Pipe Insulation

01/20/2011 12:09 AM

Can high density glasswool pipe insulation with aluminum foil vapor barrier and then wrapped in polythene sheets (like that of garbage bags) be used for insulating domestic hot water supply and return pipes buried underground at a depth of 3 feet and running in lenghts of about 9000 feet?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Pipe Insulation

01/20/2011 12:33 AM

For a hot pipe, is a vapor barrier necessary at all, or would it actually trap vapor that otherwise would move away from the pipe?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Sep 2010
Posts: 16
#2
In reply to #1

Re: Pipe Insulation

01/20/2011 1:43 AM

No. You do not need a vapour barrier. however one does need something to hold the glasswool together. Roll of canvas should do. Word of caution. Glass wool should only be handled with gloves and goggles preferably.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2010
Posts: 34
#3
In reply to #2

Re: Pipe Insulation

01/20/2011 3:40 AM

What will happen to the thermal conductivity of glasswool insulation directly buried in soil when the soil becomes wet from rain and groundwater? It would appear that the insualtion will just soak with water and loose its insulating properties???

Register to Reply Score 1 for Good Answer
2
Anonymous Poster
#4
In reply to #3

Re: Pipe Insulation

01/20/2011 6:11 AM

This needs to be studied. 3' underground. Chances of groundwater body coming in direct contact may be limited. Rain water percolating down may cause some concern. you need to take a call on the location and study the environmental conditions before deciding the correct course of action. We cannot always have one cut fit all.

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#13
In reply to #4

Re: Pipe Insulation

01/20/2011 11:54 PM

Wise statement! The ground ambient temp at 3 feet of depth working against the heated temp of the water in the pipe, would create condensation issues despite the type of bulk fiber insulation used or the conduit/vapor barrier encasement. Gary

Register to Reply Score 1 for Good Answer
2
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#5
In reply to #3

Re: Pipe Insulation

01/20/2011 9:42 AM

"What will happen to the thermal conductivity of glasswool insulation directly buried in soil when the soil becomes wet from rain and groundwater?"

What will be the thermal conductivity of your glasswool when compressed by burial?

__________________
Semper Ubi Sub Ubi
Register to Reply Good Answer (Score 2)
Associate

Join Date: Dec 2010
Posts: 34
#6
In reply to #5

Re: Pipe Insulation

01/20/2011 3:09 PM

In non rocky soil, rain water from continuous downpour has no place to go but down at least till it will hit our insulation! If the vapor barrier has any crack the insulation will certainly soak up the water and keep it there for a long time. Would'nt this play havoc with its thermal conductivity more than the compression of insulation would?

Using glasswool for direct bury application seems risky and it would help if anyone out there could relate their experiences or share their knowledge about this matter.

Thanks

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#25
In reply to #3

Re: Pipe Insulation

01/21/2011 6:00 AM

GA (Good Answer!) for a good question!!! Strangly enough!!

But buried hot pipes do need a sealing barrier to prevent water ingress.......I also wonder if even if water does not enter, what happens with the insulation factor if the glass wool is highly compressed by the weight of the earth around it? Probably works far less well......

Perhaps there is a better type of insulation for this type of installation? Its not my area of knowledge, sorry.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Anonymous Poster
#7

Re: Pipe Insulation

01/20/2011 10:38 PM

9000 feet of domestic hot water is about 300+ gallons in the pipe alone. So you would want to heat 300+ gallons just to get the pipe full? I would move the heater closer to the user.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#8

Re: Pipe Insulation

01/20/2011 10:42 PM

Add along with proper wrapping of wooden shred will increase heat transfer insulated coefficient economically and efficiently!

Register to Reply Off Topic (Score 5)
2
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#9

Re: Pipe Insulation

01/20/2011 10:44 PM

Why not look into using either Rock Wool or Mineral Wool that is wrapped (not too tightly) around your heat pipe and then inserted into a large enough PVC carrier pipe with solvent welded or push-on rubber gasketed joints? That way you avoid the entire issue of water percolating down into your pipe trench and damaging the insulation.

