choice for my own house. I have used Grundfos constant pressure pumps but find these a little more reliable and I don't have have a special motor. Good Luck.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Commentator

Join Date: Dec 2010
Posts: 89
Good Answers: 1
#11

Re: Sprinkler System Pressure Requirements

12/05/2010 4:26 PM

Great discussion fire Marshals, factors of 3 an so on. People really shouldn't give advice if you don't know.

1) fire marshals are not qualified engineers and if you're system didn't work they would be sues if they gave engineering advice.

2)state laws do not determine pressures at sprinkler heads, if fact there are no state laws for sprinklers other than for buildings legally required to have them and that does not include domestic residence under law.

3)where a building falls under legal requirements of sprinkler systems the fire marshals can provide you with minimum requirements of area coverage. If they offer advice on a design or product that does not work they are liable, again as they are not engineers.Fire safety is called that because it relates to the safety of lives not the saving of property. Safe exit routes etc

4)in respect to increase the pressure by a factor of 3 or any factor greater than the sprinkler head flow rate, you will create mist and lose the design and ability of the head to put out fires.

if you want to design a system, you need flow rate of litres/gallons per minute, a simple bucket test will tell you this. Secondly the size of your current pipe is moot, the flow rate and pressure will change when you downsize the pipe to fit the sprinkler, even if you ran 2 inch pipe to the head, the inlet of the head will only be about half an inch to an inch max, the purchased head will have a desired flow rate. Take 80 percent of you flow rate as you rate, after you attach the correct size to your tank line do the bucket test for litres per minute, or go an but a cheap 20 dollar engine pressure tester, the one with the rubber half sphere on it that goes on the spark plug outlet and place it on the end, it will give exact pressure, dive this by the sprinkler head pressure and it will tell you how many you need to use to have the right pressure on the head. Except in cases where there is mains line pressure this is exactly how it is done on the job.

Pressure/flow rate divided by the sprinkler head requirement to operate equals number of heads available. If you are wondering how buildings in the same area have different amounts of sprinklers, then they choose higher lower flow sprinkler heads, or put a line restrictor on the system.

I know a general conversation about hot rods or solar panels or any other engineering subject is great for throwing around ideas, but this involves the safety of human lives, and perhaps lack of actual knowledge should make you think twice before answering.(though we do appreciate the thought)

Archie

(I have held qualifications in sprinkler system design since 1996- Grovelly Tafe Brisbane)

Register to Reply Score 1 for Good Answer
Participant

Join Date: Dec 2010
Posts: 3
#12

Re: Sprinkler System Pressure Requirements

12/05/2010 7:38 PM

Hi folk, Firstly, thank you to all for your comments. I really appreciate all of them and the thought and effort made. When I posted the Q, I knew that I did not have sufficient detail for an absolute "yes or no" answer, just an, "It looks possible/I don't think it will work" recommendation, and I know a margin of error needs to be allowed. I think I need to clarify a few things too, and apologise for not making them clear earlier. I didn't think a very wordy question would invite many answers so had tried to just put down essential facts! I am in New Zealand, so the legislative environment is a little different from that for many of you. The domestic sprinkler industry is a relatively fledgling one here, as the Standard for domestic sprinklers that can be fed off the house water supply and be installed by suitably certified plumbers was only introduced in 2002. Prior to this, all sprinkler systems had to comply with the more expensive and higher standard of commercial sprinklers. These systems are not yet compulsory here, but I know they are worthwhile, especially because the location and access to my house site means the Fire Service, (a volunteer organisation in rural areas like my site), would really only be turning up to damp down the embers. My water supply will be any rainwater collected off my roof, draining to a smaller tank then pumped uphill to the two 25,000L tanks (with room for one more) 50m vertically up the hill from the house site, (which is as high as I can practically go on my site). The actual stored volume will therefore vary from season to season, and I accept that at times there may not be a lot left for fire suppression! I do not wish to use a pump for primary water supply pressure, as my power supply will be off-grid solar and wind, with diesel generator backup. One that switches on to boost pressure when needed might be possible, but is an additional expense and complication I would prefer to avoid. Because of the timing for my project, I really need to install the main water supply pipes to and from the tank prior to completing the house design, (as I will initially be living on site in temporary building), but do not want to install 250m of a pipe size that will make sprinklers useless. So any water flowing to the sprinklers will flow from these uphill tanks, through estimated 50mm pipe for 250m to the house, where it will enter the probably 28mm house loop of (guessing only) up to 70m full loop length, so 35m worst case, and then through any necessary extension to individual sprinklers probably ~2m max. The standard requires the flow for 2 sprinkler heads at once to be 60L/min 1L/s, and assumes that a maximum of 2 sprinklers are likely to be set off at once. I could contact certified installers for more detailed information about the system design, but they are still establishing themselves in a new field and of course charge for advice, so I came here. I will have to get someone involved at the time the design is finalised, but cannot afford it now. Thank you for your help with this. Sorry for the formatting: my paragraphing with line breaks seems to be removed on submission

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13
In reply to #12

Re: Sprinkler System Pressure Requirements

12/05/2010 7:49 PM

Good Luck.

Register to Reply
Commentator

Join Date: Dec 2010
Posts: 89
Good Answers: 1
#14
In reply to #12

Re: Sprinkler System Pressure Requirements

12/05/2010 7:57 PM

Install the largest affordable pipe to the house, therein lies the gravitational maxim, after you reach the lowest point of fall then you change down to your house line size - otherwise you only have gravitational; weight pressure not increased pressure by reduced line size, as for all these loops you mention, the fire system loop needs to be a separate line from the entry point to the house directly to the sprinklers. Reasons are.

