Too Large of Inline Fan

02/06/2011 2:36 PM

Back in 08 I installed a inline fantech fan in my 12" flexible insulated hot air heat pipe. It has a fan control-(rheostat) I run it on the lowest settings but it still is running to fast, Is there anyway to slow it down more.It is producing to much air even on the slow speed. I know I should have bought the smaller one, but it is to late now and the fan is installed and hard to get to, It also was not cheap. When I purchase I was afraid I was not getting one large enough. Wrong. The reason for installing in the first place was that in my upstairs there was next to no air flow. this was installed after the house was built and the only way to get heat up stairs. It was a all electric house when built. And then air was added also for central a/c.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: To large of inline fan

02/06/2011 2:56 PM

You should be able to use a plug-in speed controller from some place like Radio Shack, etc. (Usual disclaimer). I'm no expert, but someone here will give you good advice.

Register to Reply
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#2

Re: To large of inline fan

02/06/2011 4:01 PM

A fan controller could be used. Two alternatives come to mind.

One is an adjustable louver at the exhaust end of the 'pipe'. (There is also magnetic sheet material that can be used over an existing steel exhaust vent to block some of the air flow, if a louver can't be used.)

The other idea is to install a Y coupling downstream of the fan and direct some of the air to another location.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Too Large of Inline Fan

02/06/2011 8:32 PM

I'm not sure why the existing rheostat wouldn't have a large enough resistance to slow the fan to near zero, but I imagine that you could add a further resistance in series (making sure it can handle the wattage.) Not enough numbers are present to assist with calculation. If the fan is hard to access, maybe the circuitry is easier.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #3

Re: Too Large of Inline Fan

02/07/2011 4:13 AM

To progress this idea of yours a bit further, a single diode, with a reasonable current and voltage capacity will effectively halve the voltage and should put the fan at about half of its slowest speed now, aproximately...

You may even need to turn the pot up slightly just to make sure it "self starts" each and every time....

try it out, its cheap and simple.

If you ever need the full speed again, just place a switch across the diode and switch it on to take the diode out of the circuit....

If this fan is so difficult to get at, what will you ever do if it fails? Because at some point it will.......maybe 10 years down the road.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#4

Re: Too Large of Inline Fan

02/06/2011 11:17 PM

In domestic ceiling type fans when the fan regulators are not functioning properly we replaces the capacitor and it works. There may be some emf induction . Check the control wiring.

Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#5

Re: Too Large of Inline Fan

02/07/2011 12:08 AM

What about adding an ambient air bleed to the input (low pressure side of the fan) duct with an adjustable louvre if you want to lower the temperature further,

OR

If you want to reduce the flow at the current temperature you could add an in line louvre before your fan to restrict the airflow.

Register to Reply
Anonymous Poster
#6

Re: Too Large of Inline Fan

02/07/2011 12:22 AM

I would be cautious about trying to slow the fan motor down as many of the small motors greatly loose power & this causes high current draw & can over heat them quickly & even start fires at the motor, I have seen this happen with exhaust fans & even had to help put out the fire caused by a fan in the cieling of a house.

If you have to slow the fan use an electronic motor controler with current control incorporated, but I would be more inclined to do as sugested by Usbport & install a T after the out put of the fan and redirect some of the air, even if it is straight back to the room it comes from, controled with a damper like they use in ducted air con.

Even a basic flat slide over a hole in the side of a straight section of duct would be sufficient to redirect some flow Basically just vent the air to any other location to get the desired flow upstairs

Register to Reply
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#7
In reply to #6

Re: Too Large of Inline Fan

02/07/2011 12:25 AM

oooops I forgot to sign in when I made the post above sorry

Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#8

Re: Too Large of Inline Fan

02/07/2011 12:31 AM

Which model Fantech do you have? From what I looked into, I will take a guess you have the 115V permanent split capacitor type motor. Looking at the flow chart, min CFM is around 900. If this is correct, it is possible that it can not run slower than this due to it's design. It does have class F insulation. I may over heat if run slower.

It does have an auto thermal reset so you cold try using a variable speed plug in unit. I have one for my router and works great. You could give it a try. They sell for around $20.00. It may have to be rewired into your control circuit.

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #8

Re: Too Large of Inline Fan

02/07/2011 4:17 AM

Then run faster!!!! Cooling wind?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Feb 2007
Location: Nebraska
Posts: 104
Good Answers: 2
#11

Re: Too Large of Inline Fan

02/07/2011 9:40 AM

Sure you can it's called a damper . Install a damper to restrict the upstream side of the fan. You can reduce the size of the ductwork but thats more work then just adding a damper. They even make dampers that you drill a hole in the duct then slide the colapsed damper through the hole and then it opens up. We have used them before and they work ok. But a single blade damper works best. You can pick those up as most hardward stores.

Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#12

Re: Too Large of Inline Fan

02/07/2011 10:34 AM

At least half of these posts recommend restricting inlet or outlet to slow airflow. Your fan is over sized. Get the correct one. It will be quieter, more efficient, and not overheat because you are supplying incorrect current.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#13

Re: Too Large of Inline Fan

02/07/2011 3:57 PM

Post 11 called for a damper- good choice, but better if installed on the inlet side.