Just a thought....I'm doing it that way for the heat pipes going to and from my solar collectors mounted on the tool shed out in the backyard.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Dec 2010
Posts: 89
Good Answers: 1
#10
In reply to #9

Re: Pipe Insulation

01/20/2011 10:53 PM

quite right, glass wool is a poor insulator it is merely a suspension device to create an air gap, Glass itself actually conducts the heat and as previously noted water contact would create a heat sink, the idea of the enclosure pipe has my vote,

However the comment regarding the 9000 foot volume of hot water is the most noteworthy, at that distance it would need to be a heated pipe to constitute the word "hot", you are talking about 3 kilometers. the question is not real or the writer clueless to the task at hand

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#11
In reply to #10

Re: Pipe Insulation

01/20/2011 11:09 PM

Also when you trench 3' deep through undisturbed soil you are creating a two mile long, 3' deep soft spot in the ground that will probably collect and hold water like a resevoir.

Probably encasing it in some thin walled pvc with insulation, sealed, would be the best bet. Then you can compact the heck out of the backfill to avoid attracting water in the trench.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#14
In reply to #9

Re: Pipe Insulation

01/21/2011 12:05 AM

Rockwool is another alternative as suggested. Rock wool of suitable thickness+ Vapor barrier+ Hessian cloth + Chicken wire mesh + Cement plaster may give strength to the structure in addition to the insulation.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2006
Location: Western Pennsylvania, USA
Posts: 761
Good Answers: 9
#29
In reply to #9

Re: Pipe Insulation

01/21/2011 9:21 AM

You beat me to some of the ideas I was kicking around.

Why not Foamglas?

Foamglas® Pipe & Block Insulation by Pittsburgh Corning

Pittsburgh Corning's FOAMGLAS® pipe and block insulation is a lightweight, rigid insulating material composed of millions of completely sealed glass cells, each an insulating space.

Foamglas pipe insulation's all-glass, closed-cell structure provides an unmatched combination of physical properties, it is impermeable to moisture in any form, cannot burn and it is non-combustible. Foamglas pipe and block insulation is used most frequently in applications involving process piping, tanks, vessels and equipment which are most commonly used by the gas processing, refining, petrochemical and specialty chemical industries. Temperatures from -450°F to +900°F (-268°C to +482°C).

Uses:

  • Low temperature pipe, equipment, tanks and vessels
  • Medium and high temperature pipes and equipment
  • Hot oil and hot asphalt storage tanks
  • Heat transfer fluid systems
  • Hydrocarbon processing systems
  • Chemical processing systems
  • Above ground and underground steam and chilled water piping
  • Commercial and institutional piping and ductwork

FOAMGLAS® insulation is:

  • Resistant to water in both liquid and vapor forms
  • Non-corrosive and will not support corrosion
  • Non-combustible - will not absorb flammable liquids or vapors - cannot burn
  • Resistant to most industrial reagents
  • Dimensionally stable under a variety of temperature and humidity conditions
  • A material with superior compressive strength
  • Foamglas pipe insulation is resistant to vermin and microbes
  • Fiber, CFC and HCFC free
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#32
In reply to #29

Re: Pipe Insulation

01/21/2011 11:43 AM

Looks good! I suppose Tornado would need third party testing before he could allow this recommendation to be posted. Gary

Register to Reply
Guru

Join Date: Sep 2006
Location: Western Pennsylvania, USA
Posts: 761
Good Answers: 9
#35
In reply to #32

Re: Pipe Insulation

01/21/2011 7:32 PM

Depending, I would maybe use Cheap SDR as a "casing".

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#36
In reply to #32

Re: Pipe Insulation

01/22/2011 12:48 AM

Are you crazy? The thickness and thermal conductivity of the Foamglass material are quite easy to understand as part of well known thermal transfer. Moreover, I wouldn't be surprised if it has been suitably tested. I have heard of it before, but most of my work has been with low temperature piping, so I forgot the name.

High vacuum has very low thermal conductivity (approaching zero), so a thin layer of it, as in a Dewar flask or Thermos bottle, makes for good insulation. Your claims are fantastic, but you haven't given a good rationale of how your material is supposed to work. And by halskinner's complaints, it doesn't seem that testing labs support this concept, either. To say the least, it is very unconventional.