1)the water will loose pressure by friction loss the more turns it has to make through your system

2)the system will be non operational or less operation if any other system is left running - or if plumbing repairs are needed in the house - in fact during construction if the fire line goes in first, any fire that ensues before the building is finished will be covered. Put on the heads as soon as the ceiling is up

3) in the event of a fire in the house they usually start low at floor or wall level, any system linked to general plumbing through the walls risks being destroyed in the first stages of the fire - not because the copper melts, usually a wall section collapses and breaks or kinks the softer heated pipe. So single line in from outside as short a route to the ceiling space as is possible.

Hope this helps

Register to Reply
2
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#15
In reply to #12

Re: Sprinkler System Pressure Requirements

12/05/2010 11:22 PM

Sprinkle-

I apologize for not knowing the standards and codes in New Zealand, I'm a New Jersey (USA) boy myself, but I do know that much of what has been posted is untrue and could get you in a lot of problems and possible at a big expense. I do know what (or know where to find it) is required in the USA for resident sprinklers and industrial systems.

Fire Marshals in Australia might not be certified engineers of sprinkler systems but Fire Marshalls in New Zealand have access to the codes and can direct you to personnel who can answer any questions you may have that they can not answer.

Installing the largest pipe financially possible will probably under size the pipe or else end up wasting money with a pipe larger than necessary.

The size of the pipe(s) feeding a sprinkler head does matter. Thats why reducing "T's" are used as the head gets further away rom the main feed.

If you are using sheet rock for the walls there is very little need to have the pipe feeding the water to the ceiling enter the building at the upper wall or ceiling from the exterior. If the head opens up it will, in most cases except a conflagration, confine the fire to a small area and the thermal insulation and fie resistance of the sheet rock will protect the piping.

The correct method to get the information you need is to contact those personnel who know, the fire professional, get the standards and codes, apply what is required and see what the system will entail. The statement posted by one contributor "People really shouldn't give advice if you don't know" follows several statements that are not supportive of a good sprinkler system. Go to the pros.

At least in the USA the statement "Fire safety is called that because it relates to the safety of lives not the saving of property. Safe exit routes etc". is not correct since fire safety includes life safety, properties safety, environmental safety and several other areas. Life safety is based on having safe properties.

I am the chief of the local fire dept and have been an emergency responder for over 40 years. I am also a retired Chem Eng with extensive experience in fire safety, personnel and property safety, environmental, among several other areas of the profession. I make it a practice of getting the best advice from the best sources available. Your life is potentially going to be saved or lost with this sprinkler system, don't be foolish and use such a forum as this to design a sprinkler system, go to the pros.

The following are several sites which looked like you could benefit from their content:

http://www.google.com/search?q=residential+fire+sprinkler+code&rls=com.microsoft:en-us&ie=UTF-8&oe=UTF-8&startIndex=&startPage=1

http://www.ircfiresprinkler.org/resources.aspx

http://www.usfa.dhs.gov/citizens/home_fire_prev/sprinklers/

http://www.fire.state.mn.us/GovernorsCouncil/ResSprinkWhitePaper113009.pdf

http://www.ircfiresprinkler.org/docs/Klein-Ballanco%20Residential%20Sprinkler%20Design%20Made%20Easy%20-%20Plumbing%20Systems%20and%20Design%20Mag.%20Sept%202008.pdf

http://www.ircfiresprinkler.org/docs/Reports/Prince%20George%20County%20Maryland%20Residential%20Sprinkler%2015-year%20Experience%20Report.pdf

http://www.ircfiresprinkler.org/docs/Res_Sp2_v0017-FINAL.xls

Remember, no matter where you live FIRE KILLS.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2009
Location: Land o' Lincoln
Posts: 124
Good Answers: 7
#22
In reply to #15

Re: Sprinkler System Pressure Requirements

12/06/2010 3:00 PM

In my opinion, very sound recommendations. Speculation may lead to overdesign or under performance. And when dealing with something as critical as fire protection, under performance is not desired. Considering Sprinkle may become a design reference for NZ authorities, it would be best to design to the best available technology. As noted previously, NFPA 13 on sprinkler systems, provides design guide for pipe sizing, water flow, and pressure requirements and should provide the basis for a sound design. The references posted, upon quick scan only, seem to provide clear direction for installing a well thought out system.

__________________
If you can't do it right the first time ... do it wrong, then let the professionals fix it.
Register to Reply
Anonymous Poster
#17
In reply to #12

Re: Sprinkler System Pressure Requirements

12/06/2010 7:50 AM

I don't know if you get ahold of a copy of NFPA 13D, but that would help you out. I belive you have a good idea and should have enough water and pressure for a resident system. Look inot listed plastic pipeing if you can get ahold of it. In the US, you would need sevral inspections and maybe a design by a registered engineer. or maybe not. In TN, a P.E. in needed for any facility above 5,000 sq. ft. I am a register P.E. in fire protection and I hope this helps out.

Register to Reply
3
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#20
In reply to #12

Re: Sprinkler System Pressure Requirements

12/06/2010 11:05 AM

Sprinkle-

Here are some more links which will probably be of more total help to you than some of the postings. These tell you how to do what you have to do.

http://www.toolbase.org/Design-Construction-Guides/Plumbing/Fire-Sprinkler-Design-Guide

http://www.azfma.com/files/blazeng.pdf

http://www.sjfd.org/fireprev/sprinklersystems.pdf

http://www.wbdg.org/ccb/browse_doc.php?d=8091

http://www.wbdg.org/design/dd_fireprotecteng.php

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 3)
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: