Reducing Temperature in a Cooling Tower

03/25/2007 2:45 AM

Dear Sir

i asked u to please some information about cooling tower, how we reduce temperature of our cooling tower ambned temperature=28C to 32C our requirement is 22C, if total recycled water=500mt/hour temp of hotwell Temp= 48C where water goes to cooling tower (induce type ) and cooling temp we get 28C to 32C in hot day its is the problem create on vacuum system, please briefly under stand me.

Thank you

yours truly

Khalid Azam

Reply
Pathfinder Tags: cooling temperature Vacuum
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Reducing Temperature in a Cooling Tower

03/25/2007 10:46 PM

Khalid,

I had a problem like this years ago and corrected it by cleaning the area where the water begins to drain into the structure and adjusting the inlet flow rate.

Good luck,

Ted

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Reducing Temperature in a Cooling Tower

03/26/2007 4:38 AM

Many years ago an inexperienced engineer at a primary pharmaceutical manufacturing works in Dagenham complained at the high temperatures of the cooling water circuit that occurred during a hot and particularly humid summer. This individual hadn't understood use of psychrometric charts as a guide to the performance of cooling tower systems at different times of the year.

The minimum air temperature in a cooling tower is the wet-bulb temperature of the air passing through it. As the air approaches this temperature, there is less scope for the water to evaporate to absorb the sensible heat. At the wet-bulb temperature, that's it: one cannot go lower.

To go to a lower service temperature than the local wet-bulb, and certainly to maintain a constant cooling medium supply temperature (why?), one must use some form of refrigeration. One might also question the "requirement" for 22degC in the context of the process plant where the cooling service is required.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Brecksville, OH
Posts: 1621
Good Answers: 18
#4
In reply to #2

Re: Reducing Temperature in a Cooling Tower

03/26/2007 9:08 AM

An excellent reply. Other than a refrigeration system it is impossible to get to lower than the wet bulb temperature.


I have observed that few engineers have a good grasp of use of the psychometric charts. If a tower is properly designed and maintained, it will do what it is engineered to do. Unfortunately, other operators will add on heat loads not initially intended for the system and then wonder what happened.

__________________
"Consensus Science got us into this mess, then why can't it get us out?" : Rephrase of Will Rogers Comment
Reply
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#3

Re: Reducing Temperature in a Cooling Tower

03/26/2007 4:53 AM

Khalid

Been a few years since I had a brush with cooling towers. However, puzzles like this are great fun. Just don't take this response too seriously.

Since the calculations for cooling flow are done in advance of the tower construction, I'm in general agreement that a flush, cleanup or overhaul might be indicated to bring the tower back into line. But as these are generally done in the off-season anyway, perhaps you might examine a re-calculation of tower size or some creative modifications.

Hypothetically, the cascade's effectiveness might be enhanced through the provision of a shade canopy or incremental extension of the vanes, producing a greater turbulence and air exposure to the coolant; or the tower might be supplied with a supplemental radiator or titanium heat exchanger cooled by the first circulation of the newly cooled cooloant.

Mark

Reply