I don't mean to me a slave to conventional thinking, but the burden of proof belongs to the person making the extraordinary assertion. It is not my homework to furnish proof of your concepts. If you think I missed out on something, fine--please give a brief and cogent explanation. Your insults are counterproductive.

I like several aspects of this coating, but because of your attitude, I would not authorize, purchase, or recommend it. But go ahead, keep shooting yourself in the foot. Indeed, I think your insulting tactics could be the hallmark of a fraudster.

Neither you nor your buddy has given a competent citation of the Las Vegas study. Why not?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#47
In reply to #36

Re: Pipe Insulation

01/22/2011 8:25 PM

You are correct in your assumption. I am Crazy! If I were trying to sell you something, it would be incumbent on me to prove the value of my product for your project. However, you are not the OP and I was not talking to you before you interrupted the conversation with your derogatory commentary. I don't care what you think of Hal, Me or Cerama-Tech! Either contribute to the OP's needs with your own recommended solution or stay out of my conversations. I could care less if you understand how Cerama-Tech works, as you have made no effort to understand it and you repeatedly questioned it's properties without attemptiong to gain real experience or research. As for my attitude, don't start no crap, there will be no crap! No insult intended! As for why no one has provided you with additional information, you haven't expressed a legitimate interest in any application that justifies impressing you. Nor would I ever attempt to do so!! God Bless You and Yours and I wish you a happy New Year!

Gary

Register to Reply
Guru

Join Date: Sep 2006
Location: Western Pennsylvania, USA
Posts: 761
Good Answers: 9
#39
In reply to #32

Re: Pipe Insulation

01/22/2011 7:55 AM

You were right!

In Las Vegas no less, with w****s, slots, and mind expanding libations.

A 3rd party evaluation in Las Vegas???

Those who can't or never did pontificate.

Y'all have a good day now.

Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#40
In reply to #39

Re: Pipe Insulation

01/22/2011 1:13 PM

Insulting students and professors because their University is located in Las Vegas seems childish. Gary

Register to Reply Off Topic (Score 5)
Guru

Join Date: Sep 2006
Location: Western Pennsylvania, USA
Posts: 761
Good Answers: 9
#41
In reply to #40

Re: Pipe Insulation

01/22/2011 2:02 PM

childish!

That is me, most get back what they give.

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#42
In reply to #41

Re: Pipe Insulation

01/22/2011 2:35 PM

I gave you a compliment about your post and the UNLV folks didn't do anything to you. Tornado has taken upon himself to attack Halskinner and now me whenever Cerama-tech is mentioned. He wasn't attempting to answer the OP's question. He was blatantly interrupting with the purpose of criticizing a product he knows little about. My comment was directed at him as he has appointed himself the third party testing monitor of the group. I do think our posts were the best recommendations for the OP's situation. Gary

Register to Reply Off Topic (Score 5)
Guru

Join Date: Sep 2006
Location: Western Pennsylvania, USA
Posts: 761
Good Answers: 9
#43
In reply to #42

Re: Pipe Insulation

01/22/2011 2:50 PM

I will apologize to you.

It was meant to counter Tornado's inane comments, here and on other threads.

I am a SSPC certified coating inspector, have done a lot of CUI, and I understand and respect any kind of ceramic technology.

Living and working here in The Marcellus, I see a lot of potential for your product, along with FoamGlas.

I did a pretty neat job for the oil sands in Alberta, where almost any other technology was unsuitable.

Tornado caught me at a bad time, I guess, thanks for taking me to task.

Like another guy who asked for some ASTM info and I shared a legal copy of the standard, of course he would Copy and paste parts of any standard his company had, but he reported me as posting copyrighted material.

Sometimes it does not pay to try be helpful.

Do you have a presence here in Pennsylvania?

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#44
In reply to #43

Re: Pipe Insulation

01/22/2011 7:37 PM

I thank you! Perhaps I am a bit sensitive. Every time I post on this site, someone takes it upon themselves to belittle me. I truly thought you were in support of Tornado's bent. I must have been delusional if your comment was tongue in cheek and I missed that. Penn is not saturated and we could use a rep there. Gary

Register to Reply Off Topic (Score 5)
Guru

Join Date: Sep 2006
Location: Western Pennsylvania, USA
Posts: 761
Good Answers: 9
#45
In reply to #44

Re: Pipe Insulation

01/22/2011 8:00 PM

Gary,

You were dead on, and his post rambled belittling both of us. As the saying goes, theory is great, but the practical world workings prove or disprove a idea, theory, or product. Tornado seems to be a person who has NO practical experience at all, and the theory makes me shake my head also. He has tossed out some crack-pot ideas on other threads, belittling all of the responders, who usually are in pretty close agreement.