MUCH better choice is to replace the fan motor with one rated for slower speed- 1750 RPM to 1140 RPM or equivalent. The motor will be relatively inexpensive, only draw the power required (rather than burning it up with unnecessary load (damper) or through the reostat) and will produce 2/3 of the air volume that the original fan is (trying) to produce.

If you still get too much air, the damper will be the easiest to achieve your goal (and the least expensive- first and on-going cost.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Associate

Join Date: Jan 2009
Posts: 47
Good Answers: 1
#14
In reply to #13

Re: Too Large of Inline Fan

02/07/2011 8:44 PM

Hi all: I called where I bought the fan and dug out the invoice. Here is what I have, Fantech FG Series Fan Model FG12XL Inline Centrifugal Fans Air Tight Steel housing For 12" found Duct - 940 cfm. Accessories Model WC 15 Fantech 0-100% variable speed controller ( 115V) Rotary speed controller with on - off switch 5 amp. I called the supplier and they said that the controller I have puts out around 122 volts to 70volts. He said that I could slow it down more but I would have to go to someone like grainger to get the advice and what I would need. He stated that the fan was capable of running at a slower speed but he did not have what I needed. Any ideas. Thanks. This is installed in a flexable insulated duct, so putting a damper on the inlet I would think may collapse the duct pipe. the inlet of this pipe is connected to the furnace outlet plenum.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#15
In reply to #14

Re: Too Large of Inline Fan

02/07/2011 8:49 PM

the damper would be directly at the fan inlet- not the end of the inlet duct

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#16
In reply to #14

Re: Too Large of Inline Fan

02/07/2011 11:49 PM

OK, you have your answer. Now you need a speed controller based on what you were told that this operates at 70-120VAC. Take a look at:

http://www.harborfreight.com/router-speed-control-43060.html

__________________
"Real Bass Players" do not use picks
Register to Reply
Active Contributor

Join Date: Jan 2011
Location: Nara Prefecture
Posts: 14
#17
In reply to #14

Re: Too Large of Inline Fan

02/08/2011 12:28 AM

There are starting and stalling issues if you try to operate below a characteristic speed/voltage. The fan people would design the controller supplied within 'reliable start/run parameters'.

Going outside those is not advisable. I.e. by using an even lower voltage.

I am not a big fan <pun) of starving a 'whole fan' of intake, as it can lead to motor cooling issues.

Therefore what I would suggest is circumferential masking to reduce the fan tips access to air and assure flow past the motor is maintained. "Tips" do most of the "velocity work"

This would be say a 10" hole in a plate, or disc, fitted directly on the suction side of the fan shroud. Then increase or decrease hole dia till you find your desired flow.

__________________
"The Way of the Warrior is resolute acceptance of death" Miyamoto Musashi
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#18
In reply to #17

Re: Too Large of Inline Fan

02/08/2011 12:41 AM

That was my first concern after looking at the data for this fantech product. Which maybe the reason they do not run below 70V, although they claim 0-100% speed control. Personally, I would not have installed this in my duct work at home. And even after the OP said that they themselves didn't know an listed Grainger as a contact to talk to. Anyone selling any product and does not know everything about it, do not buy it from them. That said, I wold not install one of these in anyone's home or business.

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#19
In reply to #18

Re: Too Large of Inline Fan

02/08/2011 1:24 AM

Thinking further about the whole design, I would have installed the blower on the intake side of the heater, whereas it appears to have been installed in the hot air distribution side which makes motor cooling even more of a concern......

Assuming that this is OK perhaps an adjustable bleed duct/diverter take off after the blower feeding back to the heater input ..... presumably the heater is thermostatically controlled so a proportion of warmer intake air would not affect output temperature, the blower motor would get full throughput, but the destination would get only as much air as required, and be more adjustable - depending on the diverter chosen - plus the blower speed control

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#20

Re: Too Large of Inline Fan

02/08/2011 12:43 PM

I know you said the fan is hard to get at (which is to my mind almost a cardinal failure in itself!), but if you could take it out, attach power and use something to cut 30% off the blades, then run it against a file to get them all the same length and weight!!

That will severely reduce the thru put!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Jan 2009
Posts: 47
Good Answers: 1
#21
In reply to #20

Re: Too Large of Inline Fan

02/08/2011 8:08 PM

I would like to thank everyone for there input. I have found the solution, I called Fantech the Co. not a supplier, I got in touch with the tec department. easy fix, I told the man what I was doing and the problem, He said that I had everthing that I needed, I should remove the face plate on the speed control and look for a small screw, it would be marked witch way to turn and the factory setting was only around 20% and I could get any speed that I needed and the fan was designed for it. No problem and Problem solved.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#22
In reply to #21

Re: Too Large of Inline Fan

02/08/2011 8:21 PM

There ya go. When all else fails, call the MFG. Glad you have solved your problem

__________________
"Real Bass Players" do not use picks
Register to Reply
Register to Reply 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (3); Anonymous Poster (1); brettj1au (1); digger104 (2); energygod (2); fishpipes (1); Jimh77 (4); lyn (1); mrswamy (1); PFR (1); Tornado (1); Usbport (1); WAWAUS (2); YoroIdoshi (1)

Previous in Forum: Problem In Stress Analysis Of Piping   Next in Forum: Model Train

Advertisement