Tripping of Feed Pump

12/24/2010 2:30 AM

hello everyone,

i have a problem with feed pump motor/starter system, it's 110 kw motor with soft starter make seimens and model 3rw44

Problem is that motor trip any time may be after 3 hours or 24 hour remain uncertain and start again after removing trip

after checking parameter of soft starter i find that current shown in soft starter display are very much uneven say r-67, y-70 , b-95 but on motor terminal its same 128 +/- 3 volts

firstly i change motor as current in soft starter are not in range but problem remain same with new motor too.

what to do now , kindly suggest

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: tripping of feed pump

12/24/2010 2:54 AM

Obviously soft starter problem.Try and by-pass the soft starter with ordinary starter and observe results for one or two days.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply Score 1 for Good Answer
Member

Join Date: Dec 2008
Posts: 6
#13
In reply to #1

Re: tripping of feed pump

02/02/2012 11:06 AM

i had bypass the soft stater by putting a timer with 15 sec. time after getting start by same & solve the problem

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: tripping of feed pump

12/24/2010 3:36 AM

These numbers are somewhat confusing. 110 kw ≈ 150 hp. A 460/3/60 motor would draw about 180A, a 230/3/60 motor about 360A. The unbalance on a new motor does make the soft starter look suspect, as Ramvinod notes. Or possibly a wiring fault such as moisture in the insulation. Some megohm testing would be in order.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Tripping of Feed Pump

12/24/2010 10:08 AM

This sounds like a wiring problem to me. Disconnect the wires at both end and megger them to ground. Sounds like you have a phase conductor partially shorted to ground that is sucking off current.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Tripping of Feed Pump

12/24/2010 11:51 AM

The 3RW44 has integral bypass contacts. After ramping, the motor is DOL from then on. If it tripped in 2-3 hours, it probably has nothing to do with the soft starter other than the protection system may be doing its job.

The protection built in to it does monitor for phase current imbalance and even if you do not set it to trip at a specific unbalance percentage, it biases the thermal OL curve so it will eventually trip on OL to protect the motor windings from further thermal damage. You did not state what the trip was, it is recorded in the 3RW history, I suggest checking into that.

When you are reading the different values between what the soft starter says and what you see on the output terminals, when are you reading that? If it is during the ramp sequence, your meter may not be capable of accurately representing the chopped sine wave current. If it is after the ramp is complete, they should agree. The 3RW44 just has CTs inside that are reading the current, there is no magic involved. So either you are doing something wrong with your meter or there is something seriously wrong with your 3RW44, like maybe it is so small compared to the motor that you are saturating the internal CTs? You may also have the 3RW44 set up to think it is being used "inside the delta" when in fact you are not, or vice versa.

I suggest before you do anything else, step through ALL of the parameters and write down everything that is set. The back of the manual provides a list for doing this. If you don't have the manual, or yours is more than 2 years old, download the latest version from Siemens. If you see a lot of things you don't understand, post them here and I will try to help if I have time. Or do the routine to reset everything back to factory defaults and start over.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#5

Re: Tripping of Feed Pump

12/24/2010 3:18 PM

What are you pumping what is the mechanical conditions present?

__________________
klearzen
Reply
Member

Join Date: Dec 2010
Posts: 5
#6

Re: Tripping of Feed Pump

12/25/2010 12:21 PM

Is soft starter in series with motor power supply from it's MCC feeder during normal running of motor? If it so ,then Soft starter is a culprit, since soft starter's current out put is not balanced as mentioned by you.

Reply Score 1 for Off Topic
Anonymous Poster
#7

Re: Tripping of Feed Pump

12/25/2010 2:49 PM

Tripping always occurs when current higher than should be. It might happen that the resistance to flow in the installation is lower that predicted. That would cause feeding more than the feed that is normal, which always increases power consumption by motor driving the pump. You have two options: one on electrical side and another on hydraulic side:

Hydraulic side: Place Orifice in the flange of the suction part of the pump. Proper size would probably be aperture 90% of the flange aperture.

Electric side: Increase level of the tripping current by 10%.

Proper way would involve flow measure vs current of motor and finding out what to do!

Good luck as it is to late for knowledge for you!

Advise is not to trust what I wrote, as I do not have any idea about your system. This problem might relate to wrong selection of trip for the range of the operation of your pump.

Reply
Member

Join Date: Dec 2010
Posts: 5
#8

Re: Tripping of Feed Pump

12/26/2010 1:30 PM

Is soft starter in series with motor power supply from it's MCC feeder during normal running of motor? If it so ,then Soft starter is a culprit, since soft starter's current out put is not balanced as mentioned by you.

Reply Score 1 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: Tripping of Feed Pump

12/27/2010 11:51 AM

AGAIN,

That soft starter has integral bypass contacts. At the end of ramp, i.e. 10-30 seconds later, the bypass contacts close AND THE SOFT STARTER IS NO DIFFERENT THAN A DOL STARTER. Nothing the soft starter does, or doesn't do, is going to affect the tripping 2-3 hours into it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#10
In reply to #9

Re: Tripping of Feed Pump

12/27/2010 4:00 PM

Good point - check one or more of the bypass contacts are not cooked.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#11

Re: Tripping of Feed Pump

12/27/2010 6:46 PM

Yet one more time... no further input from a "guest" after posting a question asking for aid and receiving responses from the community.

Me thinks in the future, I will ignore requests from guests.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Member

Join Date: Dec 2008
Posts: 6
#12

Re: Tripping of Feed Pump

09/25/2011 10:20 AM

Thanx to all my friends for reply

my office IP was Blocked i don't know way

i had put a new soft stater in place of old

and problem solved

Reply
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (1); Anonymous Poster (1); gosainmanoj75 (2); JRaef (2); klearzen (1); North of 60 (2); ramvinod (1); rilengr (2); Tornado (1)

Previous in Forum: Could Anyone Identify What Component is This?   Next in Forum: NGR of Parallel Generators...

Advertisement