Check out this thread:

http://cr4.globalspec.com/thread/64482#comment677953

As to the ceramics, me, always being a seeker of knowledge, first heard about ceramics way back in 1962, as a sophomore in HS. A friend declared he was going to go to Penn State for Ceramic Engineering. What in the heck was that? Living near PPG and the Corning Labs, I started reading and after HS, actually called on these labs for some info. I kept reading from there, and have been pleased with the properties I have seen and the many uses ceramics have been put to good use in industry.

I clicked on your link, but for some reason, I am having script problems with it.

Keep up the good work, and check my LinkedIn page out to see just what I all I am into.

Respectfully,

qaqcpipeman

http://www.linkedin.com/profile/view?id=73141802&locale=en_US&trk=tab_pro

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#48
In reply to #45

Re: Pipe Insulation

01/22/2011 8:30 PM

Huh? In the thread you cite, we seemed to be in substantial agreement, and you called one of my comments "right on." You now seem to be confusing me with "lifeisenerventure".

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#46
In reply to #44

Re: Pipe Insulation

01/22/2011 8:07 PM

Oh, cry me a river.

You seem to have an excellent and versatile coating product, but you are making thermal claims about it that are highly unusual. Despite repeated requests for an underlying explanation or recognized testing, you have furnished nothing cogent. Instead, you have resorted to evasion and insults.

Just get an independent party to prove that this product has a consistent R-value per unit of thickness. If/when such results are in hand, you will have confirmation of your claims. But if independent testing fails to confirm the claims, discontinue them and focus instead on what can be proven.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#49
In reply to #46

Re: Pipe Insulation

01/22/2011 8:34 PM

Please get off my back! Who cares if you are convinced? Does everyone in this group care whether you approve of a product or not? Cry me a river in deed! Gary

Register to Reply Score 1 for Off Topic
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#12

Re: Pipe Insulation

01/20/2011 11:10 PM

999, I would recommend coating the pipes with Cerama-Tech coating during the installation. This will retain the heat in the lines better than exterior wraps without the moisture degradation concerns and will protect the pipes from deterioration when in contact with soils.

Warm regards,

Gary A. Coffing, Sr.

830-899-4700

www.ct-texas.com

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #12

Re: Pipe Insulation

01/21/2011 12:17 AM

Ceramic-enriched paint may be a superior coating, but unless its thermal conductivity is essentially zero, it can't really be much of a thermal insulator. (Unless applied really thick, like inches.) The marketing for this should focus on corrosion resistance, durability, and reflectiveness--but not insulation.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#17
In reply to #15

Re: Pipe Insulation

01/21/2011 12:47 AM

I would agree with your comment, however, you may be missing the thermal conductivity/emissivity of the product of 90%. 90 percent of the heat within the pipe is reflected back in wards toward the source. The other insulation and conduit recommendations require dry air space for the insulation to perform. The cool ground temp and the hot water in the pipe will create condensation and thus nullify the insulation values intended. A coating with high reflectivity and low emissivity is the best solution to this equation. The added protection of the pipe against corrosion/decay is a bonus. Gary

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18
In reply to #17

Re: Pipe Insulation

01/21/2011 1:21 AM

I agree that the emissivity would be a good feature of this product, but I think it is unwise to conflate it with thermal conductivity. There is a risk of underperformance on the thermal conductivity aspect, which could wipe out the successful aspects. When halskinner complains about testing labs, it places his credibility in doubt.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#19
In reply to #18

Re: Pipe Insulation

01/21/2011 1:55 AM

Help me understand your concern. If a 200 degree F heat exhaust pipe is coated with Cerama-Tech and it reduces the temp to 100 F degrees, would that not indicate that the same coating could reduce the heat loss into the relatively stable ground ambient temp soils? The outside air is the ambient and the interior pipe temperature is the source. The water pipe is heated and the ground is cooler like the air. Hal is very excited about the product and can sometimes come off as a little incredible in the way he presents it's attributes. I would not want to present the product as the cure all, however, given this extraordinary request for insulating a 9000 ft run of Hot water pipe in 3 ft deep soils, I would back this product against the other suggestions. Gary

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#20
In reply to #19

Re: Pipe Insulation

01/21/2011 2:32 AM

This is underground. Air temperature is irrelevant. There is no light (or solar radiation) to be reflected. I could be wrong, but I do not believe that this material would reduce the temperature by 100°F between the inside and outside of the coating, if it anything like the normal thickness of paint-like coatings. The concept of temperature gradient times thickness is fairly simple, but you guys don't seem to address it in your presentations. Sooner or later, it may bite you.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#21
In reply to #20

Re: Pipe Insulation

01/21/2011 3:26 AM

I agree that this is underground. What part of this exercise has anything to do with solar radiation? The heat from hot water and solar radiation react the same way when they come in contact with this coating. They are repelled back to where they came from! Certainly not 100 percent, however, more than you would like to believe!! If you coat a hot water pipe with this product, it will retain far more heat than if you were to wrap it with fiber bulk insulation. Gary

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#22
In reply to #21

Re: Pipe Insulation

01/21/2011 4:04 AM

I would like to see an independent lab test that confirms this. Halskinner had a weird "conspiracy theory" complaining about why this hasn't happened. Maybe there is updated news about this?

(So far all I have heard is unverified (unverifiable?) sales hype.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#23
In reply to #22

Re: Pipe Insulation

01/21/2011 4:35 AM

The proof is in the putting! I researched the product through the Internet and made a commitment to market the product along with several others. I found studies done by the University of Las Vegas that confirm my assertions. I still can't understand what this has to do with the OP's request. If you require independent lab tests to help you understand how this product works, please investigate these on your own. In the meantime, I recommend coating the underground pipes with Cerama Tech. Gary

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#24
In reply to #23

Re: Pipe Insulation

01/21/2011 4:59 AM

That didn't produce one iota of usable data. Thanks a heap.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#31
In reply to #24

Re: Pipe Insulation

01/21/2011 11:23 AM

Do your own homework, Junior. You'll thank me later. Gary

Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#50
In reply to #15

Re: Pipe Insulation

01/22/2011 9:06 PM

Cerama-Tech is not a Ceramic-enriched paint. It is a carefully designed coating. G

Register to Reply
Power-User

Join Date: Aug 2009
Posts: 100
Good Answers: 8
#16

Re: Pipe Insulation

01/21/2011 12:36 AM

I would be curious to know whether frost is an issue and if ground water is an issue. Here in Alaska we use Arctic pipe of various types all of which are basically a pipe within a pipe using closed cell foam as an insulator layer between the two. For frost protection there is often a void for a heat trace cable to run through. This type of arrangement has proven it's superiority over all other systems for many years. Whether holding heat in, or holding cold out I think this will be your best long term solution. Almost any major pipe supplier can source this for you.

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#26

Re: Pipe Insulation

01/21/2011 7:16 AM

I'm a bit confused. (No hard to do at my age) Why does the OP want to run a hot water line this long? What is preventing heating the water closer to the use site? Just wondering if the cost benefit has been considered here.

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Associate

Join Date: Dec 2010
Posts: 34
#27

Re: Pipe Insulation

01/21/2011 7:33 AM

The generous and rich responses have shed useful light on the subject and each one of the respondents deserve loads and heaps of gratitude.

The matter at hand is that insulatiing buried domestic hot water (supply and return) cPVC pipes is stated without any details or specific reference about the type of insulation. The long runs of these pipes to about 18 buildings from the central heating plant (storage type calorifiers in which water is heated by steam from adjacently located gas fired boilers) needs to be insulated. If we add up the circuits it adds up to a lot of pipe and insulation. The claim for a variation order did not succeed because insulating the pipes is indeed stated in the specs. Therefore any solution needs to be functional and acceptable to the client and at the same time afordable. This is why glasswool insulation instead of preinsulated HDPE (High Density Poly Ethylene) cPVC pipes is being considered. The HDPE would not absorb water (as even low density coffee cups from such material don't) so this would have been a good alternative, but once again the cost barrier cannot be broken.

How about if we encase the pipes in concrete after first insulating them with glasswool that has aluminum foil vapor barrier and polythene bags are wrapped around this assembly to seal it good to keep the water of concrete from getting in. We can then backfill above this concrete and this will eliminate the problem of compression of insulation and of water getting in?

Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#28

Re: Pipe Insulation

01/21/2011 8:51 AM

I don't know exactly where you are located, but burying this heated pipe 3 feet down suggests to me that you're dealing with a ground frost issue there? Around these parts in upstate NY (Albany area and surrounds) we typically experience frost to at least 4 feet below grade, although I've seen it go down to no less than 8 feet below grade one winter (1994) in Amsterdam NY during a nasty cold snap when we were trying to locate a massive water main break....losing no less than 15 MGD from a 21-inch CIP main! The ground in that location was porous sand with a fairly large void structure, therefore permitting extensive frost penetration.

Typically, in this area we provide at least 5.0 Feet minimum depth of cover above the crown of water mains and 4.0 feet minimum cover atop sewers to prevent freezing. Up in the "North Country", aka Adirondack Mountains and the St. Lawrence River plain the frost depth requirements are much deeper.......so soil examinations/explorations for larger water and sewer projects are absolutely imperative, so, please keep in mind what types of soil that you're encountering in your project site as the required depth of bury may have to go deeper. Frost requirements will vary and you should investigate what is the normal or required minimum depth of bury for pipes in your area. Also, remember that typical ambient earth temps around 5 feet below grade are normal in the range of 51 to 54 F....but this may vary due to various local soil and ground water factors, and should be evaluated on a case to case basis.

If you're considering placing concrete around your pipeline I strongly suggest that you do so with a "concrete flowable fill", a low strength concrete backfill (typically having a compressive strength [f'c] = 1,500 psi or less) that can be excavated from the trench anytime in the future in the event that you must perform maintenance and/or repair activities on you pipeline.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#30

Re: Pipe Insulation

01/21/2011 10:24 AM

My answer would be a resounding NO for the reasons mentioned in prior posts. Fiber insulation will get wet and compress essentially becoming useless very quick. If you manage to keep it dry, it becomes ideal areas for rodent nesting. I have dealt with insulation for frost protection and I suspect if good insulation is applied it will work both for cold and hot applications; although, cold applications can be a little more forgiving.

As the system is domestic, you of course would look for economy but not want to compromise the thermal advantages you can gain. As such I would recommend a good commercially manufactured insulation like Maxxr. A more commercial/industrial Dritherm may be easier insulation to apply but does require better preparation before being used. Both of these insulation products are expensive. The pay back may be in the recovery of heating the water in your pipes. 9000 feet of piping is a long distance and I would suggest you retain someone well versed in the insulation field. They may have ready made products that will work and be economical. I have always used a local commercial insulation company for any interior insulation and that was just for condensation control.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Aug 2009
Posts: 100
Good Answers: 8
#33

Re: Pipe Insulation

01/21/2011 12:32 PM

If arctic pipe is out of the question and concrete is an acceptable alternative. then I would suggest you go to cretefoamer.com and see about using their system. You can add as much foam to the concrete as you desire and since strength isn't really an issue here you could turn it into a functional insulating layer. Anything to combat the condensation issue. Good luck to you.

Register to Reply Score 1 for Good Answer
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#34

Re: Pipe Insulation

01/21/2011 1:28 PM

There are several companies that fabricate pre insulated piping that is approved for direct burial.

Any water that makes it's way into the glass-wool insulation, will change it into a heat conductor.

One place to start is Ureacon. http://www.urecon.com/main/home.html

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#37

Re: Pipe Insulation

01/22/2011 12:58 AM

When this 9000ft pipe is laid, it will be something like 60°F. If it is then heated to 180°F, it will expand in length by several feet. Has the design accounted for that?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Dec 2010
Posts: 34
#38
In reply to #37

Re: Pipe Insulation

01/22/2011 5:56 AM

Your comment was indeed considered and the experts said expansion joints are not needed for underground pipes. This was the verdict from more than one Engineer in the field.

For example also in the case of uPVC pipes with bell and spigot joints expansion can easily be contained by simply not pushing in the pipe completely in the bell. However, the advice was that this need not be done when the pipe is laid underground, because the friction of soil will not let the pipe to move in any case.

Now your comment has cast doubt about the matter sending us back to the drawing board. Therefore feedback from experts in the field will be appreciated.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#51

Re: Pipe Insulation

01/23/2011 5:15 AM

Then why does your Website read like this?:












Awesome Savings

Here is what your Utility Company does not want you to know. You can Insulate your home, commercial or industrial property and save over 50% of your energy costs with just ONE COAT OF PAINT!

Cerama-Tech incorporates into its copolymer, elastomeric coating, ceramic platelets, which have the ability to dissipate heat at a very rapid rate and also allows them to reflect heat back into the atmosphere, rather than allowing the heat to be conducted to the underlying substrate.

Cerama-Tech is a fluid applied ceramic coating that INSULATES, is a certified FIRE RETARDANT, suppresses SOUND, ENCAPSULATES ASBESTOS and LEAD, applies and looks like paint.

Cerama-Tech

Cerama-Tech is classified as a Radiant Control Coating (RCC), that is, a coating that creates a radiant barrier which reflects the sun's heat. It is also certified as a Fire Retardant, is a Water Precipitant which creates a water resistant barrier, an Elastomeric that expands and contracts, and a long lasting abuse resistant which is impervious to outside elements and atmospheric conditions. The product applies like paint at thickness of 24 wet mils and dries between 8 and 11 mils.

Are you interested in reducing your power consumption significantly on homes, office buildings and roofs, warehousing, cold storage and exposed HVAC ducts, throughout the year and at moderate cost? Are you in need of a long lasting coating which will allow longer periods between re-painting of outside environments and interior high traffic areas? Is the added protection of a fire retardant for your structures and your personnel a consideration? Do you need a product that will inhibit sound, and encapsulate asbestos or lead based paint? Cerama-Tech will help you achieve these goals.

Goto Energy Star.Gov
Qualified


Use: DrHarryO@Cerama-Tech-Int.com, account to make payments.

Click Here to Pay Online with your Credit Card

You yourself have used the word "paint" (basically a vinyl acrylic carrier infused with "ceramic platelets." How dare you quibble with my description as "ceramic-enriched paint"?

And why does your FAQ page say that this product has no defined R-value?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 84
Good Answers: 1
#52
In reply to #51

Re: Pipe Insulation

01/24/2011 1:24 PM

I suppose they thought the site looked good as written. I quibble because this is not paint bought from Home Depot with ceramic powder mixed in, it is manufactured as a coating. They were most likely trying to explain to hard headed people that the product works differently than R-valued types of insulation. Thanks for posting the site. Gary

Register to Reply
2
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#53

Re: Pipe Insulation

01/25/2011 12:36 AM

I have experience in district heating systems. Insulation is only one (and not the most significant) factor in the design of your pipe.

You mention the crucial point of 9000 feet or 2700 meters. Your prime problem is going to be longevity and maintenance of supply. You should consider pre-insulated pipe designed for the purpose (like Perma-pipe) to protect the pipe from the ravages it will experience when buried underground. A side-effect of protecting the pipe will be the insulation factor.

Also consider a ring-type network with frequent isolation valves such that some supply can be maintained during maintenance, adaption or repair.

Interruption of supply will bring misery to perhaps thousands of customers but a great joy to those skilled in class action lawsuits.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Good Answer (Score 2)
Register to Reply 53 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (1); admeraj (1); Andy Germany (1); Anonymous Poster (3); BabyGuinness (1); CaptMoosie (2); Doorman (1); ENGINEER999 (4); gcoffing (15); Icarus (1); kevinm (1); Life is Enerventure (1); mrswamy (1); qaqcpipeman (6); Sourdough (2); Tom_Consulting (1); Tornado (11)

Previous in Forum: Spring Loaded Ball Valve   Next in Forum: What Does C.O.G. Stand for?

Advertisement